Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Another 17kw Grant Heat Pump - Advice Needed!
@allyfish Thank you, I've learnt so much more I'm the last week than the time the ashp were installed.
I'm assuming both pump adjustments would have to be like for like?
On a side note since the milder weather I'm finding the radiators warmer than ever.
2 10kw Grant Aerona3
Heat loss calc 16.5 kw @ -2.8 degrees
4.32 PV
@bretix we're all learning on these systems 🙂 I would set the secondary pump to full flow, always. If the pipe distance between your low loss header (white rectangular box in photos above) and the outdoor unit is quite short, and is larger 28mm pipe, a lower speed setting on the pump inside the ASHP might better balance. Most of the system restriction is on the secondary (radiator and house side) of the system, there's normally much less pressure loss between the low loss header and the ASHP. ASHPs need more flow than fired boilers, because they have a lower deltaT temperature difference between flow and return. For half the delta T you need to double the flow to transfer the same heat energy in kW.
There's not too much to worry about having too high a flow on the primary side, but best to balance primary and secondary if possible. What happens with the low loss header is that water can pass down through it, short circuiting the secondary flow and return. They are designed to do this for installations where the primary ASHP side flow is constant, such as a fixed speed primary pump, like as used in Grant's units, but the secondary side flow might vary due to on/off zoning controls or zone modulating controls like TRVs or UFH control valves. The ASHP sees a slightly higher return water temperature then, but it just modulates down in response. The opposite, having higher flow on the secondary side than the primary, is more of a problem, as the secondary pump starts recirculating return water up through the header, into the secondary flow pipe, and you see a temperature drop - the flow to the radiators on the secondary side is colder than the flow from the ASHP on the primary side. That's not so good, as all the heat energy generated by the ASHP is then not flowing into the emitters.
Check that weather compensation is enabled and set to something sensible, the Grant default settings are a good starting point.
- 26 Forums
- 2,646 Topics
- 61.8 K Posts
- 740 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
@editor Sorry Mars, I didn’t see a notification about ...
By Toodles , 5 minutes ago
-
RE: Hitachi Heat Pump being replaced with Vaillant
Yes to be configured as a volumiser. The pump is to be...
By trebor12345 , 23 minutes ago
-
RE: Anyone concerned about GivEnergy?
So it seems subscription day has finally arrived for Gi...
By TechnoGeek , 2 hours ago
-
RE: How many people are happy with their ASHP and do you believe them?
I agree, and not. Energy prices are a largely politica...
By JamesPa , 4 hours ago
-
RE: Solar Produced vs Home Consumed
All inverters will use solar power in preference to dra...
By JamesPa , 4 hours ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 5 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 17 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 1 day ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 1 day ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago