Posted by: @hydrosThe cycling is only occurring at outside temperatures above about 8C so probably nothing to worry about. COP for yesterday was 3.18, not bad but I was hoping for a little better. Not sure what else I can do to improve this?
Regarding thermostat. It is a remote thermostat that the installer fitted, which gets interfered with by something in the house, so this needs replacing with a different model. I like the idea of a smart version to be able to see some stats on the house temperature but from the experience over the last week, I think it's something that will mostly be forgotten above once weather compensation curve is fully optimised, so a basic wired version is probably sufficient.
Hi Hydros,
You don't actually need a thermostat in your system, in fact it would be better to remove the thermostat altogether, and move your Daikin controller into the main living area and set it for Leaving Water Temperature Modulation.
One way to improve the COP for DHW production would be to reduce the setpoint to the lowest acceptable level, thereby reducing how hard the heat pump has to work. Another way to improve the COP is to schedule DHW production when the outside air temperature is warmest, often mid to late afternoon.
It is my understanding that the sanitisation cycle is only required once per week, and needs to raise the water temperature above 60C for approximately 10 minutes. Again, if this were to be performed mid to late afternoon, in place of a normal heating cycle, this should help to improve the overall COP values.
@heat-pump-newbie electricity usage is about the same for a comparable day, but heat output is higher, so that's a win. But I've noticed the compressor cycling has gone up at the lower running temperature on days like today when it only needs to run at 26-28C, this isn't good for wear & tear on the compressor.
This has reminded me of the SuperHomes report from Ireland where they advocated a minimum output temperature for radiator circuits, controlled by a thermostat to reduce the cycling. The final report is Superhomes 2.0 D4.4 Best Practice Guide for ASHP Retrofit Final.indd (lit.ie) and the section 3.4 (page19) about radiator performance during low heat demand is making for an interesting read. I first read this months ago but had other things to sort with the original installer back then.
@derek-m if you haven't read this report I'd be really interested to hear your opinion.
@kev-m was going to try this approach of controlling the house with a thermostat last week, I think I read on another thread so it'll be interesting to hear the results of that trial.
@derek-m forgot to add - agreed on scheduling the time of the hot water run, I did find that improved things. I've already got mine setup for late afternoon. I might secretly drop the tank temperature a degree or two and see if it gets noticed. 🙂
Posted by: @hydros@heat-pump-newbie electricity usage is about the same for a comparable day, but heat output is higher, so that's a win. But I've noticed the compressor cycling has gone up at the lower running temperature on days like today when it only needs to run at 26-28C, this isn't good for wear & tear on the compressor.
This has reminded me of the SuperHomes report from Ireland where they advocated a minimum output temperature for radiator circuits, controlled by a thermostat to reduce the cycling. The final report is Superhomes 2.0 D4.4 Best Practice Guide for ASHP Retrofit Final.indd (lit.ie) and the section 3.4 (page19) about radiator performance during low heat demand is making for an interesting read. I first read this months ago but had other things to sort with the original installer back then.
@derek-m if you haven't read this report I'd be really interested to hear your opinion.
@kev-m was going to try this approach of controlling the house with a thermostat last week, I think I read on another thread so it'll be interesting to hear the results of that trial.
I'll post some interim results soon. Some interesting results re cycling as well as energy consumption.
I have posted a link to the report, it's just not showing as one. I'll insert it properly here as I can't edit my original post.
Hi to all, first of all wish you all the best for this holidays, I am new here, from Croatia and I found this forum gives a lot of answers really, good job!! I will ask later a detailed question but for now...i have more or less similar problem.
Heat pump going on of pretty often when the cycle is running.
On which percentage should be set the room influence??
Goran
@rocky11, welcome to the forums. When you're ready, please start a new thread detailing your system and what's going wrong with it.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Where is the auto bypass installed in the system? Is it close to the ASHP end of the circuit as implied by the diagram?
Internationally recognised award winning installer of heat pumps and stuff
Auto bypass? Diagram? Really difficult whilst not knowing what make etc of system you have.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi @hydros
I have read through the full report and although it is now several years old, much of it is still relevant.
There are however a few areas where it does appear to be contradictory, in one section highlighting the problem of compressor cycling and the need for continuous consistent operation, and then another section would be advocating on - off operation in preference to continuous operation.
One thing that is abundantly clear is that there is no 'one solution fits all situations', and that careful design, correct installation and optimal configuration and commissioning are all required to produce a system that operates with the best efficiency.
Posted by: @hydrosI have posted a link to the report, it's just not showing as one. I'll insert it properly here as I can't edit my original post.
Reduction in COP due to excessive cycling sounds a feasible theory but if the quality of the data analysis in the attachment is similar to that of the arguments and written text I don't believe any of the results. I'm not sure what they have proven, other than the manufacturer's stated COP isn't being achieved in a single ASHP installation. I'm not even sure the data supports their theory that the reduction in COP is due to cycling; COP seems to stay constant as cycling increases.
I'll publish my own results soon. 🙂
-
Surface mount or bury primaries for heat pump installation?
6 days ago
-
UFH and ASHPs
2 months ago
-
Installing your own ASHP - DIY
3 months ago
-
ASHP install contract and BUS grant money
4 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
4 months ago
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 98 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
It does indeed look like that, @skyefarmer. There is ...
By Majordennisbloodnok , 59 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist I found the switching between tariff jus...
By Toodles , 16 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 19 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 22 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 1 day ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 2 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 2 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 2 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 3 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 3 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 3 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 4 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 4 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 4 days ago