ASHP Cycling On/Off - Is it an issue?
Hi @hydros
I'm not an expert on balancing, but you could try the following.
Open up all the radiator valves fully, noting how many turns to fully open from their present setting, so that you can always go back to the start position.
Allow the room temperatures to stabilise and then measure the temperature in the centre of each room.
Gradually close the lockshield valve in the warmest room, a quarter turn at a time, until the desired temperature is achieved.
Continue the above going down the order from warmest room to coolest room.
Recheck the temperature of each room and make adjustments as necessary, until all rooms are at the desired temperature.
Obviously for bedrooms use the TRV's to set a lower desired temperature.
Here are a few thoughts and pictures about cycling. I can only speak about my situation and ASHP (Mitsubishi) but it may help the wider debate. I've been looking through my data logs and this is what happens at around 8C outside temperature. As the temperature rises, the ASHP can't modulate down enough to keep to the weather compensation flow setting so turns on and off
The cycling is about 3 times per hour. The green line is the average energy consumed during the cycling. It's worth pointing out that a steady 20 on the energy scale is 1.2kW so consumption is quite low here. That's to heat the whole house to 20-21C.
This is what happens at about the same outside temperature when using a constant flow rate of about 44C and using the room thermostats. The cycling is controlled largely by the thermostats.
The cycling has reduced but is it using less energy? I'll post the full results of the experiment in a couple of days when I have more cold weather data. It's hard to tell from snapshots like this but it's looking like the weather compensation method uses significantly less energy per day at all temperatures sampled.
I've put my numbers in to your modelling sheet. Not entirely sure I understand what is that's going on, but if I'm reading it correctly I think it says that at 7C outside, I don't have enough output capacity within my radiators to run at a LWT below 35C. FYI - I have an 11kw Daikin system, so slightly smaller than yours but I can't find the details online to be able to update the performance figures.
Not sure it makes much difference but the total emitter output at deltaT50C is 21500w, another thing incorrect on the original installers heat loss report.
Hi @hydros
The reason that I suggested that you look at the modelling tool, was so that you could see the effect on efficiency of changes to insulation levels and heat emitter output.
If you cannot find appropriate Daikin data to repopulate the spreadsheet, you could try using the data for a similar sized Ecodan.
Obviously, by increasing the heat energy output capacity of your heat emitters, your system could operate at lower water flow temperatures, but a similar effect can by achieved by reducing heat demand with improved insulation. Both methods will reduce energy consumption and improve efficiency.
Thanks Derek
Ive used your numbers, I don’t think they are far off my pump, the Daikin is smaller but isn’t quite as efficient, so close enough for a mess about.
I have now completely disabled the thermostat in my system by changing the settings and the heat pump is operating even better. If you recall, my remote thermostat appeared to be suffering interference so I moved it next to the receiver, well it’s still be switching off/on occasionally. With the thermostat completely removed the system is working way better but it’s cold now so you’d expect cycling to reduce anyway, it’ll be interesting to see how it performs when we get a few warmer days.
The feedback from this forum has been so valuable in helping me get to this point. I’ll let it run a little longer before sharing the feedback with my installer.
Posted by: @hydrosThanks Derek
Ive used your numbers, I don’t think they are far off my pump, the Daikin is smaller but isn’t quite as efficient, so close enough for a mess about.
I have now completely disabled the thermostat in my system by changing the settings and the heat pump is operating even better. If you recall, my remote thermostat appeared to be suffering interference so I moved it next to the receiver, well it’s still be switching off/on occasionally. With the thermostat completely removed the system is working way better but it’s cold now so you’d expect cycling to reduce anyway, it’ll be interesting to see how it performs when we get a few warmer days.
The feedback from this forum has been so valuable in helping me get to this point. I’ll let it run a little longer before sharing the feedback with my installer.
Thanks Hydros,
It is in fact a sorry state when the customers are having to educate the installers.
@derek-m, you are so right. I'm getting more and more disillusioned with each passing comment at how many incompetent and/or lazy installers there are out there, which isn't doing the UK any favours on its path to net zero.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
the industry is set up as the boiler industry to exploit U.K. consumers
Installers are poorly supported which is why this London based heating engineer won’t be touching an ASHP any time soon
Professional installer
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
1 day ago
-
Rodents! A word of warning for heat pump owners
3 weeks ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
1 month ago
-
Running my new Nibe ASHP efficiently
1 month ago
-
Weather compensation- why you should use it
1 month ago
Currently viewing this topic 2 guests.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 401 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
Without knowing it, @andrewj, you've laid down the gaun...
By Majordennisbloodnok , 3 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos and @cathoderay thanks. I have some history grap...
By benson , 7 minutes ago
-
I am having my existing heat pump changed to a Vaillant...
By trebor12345 , 40 minutes ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 1 hour ago
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 2 hours ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 3 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 4 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 4 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 4 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 5 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 9 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 20 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 22 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago