(@derek-m)
Illustrious Member Moderator
13637 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4156
 

Hi @hydros 

I'm not an expert on balancing, but you could try the following.

Open up all the radiator valves fully, noting how many turns to fully open from their present setting, so that you can always go back to the start position.

Allow the room temperatures to stabilise and then measure the temperature in the centre of each room.

Gradually close the lockshield valve in the warmest room, a quarter turn at a time, until the desired temperature is achieved.

Continue the above going down the order from warmest room to coolest room.

Recheck the temperature of each room and make adjustments as necessary, until all rooms are at the desired temperature.

Obviously for bedrooms use the TRV's to set a lower desired temperature.


   
HydroS, Mars, HydroS and 1 people reacted
ReplyQuote
(@kev-m)
Famed Member Moderator
5550 kWhs
Joined: 3 years ago
Posts: 1299
 

Here are a few thoughts and pictures about cycling.  I can only speak about my situation and ASHP (Mitsubishi) but it may help the wider debate.  I've been looking through my data logs and this is what happens at around 8C outside temperature. As the temperature rises, the ASHP can't modulate down enough to keep to the weather compensation flow setting so turns on and off

Weather Comp

The cycling is about 3 times per hour.  The green line is the average energy consumed during the cycling.  It's worth pointing out that a steady 20 on the energy scale is 1.2kW so consumption is quite low here.  That's to heat the whole house to 20-21C.  

This is what happens at about the same outside temperature when using a constant flow rate of about 44C and using the room thermostats. The cycling is controlled largely by the thermostats.  

 

45C Flow & Thermostats

The cycling has reduced but is it using less energy?  I'll post the full results of the experiment in a couple of days when I have more cold weather data.  It's hard to tell from snapshots like this but it's looking like the weather compensation method uses significantly less energy per day at all temperatures sampled.  

 


   
HydroS, Derek M, HydroS and 1 people reacted
ReplyQuote
(@hydros)
Estimable Member Member
326 kWhs
Joined: 2 years ago
Posts: 59
Topic starter  

@derek-m 

I've put my numbers in to your modelling sheet. Not entirely sure I understand what is that's going on, but if I'm reading it correctly I think it says that at 7C outside, I don't have enough output capacity within my radiators to run at a LWT below 35C. FYI - I have an 11kw Daikin system, so slightly smaller than yours but I can't find the details online to be able to update the performance figures.

image

   
ReplyQuote
(@hydros)
Estimable Member Member
326 kWhs
Joined: 2 years ago
Posts: 59
Topic starter  

Not sure it makes much difference but the total emitter output at deltaT50C is 21500w, another thing incorrect on the original installers heat loss report. 


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13637 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4156
 

Hi @hydros 

The reason that I suggested that you look at the modelling tool, was so that you could see the effect on efficiency of changes to insulation levels and heat emitter output.

If you cannot find appropriate Daikin data to repopulate the spreadsheet, you could try using the data for a similar sized Ecodan.

Obviously, by increasing the heat energy output capacity of your heat emitters, your system could operate at lower water flow temperatures, but a similar effect can by achieved by reducing heat demand with improved insulation. Both methods will reduce energy consumption and improve efficiency.


   
HydroS, Mars, HydroS and 1 people reacted
ReplyQuote
(@hydros)
Estimable Member Member
326 kWhs
Joined: 2 years ago
Posts: 59
Topic starter  

Thanks Derek

Ive used your numbers, I don’t think they are far off my pump, the Daikin is smaller but isn’t quite as efficient, so close enough for a mess about. 
I have now completely disabled the thermostat in my system by changing the settings and the heat pump is operating even better. If you recall, my remote thermostat appeared to be suffering interference so I moved it next to the receiver, well it’s still be switching off/on occasionally. With the thermostat completely removed the system is working way better but it’s cold now so you’d expect cycling to reduce anyway, it’ll be interesting to see how it performs when we get a few warmer days. 
The feedback from this forum has been so valuable in helping me get to this point. I’ll let it run a little longer before sharing the feedback with my installer. 


   
ReplyQuote



(@derek-m)
Illustrious Member Moderator
13637 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4156
 
Posted by: @hydros

Thanks Derek

Ive used your numbers, I don’t think they are far off my pump, the Daikin is smaller but isn’t quite as efficient, so close enough for a mess about. 
I have now completely disabled the thermostat in my system by changing the settings and the heat pump is operating even better. If you recall, my remote thermostat appeared to be suffering interference so I moved it next to the receiver, well it’s still be switching off/on occasionally. With the thermostat completely removed the system is working way better but it’s cold now so you’d expect cycling to reduce anyway, it’ll be interesting to see how it performs when we get a few warmer days. 
The feedback from this forum has been so valuable in helping me get to this point. I’ll let it run a little longer before sharing the feedback with my installer. 

Thanks Hydros,

It is in fact a sorry state when the customers are having to educate the installers.


   
Mars, HydroS, Mars and 1 people reacted
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
16743 kWhs
Veteran
Joined: 3 years ago
Posts: 2316
 

@derek-m, you are so right. I'm getting more and more disillusioned with each passing comment at how many incompetent and/or lazy installers there are out there, which isn't doing the UK any favours on its path to net zero.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU

Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk


   
Kev M, HydroS, Kev M and 1 people reacted
ReplyQuote
(@alec-morrow)
Honorable Member Contributor
1314 kWhs
Joined: 2 years ago
Posts: 209
 

@editor 

 

the industry is set up as the boiler industry to exploit U.K. consumers

Installers are poorly supported which is why this London based heating engineer won’t be touching an ASHP any time soon