ASHP Cycling On/Off - Is it an issue?
Hi @hydros
I'm not an expert on balancing, but you could try the following.
Open up all the radiator valves fully, noting how many turns to fully open from their present setting, so that you can always go back to the start position.
Allow the room temperatures to stabilise and then measure the temperature in the centre of each room.
Gradually close the lockshield valve in the warmest room, a quarter turn at a time, until the desired temperature is achieved.
Continue the above going down the order from warmest room to coolest room.
Recheck the temperature of each room and make adjustments as necessary, until all rooms are at the desired temperature.
Obviously for bedrooms use the TRV's to set a lower desired temperature.
Here are a few thoughts and pictures about cycling. I can only speak about my situation and ASHP (Mitsubishi) but it may help the wider debate. I've been looking through my data logs and this is what happens at around 8C outside temperature. As the temperature rises, the ASHP can't modulate down enough to keep to the weather compensation flow setting so turns on and off
The cycling is about 3 times per hour. The green line is the average energy consumed during the cycling. It's worth pointing out that a steady 20 on the energy scale is 1.2kW so consumption is quite low here. That's to heat the whole house to 20-21C.
This is what happens at about the same outside temperature when using a constant flow rate of about 44C and using the room thermostats. The cycling is controlled largely by the thermostats.
The cycling has reduced but is it using less energy? I'll post the full results of the experiment in a couple of days when I have more cold weather data. It's hard to tell from snapshots like this but it's looking like the weather compensation method uses significantly less energy per day at all temperatures sampled.
I've put my numbers in to your modelling sheet. Not entirely sure I understand what is that's going on, but if I'm reading it correctly I think it says that at 7C outside, I don't have enough output capacity within my radiators to run at a LWT below 35C. FYI - I have an 11kw Daikin system, so slightly smaller than yours but I can't find the details online to be able to update the performance figures.
Not sure it makes much difference but the total emitter output at deltaT50C is 21500w, another thing incorrect on the original installers heat loss report.
Hi @hydros
The reason that I suggested that you look at the modelling tool, was so that you could see the effect on efficiency of changes to insulation levels and heat emitter output.
If you cannot find appropriate Daikin data to repopulate the spreadsheet, you could try using the data for a similar sized Ecodan.
Obviously, by increasing the heat energy output capacity of your heat emitters, your system could operate at lower water flow temperatures, but a similar effect can by achieved by reducing heat demand with improved insulation. Both methods will reduce energy consumption and improve efficiency.
Thanks Derek
Ive used your numbers, I don’t think they are far off my pump, the Daikin is smaller but isn’t quite as efficient, so close enough for a mess about.
I have now completely disabled the thermostat in my system by changing the settings and the heat pump is operating even better. If you recall, my remote thermostat appeared to be suffering interference so I moved it next to the receiver, well it’s still be switching off/on occasionally. With the thermostat completely removed the system is working way better but it’s cold now so you’d expect cycling to reduce anyway, it’ll be interesting to see how it performs when we get a few warmer days.
The feedback from this forum has been so valuable in helping me get to this point. I’ll let it run a little longer before sharing the feedback with my installer.
Posted by: @hydrosThanks Derek
Ive used your numbers, I don’t think they are far off my pump, the Daikin is smaller but isn’t quite as efficient, so close enough for a mess about.
I have now completely disabled the thermostat in my system by changing the settings and the heat pump is operating even better. If you recall, my remote thermostat appeared to be suffering interference so I moved it next to the receiver, well it’s still be switching off/on occasionally. With the thermostat completely removed the system is working way better but it’s cold now so you’d expect cycling to reduce anyway, it’ll be interesting to see how it performs when we get a few warmer days.
The feedback from this forum has been so valuable in helping me get to this point. I’ll let it run a little longer before sharing the feedback with my installer.
Thanks Hydros,
It is in fact a sorry state when the customers are having to educate the installers.
@derek-m, you are so right. I'm getting more and more disillusioned with each passing comment at how many incompetent and/or lazy installers there are out there, which isn't doing the UK any favours on its path to net zero.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
the industry is set up as the boiler industry to exploit U.K. consumers
Installers are poorly supported which is why this London based heating engineer won’t be touching an ASHP any time soon
Professional installer
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
14 hours ago
-
Rodents! A word of warning for heat pump owners
2 weeks ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
1 month ago
-
How to choose Towel Rails for an ASHP
1 month ago
-
How to Zone with a Single Room with UFH
1 month ago
- 26 Forums
- 2,255 Topics
- 50.3 K Posts
- 612 Online
- 5,918 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Is it mad to think there should be a minimum SCOP for UK heat pump installs?
@jamespa, I don’t think that’s quite right. The regulat...
By Mars , 3 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
It is… in theory. But after some rather painful convers...
By Mars , 3 hours ago
-
@agentgeorge That’s a ittle too inscrotumable for me… T...
By Toodles , 4 hours ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
We’re really excited to be recording a landmark Homeown...
By Mars , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Thx, but Sven did the hardware development. My role (as...
By Mosibi , 4 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
Are you using Havenwise for Hot Water? I have ...
By F1p , 5 hours ago
-
RE: PV Panels on roof in Conservation Area
@majordennisbloodnok Fnaargh, I was thinking about try...
By colinc , 6 hours ago
-
RE: Electricity price predictions
@jamespa Ah, you mean MPs that have not pro...
By Batpred , 7 hours ago
-
RE: Buying large amp bidirectional RCD and RCBO
Exactly @transparent , this type of RCBOs are not easil...
By Batpred , 7 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - though I realise I am a Canute, I have an...
By cathodeRay , 7 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
And just when I think great they’re coming next week to...
By Crimson , 10 hours ago
-
RE: Very Much Awake – Renewing the Heating Industry One Step at a Time
I feel that that attitude shared by Aadil from Heat Gee...
By Toodles , 11 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
and we have some of the strongest tidal flows anywhere ...
By Old_Scientist , 13 hours ago
-
RE: Radiator Sizing Dilemma: Vertical vs Type 33 for Low-Temperature Heat Pump Systems
This looks OK. Overall you have roughly the right amoun...
By Old_Scientist , 14 hours ago
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
I'm not familiar with Hive thermostats/controllers, but...
By Old_Scientist , 14 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa mine seems changing albeit not by much, 3.21, ...
By AdamK , 1 day ago
-
@majordennisbloodnok The migration hasn't started in th...
By HCas , 1 day ago
-
RE: One room is colder than the rest of the house
@jamespa thanks for all the advice. Just so you know, ...
By AndrewJ , 1 day ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
My MMI is in the loft but I checked the pump flow rate ...
By RadWhisperer , 2 days ago