I failed to say that the design allows for a 50C flow temperature but since the engineer did some fettling I have not investigated it again.
Posted by: @timatheronwoodI failed to say that the design allows for a 50C flow temperature but since the engineer did some fettling I have not investigated it again.
Oh, you can't beat a good 'fettle'. 😋
I had the unit set to 18 overnight (till 4am) and 19 from then on but this morning at 6am the temperature in the house was down to 17.5C It had not risen beyond that by 10am. At 12 noon the temperature had risen to 18C in the house. I have changed the slope of the "curve" so that it now reaches maximum at 0C instead of -10C. This afternoon the temperature had risen to 18.5C and I have changed the temperatures to 20C in the day and 19 at night to cope with the cold weather.
Could this be due to the unit not meeting the design spec for output temperature. The Daikin literature says that we should be able to get a 65C output. But the most I have ever seen is 45C even thought it is set to 63C.
Any thoughts anyone?
If Homeowners are prepared to provide the information, then maybe a spreadsheet containing the following information would be of most use from the comparison, and highlighting of possible problems, point of view.
Forum Handle: Toodles
Manufacturer: Daikin
Model: EDLA082V3
Type: ASHP
Arrangement: Mono
Area of Country: Berkshire
Home Type: 4 bed semi 1930’s build
Size: Square Metres:95
Insulation Level: Scale of 1 to 10 possibly? 10
Heat Loss Calculation: kW @ Amb. Temp, of: ?C 6.5 kW
Type of Controller: Modulating
Type of Control: Weather Compensation, LWT setting
System Type: Radiators (Mainly new for LT use)
Total Output of Heat Emitters: kW
Buffer Tank or Low Loss Header: LLH
Secondary Pumps: Number or No 1
Solar PV System: Size or No 8.1 kWp
Power Diverter: Yes
Battery System: Size; 13.5 kW/h Tesla Powerwall
Anything else that anyone can think may be useful. Please feel free to rearrange the order. In this milder weather, we are running at 22.5 degrees nominally (we like a warm house!) and are using approx. 0.5 kW/h
For my personal viewing only, bank account details and all necessary passwords and access codes. If I told you, I would have to terminate your existence! Regardsd, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Perhaps I should add to the above system (sorry, but I failed to be able to edit the entry) based on a Daikin 8 kW ASHP that the domestic hot water heating is handled by a Sunamp Thermino ePV210 heat battery. The reason being, space is at a premium and the MCS guideline for a 4 bedroom house is 210 litres of DHW storage and we just do not have a space for such a tank! The Thermino is considerably smaller and can be accommodated (just!) in our airing cupboard - the insulation is extremely good so the total heat loss in 24 hours is less than 0.75 kW/h, so very little warming is available in the airing cupboard - just the lost heat coming from the unlagged plumbing from the LLH etc. and this helps to provide a background warmth in the cupboard.
I scored 10 myself for insulation as we have double glazing (triple in one room), cavity wall insulation, underfloor insulation from Q-Bot on the ground floor and approx. 40 cm. of loft insulation plus boarding sandwiched in the middle, plus we have approx. 5 cm. thick insulating board with a foil face between all the roof truce work just below the roofing felt. Our EPC rating before installing the Solar PV, battery and then the ASHP was a ‘B’ with notes indicating that Solar PV and / or Heat Pump would improve the rating.
I hope to incorporate an Evergreen Homely smart thermostat system for ASHP control as soon as a compatible device for the Daikin is available. Perhaps I should also mention that the Power Diverter is the Myenergi Eddi with a Harvi and several CT Clamps. We are using the Octopus Energy Agile and Agile Outgoing tariffs for import and export (no James Bond involvement however). 😉 Regards, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
If Homeowners are prepared to provide the information, then maybe a spreadsheet containing the following information would be of most use from the comparison, and highlighting of possible problems, point of view.
Forum Handle: @FJJ
Manufacturer: Grant
Model: HPID10R32
Type: ASHP
Arrangement: Mono
Area of Country: Warwickshire
Home Type: 3 bed detached 1970's
Size: Square Metres: 100
Insulation Level: Scale of 1 to 10 possibly? 7
Heat Loss Calculation: kW @ Amb. Temp, of: -1.1C 6.8 kW
Type of Controller: Modulating
Type of Control: Weather Compensation
System Type: Radiators (5K3, 3K2, 1K1 Stelrad compact)
Total Output of Heat Emitters: not known
Buffer Tank or Low Loss Header: LLH
Secondary Pumps: Number 1
Solar PV System: Size or No 8 kW
Power Diverter: Yes
Battery System: Size; 10Kw Solaredge Powerbank
Forum Handle: MikeFl
Manufacturer: Grant
Model: Aerona HPID10R32
Type: ASHP
Arrangement: Mono
Area of Country: Cumbria
Home Type: Dormer Bungalow
Size: Square Metres: 148
Insulation Level: 7? (Loft/eaves insulation topped up with 30mm+; Room in Roof insulation is less
Heat Loss Calculation: 9-10kW @ Amb. Temp, of: 10C (this is my calculation - hope the installer has a better one)
Type of Controller: Two zones (up/down) controlled by room thermostats, with TRVs on all but two radiators
Type of Control: Fixed flow temperate at installation, possibly.
System Type: Radiators
Total Output of Heat Emitters: K2 *3, K3 * 4, K1 * 1
Buffer Tank or Low Loss Header: Grant volumiser / LLH
Secondary Pumps: 1(Grundfos ups3 15-50)
Solar PV System: No
Power Diverter: No
Battery System: No
Water cylinder is a FlowCyl Slimline 170L (FCHPS2170) with 24kW heating coil installed.
Grant Aerona 3 10kW
Forum Handle: Madrajin
Manufacturer: Vaillant
Model: Arotherm Plus 7kw, UniTower plus, sensoComfort
Type: ASHP
Arrangement: Monoblock, high temp I think.
Area of Country: General Location
Home Type: House solid wall construction, built 1763 (uniTower located in outhouse)
Size: Square Metres: 126m2
Insulation Level: Scale of 1 to 10 possibly? Listed as energy mark D when I bought it
Heat Loss Calculation: kW @ Amb. Temp, of: ?C
Type of Controller: unknown (sensoComfort), EveThermo TRV
Type of Control: Adaptive, Weather Compensation, Flow Temperature, Room Temperature
System Type: Radiators unchanged, mostly double.
Total Output of Heat Emitters: ? kW
Buffer Tank or Low Loss Header: No
Secondary Pumps: No
Solar PV System: No
Power Diverter: No
Battery System: No
Forum Handle: GC61
Manufacturer: Viessmann
Model: Vitocal 151-A
Type: ASHP
Arrangement: Mono
Area of Country: Ireland
Home Type: 2-Storey detached
Size: 180 sqm
Insulation Level: 8
Heat Loss Calculation: 1.63
Type of Controller: Viessmann Vitotrol 300-E
Type of Control: Weather Compensation / Flow Temperature / Room Temperature
System Type: UFH and radiators
Total Output of Heat Emitters:
Buffer Tank or Low Loss Header:
Secondary Pumps:
Solar PV System: 4.2KW
Power Diverter: No
Battery System: No
Forum Handle: @dougmlancs
Manufacturer: Panasonic
Model: Aquarea L (R290)
Type: ASHP
Arrangement: Split with hydraulic connection
Area of Country: Lancashire
Home Type: Semi-detached house
Size: Square Metres: 110
Insulation Level: CWI, DG + 300mm loft
Heat Loss Calculation: 7.1kW @ Amb. Temp, of: -3C
Type of Controller: Modulating, no 3rd party thermostats, TRV’s set in bedrooms otherwise all open full
Type of Control: Weather Compensation
System Type: Radiators
Buffer Tank or Low Loss Header: No
Secondary Pumps: No
Solar PV System: 4.44 kW
Power Diverter: No
Battery System: 9.5kWh Givenergy battery
Smart Tech Specialist with Octopus Energy Services (all views my own). 4.4kW PV with 9.5kWh Givenergy battery. 9kW Panasonic Aquarea L ASHP
Forum Handle: @ajdunlop
Manufacturer: Mitsubishi
Model: Ecodan R32 8.5kW (PUZ-WM85VAA)
Type: ASHP
Arrangement: Mono
Area of Country: West Yorkshire, England
Home Type: End Terrace House
Size: Square Metres: 170m2
Insulation Level: 6/10 (Attic very well insulated, some main rooms with IWI, others not insulated yet and suspended floors not insulated yet)
Heat Loss Calculation: 7.54kW @ Amb. Temp, of: -2C (Self calculated using Heat Engineer)
Type of Controller: Ecodan FTC6 Main controller in Hallway, Smart TRVs on most Rads (set to limit overheating)
Type of Control: For 1st winter probably a mix of Weather Compensation and use of Ecodan's Auto Adaptive taking room temperature from main controller
System Type: Radiators (mix of very old P1, less old P2 and some newer K2)
Total Output of Heat Emitters: 9.863kW (@45C flow temp)
Buffer Tank or Low Loss Header: No
Secondary Pumps: No
Solar PV System: 4.4 kW (12x JA Solar 370W Panels evenly E-W Split, Inverter Fox ESS Hybrid H1-3.7-E)
Power Diverter: Yes (Soon to be installed Eddi, hopefully wired to use immersion at low overproduction and the ASHP for high overproduction)
Battery System: 5.8 kW (Fox ESS Cube CM2900 + CS2900)
Forum Handle: Crustydoodle
Manufacturer: Mitsubishi
Model: Ecodan R32 11.2kW
Type: ASHP
Arrangement: Mono
Area of Country: South East
Home Type: Detached House
Size: Square Metres: ~190
Insulation Level: Scale of 1 to 10 possibly? High
Heat Loss Calculation: 9.7 kW @ Amb. Temp, of: -2.39C
Type of Controller: FTC6 + Neomiser Thermostats in every room (11 zones)
Type of Control: Room temp I think; HW set to 50DegC and reheats when 10 below
System Type: UFH.
Total Output of Heat Emitters: Unsure - something says 19kW heat demand
Buffer Tank or Low Loss Header: None
Secondary Pumps: Not sure
Solar PV System: No
Power Diverter: No
Battery System: No
- 26 Forums
- 2,118 Topics
- 46.6 K Posts
- 23 Online
- 4,523 Members
Join Us!
Latest Posts
-
Where can I get these new frb lock shield valves?
Watched the latest homeowners qa and they mentioned som...
By AdamK , 1 hour ago
-
-
With their balancing process Im pretty sure all rads co...
By JamesPa , 3 hours ago
-
The sad end of my ECO4 installation.
This afternoon I was advised by a charity that was help...
By Dwynwen , 5 hours ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@davidalgarve It should just be recovered by both servi...
By dgclimatecontrol , 8 hours ago
-
RE: Who's your electricity provider and what's your tariff?
Aggregators have been recognised for many years, and it...
By Transparent , 9 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Great news I edited my previous post (probably af...
By JamesPa , 12 hours ago
-
RE: Double or Triple Glazed Windows?
@toodles Glad to hear things are progressing well for y...
By TRBob , 13 hours ago
-
RE: 300 Liter Tank - Do I have to heat it all?
I agree with @morgan. You can turn down the target t...
By JamesPa , 15 hours ago
-
How to waste energy (and time) playing with AI.
A friend of mine who subscribes to an AI service was ex...
By Toodles , 1 day ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@topher you’re more than welcome to, yes. I’ll send you...
By Mars , 2 days ago
-
RE: Fitting new shower valve ..........
I’ve never taken a chance when fiddling and changing ou...
By Mars , 2 days ago
-
You should contact the council and report the unsatisfa...
By JamesPa , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
I would deffo install an additional slinky run, especia...
By Transparent , 3 days ago
-
RE: Say hello and introduce yourself
@editor fab - thanks Mars, and keep up the great work o...
By normpang , 3 days ago
-
RE: Compressor and Evaporator Stratification
@trebor12345 So I think the 1st zigzag section shows so...
By ASHP-BOBBA , 3 days ago
-
RE: Is this just haze or something more?
@majordennisbloodnok I was giving a talk to primary sch...
By Toodles , 3 days ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
We had our Tesla Powerwall 3 (and Gateway) installed ea...
By Old_Scientist , 3 days ago
-
Indeed. With a battery its presumably the battery con...
By JamesPa , 4 days ago