ASHP choice help - 55C flow temperature required

30 Posts
10 Users
10 Reactions
3,152 Views
(@wintergreen)
Eminent Member Member
150 kWhs
Joined: 1 year ago
Posts: 11
Topic starter  

I'm grateful for your input, but it doesn't really help me.  I'm not looking to rip out the floor.  I'm investigating the possibility of a more efficient, low-carbon approach to heating it.  It requires (at least in a cold spell) a 55 degree flow temp, so I was asking whether anyone on this forum could recommend an ASHP for that spec.

In any event, I'm not sure your analysis is quite fair to Nu-heat. As you say, the arrows on the drawing have been misaligned.  The heat transfer plates are shown in red. The polystyrene board and floor insulation are intended to restrict heat supply downwards. The thermal conductivity of polystyrene is about 3 x that of plywood, so one might expect 75% of the heat to go into the floor. As for the flow rate, it is designed for 9.4 litres per minute. By my calculations, it could achieve almost double that flow at 0.9 m/s, so it would appear to be sufficient.

Stiebel Eltron WPLA07 7kW ASHP. 26 x 400W PV. 10kW Sunsynk 3-phase inverter. 6 x 4.8kWh Pylontech US5000C batteries.


   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
8408 kWhs
Veteran Expert
Joined: 2 years ago
Posts: 1396
 

Yes, I haven't yet arrived at the solutions.
I'm just doing the rough calculations, which suggest to me that Nu-Heat weren't designing with a common ASHP in mind.

Let's recall what Mars wrote earlier:

Posted by: @editor

... you're edging towards the realm of HT heat pumps, and COPs tend to suffer as a consequence.

Normally, you really wouldn't want a COP below 3.0.
But... if you're generating the electricity from your own roof-top solar panels in the first place, then it matters less.
You won't be buying in electricity at 35p/kWh.

Equally, you've got 3-phase in the house. That's a lot more efficient at operating a heat-pump.

So a high-temperature heat-pump is worthwhile investigating... although it's not in my area of expertise.

@editor also suggested looking at a Vailant Isostor, which doesn't seem to exist.
So we'll assume that he meant Arostor, which looks to be heading in the right direction.

 

Just to make sure we've covered all the bases, there are two other 'solutions' worthy of mentioning, although I think they're unlikely to be attractive to you.

A. Add further surface area to the UFH, by installing 'radiating surfaces' on wall-space.

It doesn't have to look like a radiator.
It could equally well be a sealed glazed unit with water cascading down the centre, like a waterfall.

Have a look at Primrose products, or search online for 'water wall' and then click on images.

 

B. Utilise glazing in the ceiling/roof to add passive solar gain.
That's the approach I've used in my own double-height kitchen / living-area:

image

Save energy... recycle electrons!


   
Mars reacted
ReplyQuote
Jeff
 Jeff
(@jeff)
Noble Member Member
2615 kWhs
Joined: 3 years ago
Posts: 425
 

 

@transparent you mentioned:

I'm just doing the rough calculations, which suggest to me that Nu-Heat weren't designing with a common ASHP in mind

The initial post mentioned this when they had  a gas boiler, i am not sure 10 years ago the system was ever designed with any thought of a heat pump? 

This was thermally upgraded 10 years ago, and fitted with UFH under an insulated floating engineered wood floor. 


   
Transparent reacted
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
17023 kWhs
Veteran
Joined: 3 years ago
Posts: 2341
 

@wintergreen, your best bets for HT heat pumps are Samsung and Daikin, and I believe Panasonic are coming out with one too. I suspect all the major players will have one in the next 12 months as direct boiler replacements for set ups that require more heat, such as yours.

But irrespective of the brand, COP will suffer the hotter you need to run. By all accounts, Samsung’s new unit will run at a COP just over 1 at 75C. That’s a lot of electricity consumption.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU

Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
17023 kWhs
Veteran
Joined: 3 years ago
Posts: 2341
 

@julianc has a HT Daikin unit, but I don’t think he pushes 55C because he has excellent insulation. Any comments Julian?

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU

Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk


   
ReplyQuote
JulianC
(@julianc)
Prominent Member Member
1033 kWhs
Joined: 3 years ago
Posts: 304
 

@wintergreen hi Winter. Have a look at my Worcestershire ASHP folder/content elsewhere on this site [link added]. As Mars says, I’ve had a Daikin 3H HT 18kW (nominal 12kW plus 6kW back up heater) ASHP for almost two years. This will get to 70C+ without backup heater, but as stated elsewhere, the SCOP is reduced at such high temperatures. It will easily achieve 55C. But on weather compensation, you will only need such high temperatures a few times per year. I was running at 2 and a bit when we had the -10C cold snap for a couple of day’s before Christmas. So my SCOP is 3.73. 
We have a Mixergy hot water cylinder - again recommended. Get an electric diverter to heat h/w for free from your solar PV. We have a Solic 200. You might consider a Myenergi product if you intend to get one of their EV chargers as their ecosystem work well together to balance your solar usage. 
Ping me with other questions

