Hi all
Has anyone adjusted their flow temperature as I hear it can produce decent savings on electricity usage?
Also, how often do others ASHP defrost cycle, particularly at night?Â
@hr_3, we dropped ours from 45C to 40C in November. Our previous COP was 2.7 and it’s now over 3, which is good. Depending on how well insulated you are, and if you’ve got UFH or big rads, you could get away with 35C.Â
As for defrosts, we’ll easily do 8-10 when temperatures drop. Humid evenings with temperatures in the 1-3C range are worst for us. Sub-zero temperatures don’t lead to as many defrosts for us because there’s typically less moisture in the air.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
I asked my installers about switching to weather compensation mode
This was their feedback:
"When we have rads and UFH working together we tend to find using the weather compensation curve is not particularly effective. It can mean that there’s low temperature water in a convective radiator panel which doesn’t provide sufficient output. Our customers with similar set ups are far happier to hit a set flow temp of 50/55 which ensures the panels convect warm air into the rooms.
You can experiment with using the weather compensation mode to see if it suits, but we would recommend just to keep the set flow temperature. Ultimately the thermostat will turn off once it’s hit the set temp so the heat pump will be operating for a shorter period of time at a slightly higher flow temperature and you’ll find little difference in the ultimate efficiency. You could try adjusting the set back temperature by a few degrees which would mean the temperature in the house is maintained.
Hope that makes sense and do come back to me if there are any further issues re. upstairs heating."
Â
I thought on a dual rad/ufh system the ASHP heated water to a single temperature; the rads got fed this directly and the ufh got it mixed with cold water because it didn't need such a high temperature? Would your supplier still be saying go for a set 50/55 if you didn't have ufh? A flow temp of 50 is right at the upper end. Â
@kev-m The installer (since sacked) who commissioned our rad only installation set flow temps to 55. Â I have set it down now to 40 and still the house remains comfortable.
I remember seeing an article or video where the installer said they set the radiators at 50C because otherwise the customers complained the heating wasn't working. Â
Posted by: @editor@hr_3, we dropped ours from 45C to 40C in November. Our previous COP was 2.7 and it’s now over 3, which is good. Depending on how well insulated you are, and if you’ve got UFH or big rads, you could get away with 35C.Â
As for defrosts, we’ll easily do 8-10 when temperatures drop. Humid evenings with temperatures in the 1-3C range are worst for us. Sub-zero temperatures don’t lead to as many defrosts for us because there’s typically less moisture in the air.
Hi Mars
Thanks, OK I think my ASHP (steibel eltron wpl17) is in line with your cop there (about 2.7)at the moment at 45c flow
I may drop to 35/40c and see outcome.
We have large k2 double convector rads, no ufh but system was installed from scratch, not retrofit so mainly 22mm pipe everywhere. System gets up to 20c no issues which for us is too hot and temperature seems to only drop below 19c after 11-12hours (on the recent colder days at 5c)
@hr_3, give it a bash - you should get a feel for temperature and efficiency within a few days.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 days ago
-
Rodents! A word of warning for heat pump owners
1 week ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
2 weeks ago
-
How to choose Towel Rails for an ASHP
2 weeks ago
-
How to Zone with a Single Room with UFH
2 weeks ago
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 83 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: 4 Year Ongoing Heat Pump Battle With Poor Heat Pump Installation
It's unbelievable isn't it the extent to which some peo...
By JamesPa , 21 minutes ago
-
RE: Renewables & Heat Pumps in the News
I'm still going through the latest ENTSO-E report on th...
By Transparent , 1 hour ago
-
@editor The season to start inviting prospectives to ‘V...
By Toodles , 2 hours ago
-
@bontwoody how long has it been now since you started t...
By Mars , 2 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Yes, over the last few days I've been keeping a very cl...
By Steelbadger , 2 hours ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
@lch07 it's frightening just how many of these guys jus...
By Mars , 3 hours ago
-
Absolutely. I am one of those members and I most certai...
By Majordennisbloodnok , 3 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@darrell-p There's another new Forum Member, @wully who...
By Transparent , 3 hours ago
-
RE: Forum updates, announcements & issues
We've had a slight glitch with our security software fo...
By Mars , 6 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
Er...no comment!
By JamesPa , 7 hours ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
If you do suggest you consider repurposing it as a 2 po...
By JamesPa , 18 hours ago
-
RE: Say hello and introduce yourself
Fully agree with @cathoderay. My journey took 2 years ...
By JamesPa , 19 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
Tim, Yes ChatGPT thought I could get another...
By Mike Patrick , 1 day ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
No problem, @richdorm; glad it helps.
By Majordennisbloodnok , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
If that makes you feel happier then go ahead, but it wo...
By JamesPa , 1 day ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I do already have the same basic setup, all room influe...
By cathodeRay , 1 day ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK. You dont say whether it is from the feeds to/from ...
By JamesPa , 1 day ago
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
Yes, and probably also Adia although the latter has a m...
By JamesPa , 2 days ago