Hi all
Has anyone adjusted their flow temperature as I hear it can produce decent savings on electricity usage?
Also, how often do others ASHP defrost cycle, particularly at night?
@hr_3, we dropped ours from 45C to 40C in November. Our previous COP was 2.7 and it’s now over 3, which is good. Depending on how well insulated you are, and if you’ve got UFH or big rads, you could get away with 35C.
As for defrosts, we’ll easily do 8-10 when temperatures drop. Humid evenings with temperatures in the 1-3C range are worst for us. Sub-zero temperatures don’t lead to as many defrosts for us because there’s typically less moisture in the air.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
I asked my installers about switching to weather compensation mode
This was their feedback:
"When we have rads and UFH working together we tend to find using the weather compensation curve is not particularly effective. It can mean that there’s low temperature water in a convective radiator panel which doesn’t provide sufficient output. Our customers with similar set ups are far happier to hit a set flow temp of 50/55 which ensures the panels convect warm air into the rooms.
You can experiment with using the weather compensation mode to see if it suits, but we would recommend just to keep the set flow temperature. Ultimately the thermostat will turn off once it’s hit the set temp so the heat pump will be operating for a shorter period of time at a slightly higher flow temperature and you’ll find little difference in the ultimate efficiency. You could try adjusting the set back temperature by a few degrees which would mean the temperature in the house is maintained.
Hope that makes sense and do come back to me if there are any further issues re. upstairs heating."
I thought on a dual rad/ufh system the ASHP heated water to a single temperature; the rads got fed this directly and the ufh got it mixed with cold water because it didn't need such a high temperature? Would your supplier still be saying go for a set 50/55 if you didn't have ufh? A flow temp of 50 is right at the upper end.
@kev-m The installer (since sacked) who commissioned our rad only installation set flow temps to 55. I have set it down now to 40 and still the house remains comfortable.
I remember seeing an article or video where the installer said they set the radiators at 50C because otherwise the customers complained the heating wasn't working.
Posted by: @editor@hr_3, we dropped ours from 45C to 40C in November. Our previous COP was 2.7 and it’s now over 3, which is good. Depending on how well insulated you are, and if you’ve got UFH or big rads, you could get away with 35C.
As for defrosts, we’ll easily do 8-10 when temperatures drop. Humid evenings with temperatures in the 1-3C range are worst for us. Sub-zero temperatures don’t lead to as many defrosts for us because there’s typically less moisture in the air.
Hi Mars
Thanks, OK I think my ASHP (steibel eltron wpl17) is in line with your cop there (about 2.7)at the moment at 45c flow
I may drop to 35/40c and see outcome.
We have large k2 double convector rads, no ufh but system was installed from scratch, not retrofit so mainly 22mm pipe everywhere. System gets up to 20c no issues which for us is too hot and temperature seems to only drop below 19c after 11-12hours (on the recent colder days at 5c)
@hr_3, give it a bash - you should get a feel for temperature and efficiency within a few days.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
First time wall mounting an ASHP
3 hours ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 weeks ago
-
Rodents! A word of warning for heat pump owners
3 weeks ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
2 months ago
-
How to choose Towel Rails for an ASHP
2 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,275 Topics
- 50.9 K Posts
- 191 Online
- 5,936 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard Very interesting, thanks - although I hav...
By GrahamF , 51 minutes ago
-
RE: My DIY Heat Pump installation
…and I’m assuming the “more” option on the right of the...
By Majordennisbloodnok , 1 hour ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Yup, totally understand, @gmuzz. However, fitting Ope...
By Majordennisbloodnok , 1 hour ago
-
RE: Who's your electricity provider and what's your tariff?
So I’m still with E.ON Next, and I received a pretty sn...
By Mars , 2 hours ago
-
RE: Heat Loss v Outside Air Temperature
I think this can be dealt with without the need for OAT...
By JamesPa , 2 hours ago
-
RE: First time wall mounting an ASHP
what you need to do is everything you can to remove the...
By ASHP-BOBBA , 3 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Aira 12kW - @gmuzz
By Gmuzz , 3 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
ASHP switched off per specialists guidance. Seems the b...
By Crimson , 4 hours ago
-
RE: Faulty Clivet heat pump out of the box
@steveimpey that is disappointing. I am inclined to agr...
By benson , 6 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj Bear with me, this is my first post on this fo...
By KevH , 7 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Is the ZD is a bit of a marketing ploy? has the it bee...
By BWood , 11 hours ago
-
For anyone interested in levelling up their understandi...
By Mars , 12 hours ago
-
RE: Solar panels on side of house to heat water
Thankyou for the brain dump, all very worthy items. W...
By paultheheating , 12 hours ago
-
Ecodan HW temp setting set itself to 40C
This morning I noticed that the HW was lukewarm and MEL...
By downfield , 13 hours ago
-
RE: Is Your House Warmer Upstairs Than Downstairs?
I suspect its mainly that you get the views. Upstairs...
By JamesPa , 13 hours ago
-
RE: Mitsubishi Ecodan FTC7 Legionella date set
The next run date/time is determined by the settings co...
By F1p , 14 hours ago
-
@treewizard is this not the electrical pulse that keeps...
By ASHP-BOBBA , 1 day ago
-
RE: Samsung Gen6 and Havenwise ........
I am no expert on this but on your gen 6 controller onc...
By Alfapat , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk these are called roll top rads, they were still ...
By AgentGeorge , 2 days ago
-
If the Vaillant is a 7kw unit I’d avoid. Quiet outside ...
By AdamK , 2 days ago