This post was modified 1 year ago by Transparent

Daikin Altherma 3H HT 18kW ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and Hyundai Ioniq 5 P45 electric vehicles with Myenergi Zappi mk1 charger


   
Mars and Transparent reacted
ReplyQuote



(@wintergreen)
Eminent Member Member
150 kWhs
Joined: 1 year ago
Posts: 11
Topic starter  

That's interesting - thanks Julian.  I've looked through your thread. It looks like you have achieved excellent performance.  I have searched high and low for the relevant specs on that Daikin model. I am particularly interested in the COP curve at 55 degree LWT.  Do you happen to know what that looks like, or where I can find it? The more general data is useful, but is likely to have less of a bearing on performance for our house given our unusual constraints. 

Stiebel Eltron WPLA07 7kW ASHP. 26 x 400W PV. 10kW Sunsynk 3-phase inverter. 6 x 4.8kWh Pylontech US5000C batteries.


   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
8408 kWhs
Veteran Expert
Joined: 2 years ago
Posts: 1396
 

@wintergreen - I've found a Daikin slideshow for the HT (high temperature) models, marked Internal Use Only.

There are 70 slides, including these two graphs which provide indicative COPs

image
image

The slides contain overlays to prevent me screen-grabbing all the data in one image.
So you'll need to view them online for yourself.

Note that the internal model numbers for the Daikin HT range has changed.
The slideshow uses the older nomenclature.
But the 14kW 3-phase model is the same, whatever they choose to call it.

Save energy... recycle electrons!


   
Mars and ronin92 reacted
ReplyQuote
JulianC
(@julianc)
Prominent Member Member
1033 kWhs
Joined: 3 years ago
Posts: 304
 

@transparent interesting graph. I’m surprised at such a difference between LT & HT. 

 

Daikin Altherma 3H HT 18kW ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and Hyundai Ioniq 5 P45 electric vehicles with Myenergi Zappi mk1 charger


   
ReplyQuote
JulianC
(@julianc)
Prominent Member Member
1033 kWhs
Joined: 3 years ago
Posts: 304
 

@wintergreen sorry I don’t. I think I have the graphs from the original quote. 
I do think the graphs can only take you so far: Daikin UK marketing director said most makes we’re similar

Daikin Altherma 3H HT 18kW ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and Hyundai Ioniq 5 P45 electric vehicles with Myenergi Zappi mk1 charger


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13747 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4169
 

@wintergreen

Please find attached detailed information for the Mitsubishi Ecodan range of ASHP's kindly supplied by Kev some time ago. There is also detailed data for the Midea range of ASHP's kindly provided by Batalto, again some time ago. Both give fairly comprehensive operating test data for the various models then available. The password for the Midea file is midea2020

Unfortunately the forum site is now limiting the size of file that can be attached, and will not allow me to upload the Ecodan data. If you DM me, I will try to send the file via that route.

I presume that you wish to keep your home warm in the most efficient and cost effective manner.

What is the calculated heat loss, each hour, for your whole home at an outside temperature of -2C? Do you have any detailed information of the output capacity of your UFH and the rest of the heat emitters in your home? What is the thermal mass of your home, and the room in question?

I fully understand your initial question, and I am not trying to dissuade you from the HT solution if that is what you desire, but I prefer to explore all the various options, based upon the laws of physics and thermodynamics. The data kindly provided by Transparent highlights the possible trade-offs to be considered between a HT unit as against a LT unit.

The first thing to ascertain is the total heat loss of your home at the normally specified temperatures of 21C indoors, and -2C it would appear outside, for your area. This would therefore provide an indication of the size of heat pump required, which can affect the overall efficiency of the whole system.

Have you considered a GSHP or Air to Air (A2A) ASHP solution?

If the required LWT differs greatly between the living room and the rest of the property, have you considered a two heat pump solution, one to heat the living room and DHW operating at a higher LWT, and one to supply the rest of your home operating at a lower LWT?

A further aspect to consider is how many days will a LWT of 55C be required? It could be that just having some form of additional heating in the living room during particularly cold spells is more efficient and cost effective than running a HT heat pump throughout the whole year.

 

This post was modified 1 year ago by Derek M

   
Mars reacted
ReplyQuote
(@fazel)
Reputable Member Member
1085 kWhs
Joined: 1 year ago
Posts: 124
 

Posted by: @derek-m

Unfortunately the forum site is now limiting the size of file that can be attached, and will not allow me to upload the Ecodan data. If you DM me, I will try to send the file via that route.

https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_ATW_Databook_R32_Vol5_5                        from page 60

https://www.vaillant.cz/downloads/projek-n-podklady/kl-06-e2-verze-01-18012023-2564719.pdf       from page 34

 


   
ReplyQuote