Hi all
Has anyone adjusted their flow temperature as I hear it can produce decent savings on electricity usage?
Also, how often do others ASHP defrost cycle, particularly at night?Â
@hr_3, we dropped ours from 45C to 40C in November. Our previous COP was 2.7 and it’s now over 3, which is good. Depending on how well insulated you are, and if you’ve got UFH or big rads, you could get away with 35C.Â
As for defrosts, we’ll easily do 8-10 when temperatures drop. Humid evenings with temperatures in the 1-3C range are worst for us. Sub-zero temperatures don’t lead to as many defrosts for us because there’s typically less moisture in the air.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
I asked my installers about switching to weather compensation mode
This was their feedback:
"When we have rads and UFH working together we tend to find using the weather compensation curve is not particularly effective. It can mean that there’s low temperature water in a convective radiator panel which doesn’t provide sufficient output. Our customers with similar set ups are far happier to hit a set flow temp of 50/55 which ensures the panels convect warm air into the rooms.
You can experiment with using the weather compensation mode to see if it suits, but we would recommend just to keep the set flow temperature. Ultimately the thermostat will turn off once it’s hit the set temp so the heat pump will be operating for a shorter period of time at a slightly higher flow temperature and you’ll find little difference in the ultimate efficiency. You could try adjusting the set back temperature by a few degrees which would mean the temperature in the house is maintained.
Hope that makes sense and do come back to me if there are any further issues re. upstairs heating."
Â
I thought on a dual rad/ufh system the ASHP heated water to a single temperature; the rads got fed this directly and the ufh got it mixed with cold water because it didn't need such a high temperature? Would your supplier still be saying go for a set 50/55 if you didn't have ufh? A flow temp of 50 is right at the upper end. Â
@kev-m The installer (since sacked) who commissioned our rad only installation set flow temps to 55. Â I have set it down now to 40 and still the house remains comfortable.
I remember seeing an article or video where the installer said they set the radiators at 50C because otherwise the customers complained the heating wasn't working. Â
Posted by: @editor@hr_3, we dropped ours from 45C to 40C in November. Our previous COP was 2.7 and it’s now over 3, which is good. Depending on how well insulated you are, and if you’ve got UFH or big rads, you could get away with 35C.Â
As for defrosts, we’ll easily do 8-10 when temperatures drop. Humid evenings with temperatures in the 1-3C range are worst for us. Sub-zero temperatures don’t lead to as many defrosts for us because there’s typically less moisture in the air.
Hi Mars
Thanks, OK I think my ASHP (steibel eltron wpl17) is in line with your cop there (about 2.7)at the moment at 45c flow
I may drop to 35/40c and see outcome.
We have large k2 double convector rads, no ufh but system was installed from scratch, not retrofit so mainly 22mm pipe everywhere. System gets up to 20c no issues which for us is too hot and temperature seems to only drop below 19c after 11-12hours (on the recent colder days at 5c)
@hr_3, give it a bash - you should get a feel for temperature and efficiency within a few days.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
Rodents! A word of warning for heat pump owners
10 hours ago
-
Surface mount or bury primaries for heat pump installation?
2 months ago
-
UFH and ASHPs
3 months ago
-
Installing your own ASHP - DIY
4 months ago
-
ASHP install contract and BUS grant money
6 months ago
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 15 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Sanity check please. Battery storage and inverter sizing.
@old_scientist yes already have a 4kwp array on a vener...
By AdamK , 9 hours ago
-
RE: Rodents! A word of warning for heat pump owners
Thanks for this. My pipe insulation in my garage has...
By JamesPa , 10 hours ago
-
RE: Why so many sigenergi installer recommendations?
I've noticed lots of love for them on YouTube too - I w...
By Old_Scientist , 12 hours ago
-
@editor Something changed in this last 12 months, they ...
By ASHP-BOBBA , 13 hours ago
-
RE: Ecodan & MelCloud scheduling
I put the above question to Mitsu UK at the sme time as...
By DavidAlgarve , 22 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: EGP01 Manufacturer: Samsung Model: 8K...
By EGP01 , 2 days ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 2 days ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 2 days ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 3 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 4 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 5 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 5 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 5 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 6 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 7 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 1 week ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 1 week ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 1 week ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 1 week ago