Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
It's great that Aira continue to add features to the app. Our 8kW efficiency figures are:
| Month | Electric Consumption | Heat Delivered | COP |
| October 24 | 403 | 1512 | 3.75 |
| November 24 | 654 | 2409 | 3.68 |
| December 24 | 713 | 2875 | 4.03 |
Has anyone got any information on how/why they justify a buffer tank in their install? Everyone seems really happy with the install and running so I assume the buffer isn't an issue but given the general feeling that buffer tanks shouldn't be used by default this is the one piece of their installation that I find a bit strange.
@andrewj Our installers fitted am LLH; their justification for fitting this efficiency reduction is that ‘It ensures that the heat pump sees a constant load and the actual secondary circuit flow rate is less critical making it much easier to achieve a constant Delta T.’ Not sure that this is the full story but suspect that, as mentioned on this hub numerous times, it reduces the chance of engineer call-outs. 😒 Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles So that would imply what I thought (perhaps I'm too cynical): it is put in to separate problem responsibility between the heat pump and the secondary circuit. Although in the case of Aira, who install both sides and presumably are responsible for warranting both, I don't think that counts for much (as opposed to, say, a Vaillant heat pump and a local installer.) Is it much of an efficiency hit or do they have it technically sussed?
@andrewj In my case, I would put any shortcomings down to the installers but fortunately for us, our system is working very well. I took the measure of optimising the things that the installers run out of time to do😉 for myself. I let them roughtly balance the radiators during a very warm end of day in February (before they all went off home or to the pub or whatever) as I knew there was no way the system would be optimised that afternoon!
I also played with the LWT and at that time, I had to let the MMI controller do what it could to run well. I gradually improved the settings for the WC and then come the following autumn, I had Homely smart control added.
In between times, I bought 4 of the temperature probes and ‘calibrated’ them, (I bundled all the probes together, let them stabilise overnight and noted the disparity in the 4 sets of readings). I taped the probes on all four pipes entering and leaving the LLH and covered each with a few layers of insulating aluminium coated sheet. I then gradually adjusted the secondary pump speed to achieve minimum disparity between the flow in and flow out to the pump - and likewise between the return flow and the LLH return to the heat pump circuit. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@andrewj Well, not everyone. My experience would probably be the one anti heat pump brigade would be keen to highlight. The product is great, the installer who came is really good. But, I don't think Aira have their operations under control.
It's day 9 and my installation is still ongoing. Not because it's a complex installation, but rather because they decided to again send only one engineer on-site this week. With a three storey house and 15 radiators, the one engineer on-site can only run around so much to check for leaks. There was a massive leak in my study and just missed the electrical sockets by sheer luck. It could have been a total disaster. I am having to help the installer with lifting and positioning a large radiator as there's no way he would be able to lift a 70 kg radiator and install by himself. And to top it all, they sent me an invoice to pay for a system that's not even commissioned!
16 * 435 watts PV
13 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
Bosch Induction Hob
Pod Point Solo 3 charger
Day nine gone, the heat pump is still not commissioned. There's a sensor problem and there's no electrician onsite to help the lead engineer. Now, they won't come back until Thursday and won't be commissioned until day 11.
Not sure what options are there to explore, complain to MCS, trading standards, Ofgem. Personally, I shouldn't have fallen for the 15 year warranty and should have gone with Octopus or Heat Geek. If their service is as bad as the installation experience, the warranty is not worth the hassle.
16 * 435 watts PV
13 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
Bosch Induction Hob
Pod Point Solo 3 charger
@chandykris Sounds like a pretty poor state of affairs. Hopefully once it is in and commissioned it will work fine and this will drift into a bad memory lost in the mists of time. I now have to decide between Octopus or Heat Geek for an install - I think I'll leave Aira and not complicate it further. I don't have all the details yet but I think the juggle will be between cost, confidence and heat pump model!
Thanks @andrewj. Hope my bad experience didn't put you off. Others in the forum have had good experiences, so maybe mine is just an odd one out.
I should have done what Toodles and others had suggested. Lower the flow temperature post installation. Let Octopus design the system at 50 degrees flow temperature, but upgrade the radiators myself at an extra cost and then lower the flow temperature. Well, hindsight is a wonderful thing!
16 * 435 watts PV
13 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
Bosch Induction Hob
Pod Point Solo 3 charger
@chandykris sorry to hear this, I hope that progress picks up and Aira will sort your system.
Aira managed to send an engineer at 5:30 pm today and it took a while, but thank Higgs Boson, we have heat! It was up and stunning around 8:30 pm starting with hot water. Then heating kicked off and the house is slowly heating up. Really surprised how quiet the unit is, I can hardly hear it working from the sun room just 1.5m away.
Still loads to do, lagging everything, sorting out some joints, cleaning up everywhere, close the boiler flue hole. But, at least the heat pump is commissioned. Like Andrew said, maybe this will just be a bad memory in the mist of time.
16 * 435 watts PV
13 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
Bosch Induction Hob
Pod Point Solo 3 charger
-
How to Understand Wiring Up a Heat Pump
6 months ago
-
Heat Pump Paradox: The Industry's Adoption Divide
2 years ago
-
Not So Hot: Too Many Subpar Heat Pump Installations in the UK
2 years ago
-
The Most Popular Heat Pump in the UK: Is It In Your Home?
2 years ago
-
Heat Pumps - An Expensive Folly?
3 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 293 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago



