Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Another 17kw Grant Heat Pump - Advice Needed!
@allyfish Thank you, I've learnt so much more I'm the last week than the time the ashp were installed.
I'm assuming both pump adjustments would have to be like for like?
On a side note since the milder weather I'm finding the radiators warmer than ever.
2 10kw Grant Aerona3
Heat loss calc 16.5 kw @ -2.8 degrees
4.32 PV
@bretix we're all learning on these systems 🙂 I would set the secondary pump to full flow, always. If the pipe distance between your low loss header (white rectangular box in photos above) and the outdoor unit is quite short, and is larger 28mm pipe, a lower speed setting on the pump inside the ASHP might better balance. Most of the system restriction is on the secondary (radiator and house side) of the system, there's normally much less pressure loss between the low loss header and the ASHP. ASHPs need more flow than fired boilers, because they have a lower deltaT temperature difference between flow and return. For half the delta T you need to double the flow to transfer the same heat energy in kW.
There's not too much to worry about having too high a flow on the primary side, but best to balance primary and secondary if possible. What happens with the low loss header is that water can pass down through it, short circuiting the secondary flow and return. They are designed to do this for installations where the primary ASHP side flow is constant, such as a fixed speed primary pump, like as used in Grant's units, but the secondary side flow might vary due to on/off zoning controls or zone modulating controls like TRVs or UFH control valves. The ASHP sees a slightly higher return water temperature then, but it just modulates down in response. The opposite, having higher flow on the secondary side than the primary, is more of a problem, as the secondary pump starts recirculating return water up through the header, into the secondary flow pipe, and you see a temperature drop - the flow to the radiators on the secondary side is colder than the flow from the ASHP on the primary side. That's not so good, as all the heat energy generated by the ASHP is then not flowing into the emitters.
Check that weather compensation is enabled and set to something sensible, the Grant default settings are a good starting point.
- 27 Forums
- 2,799 Topics
- 66.1 K Posts
- 2,366 Online
- 7,201 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Safety study for plug in batteries out to tender - looks like Q3 2027 at best before legal
I only see 1 phase, ending in March 2028?
By dansus , 17 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
@editor Manually setting the charging times and rates o...
By dansus , 49 minutes ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@carpenterstation I think you must mean “The whole ho...
By GrahamF , 3 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
Ours is similar to James, but with a few optional tweak...
By Batpred , 3 hours ago
-
RE: Renewables & Heat Pumps in the News
Yes, this is a swiss and german standard I believe, Vai...
By Batpred , 4 hours ago
-
RE: BT cuts you off, Plusnet blames Openreach... welcome to “seamless” broadband switching
My Vodafone FTTP broadband was down for a month when I ...
By JamesPa , 8 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@editor FWIW my problem was resolved, eventually, after...
By BigFish , 10 hours ago
-
My heating has been off and DHW on throughout the summe...
By DavidAlgarve , 13 hours ago
-
RE: Anyone concerned about GivEnergy?
The GivE forum seemed to have survived the collapse of ...
By downfield , 14 hours ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
@singlespeed I had better explain how my radiators are ...
By Toodles , 14 hours ago
-
RE: Cooling/heating with one unit
@mrkfm The Solo has a small capacity and only suitable ...
By dgclimatecontrol , 15 hours ago
-
First you need to know how much thermal energy you'll n...
By bobflux , 1 day ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
Come for the low-carbon homes. Stay for George Clarke’s...
By Mars , 2 days ago
-
RE: How should the Boiler Upgrade Scheme be reformed?
Not quite, regular A2W heat-pumps need a load of extra ...
By Temperature_Gradient , 4 days ago
-
RE: Heat Geek installations: share your experiences
one thing i learnt from reading people’s comments and e...
By Batpred , 4 days ago