Hi all
Has anyone adjusted their flow temperature as I hear it can produce decent savings on electricity usage?
Also, how often do others ASHP defrost cycle, particularly at night?Â
@hr_3, we dropped ours from 45C to 40C in November. Our previous COP was 2.7 and it’s now over 3, which is good. Depending on how well insulated you are, and if you’ve got UFH or big rads, you could get away with 35C.Â
As for defrosts, we’ll easily do 8-10 when temperatures drop. Humid evenings with temperatures in the 1-3C range are worst for us. Sub-zero temperatures don’t lead to as many defrosts for us because there’s typically less moisture in the air.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
I asked my installers about switching to weather compensation mode
This was their feedback:
"When we have rads and UFH working together we tend to find using the weather compensation curve is not particularly effective. It can mean that there’s low temperature water in a convective radiator panel which doesn’t provide sufficient output. Our customers with similar set ups are far happier to hit a set flow temp of 50/55 which ensures the panels convect warm air into the rooms.
You can experiment with using the weather compensation mode to see if it suits, but we would recommend just to keep the set flow temperature. Ultimately the thermostat will turn off once it’s hit the set temp so the heat pump will be operating for a shorter period of time at a slightly higher flow temperature and you’ll find little difference in the ultimate efficiency. You could try adjusting the set back temperature by a few degrees which would mean the temperature in the house is maintained.
Hope that makes sense and do come back to me if there are any further issues re. upstairs heating."
Â
I thought on a dual rad/ufh system the ASHP heated water to a single temperature; the rads got fed this directly and the ufh got it mixed with cold water because it didn't need such a high temperature? Would your supplier still be saying go for a set 50/55 if you didn't have ufh? A flow temp of 50 is right at the upper end. Â
@kev-m The installer (since sacked) who commissioned our rad only installation set flow temps to 55. Â I have set it down now to 40 and still the house remains comfortable.
I remember seeing an article or video where the installer said they set the radiators at 50C because otherwise the customers complained the heating wasn't working. Â
Posted by: @editor@hr_3, we dropped ours from 45C to 40C in November. Our previous COP was 2.7 and it’s now over 3, which is good. Depending on how well insulated you are, and if you’ve got UFH or big rads, you could get away with 35C.Â
As for defrosts, we’ll easily do 8-10 when temperatures drop. Humid evenings with temperatures in the 1-3C range are worst for us. Sub-zero temperatures don’t lead to as many defrosts for us because there’s typically less moisture in the air.
Hi Mars
Thanks, OK I think my ASHP (steibel eltron wpl17) is in line with your cop there (about 2.7)at the moment at 45c flow
I may drop to 35/40c and see outcome.
We have large k2 double convector rads, no ufh but system was installed from scratch, not retrofit so mainly 22mm pipe everywhere. System gets up to 20c no issues which for us is too hot and temperature seems to only drop below 19c after 11-12hours (on the recent colder days at 5c)
@hr_3, give it a bash - you should get a feel for temperature and efficiency within a few days.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
Rodents! A word of warning for heat pump owners
2 weeks ago
-
Surface mount or bury primaries for heat pump installation?
2 months ago
-
UFH and ASHPs
4 months ago
-
Installing your own ASHP - DIY
5 months ago
-
ASHP install contract and BUS grant money
6 months ago
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 46 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
Hi all, we've now had the heat pump moved to its final ...
By smit360 , 16 minutes ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 30 minutes ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 2 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 2 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 3 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@old_scientist, our system was royally bodged six years...
By Mars , 4 hours ago
-
@jamespa thanks, I appreciate the offer. For n...
By DREI , 17 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
I have 3 women in the house, 2 little ones, so my heati...
By DREI , 22 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 23 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 3 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 4 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 4 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 5 days ago