Good morning all,
After months of problems and complaints, I finally have a formal report from LG categorically stating that our 9kw heat pump is undersized for our 2700 sqft home - which is why we cannot heat the rooms in weather with temperatures below 4° and why the pump is so horribly noisy in those conditions as it is under significant strain and working at full capacity 24/7 to try to do so.
This is fantastic progress, but what now? I'm about to approach the developer who built my new build property, but does anyone have any advice or knowledge of laws concerning sufficient heating systems? I need to make sure the builder and Omnie, who designed the underpowered system and have always maintained there's nothing wrong with it (although could never explain why my home wouldn't heat above 16.5° all winter) have no wriggle room and recognise their legal obligations.
Do I need to engage a solicitor? What should I do in the first instance?
Help!
Sam.
Sam,
do you know if RHI is being claimed by the developer (I assume it isn't by you)? If so they would have to have filled in an MCI calculation and submitted it to OFGEM. That should ensure the sizing is correct. It'd be worth asking them for this or anything else they used to size the system.
Kev
Have LG confirmed what size ASHP is suitable?
Do you have access to the system data showing flow rates/temps etc? It would be interesting to see the flow temp when the ambient temp is sub 4 degrees to see when every zone is calling for heat what it is actually flowing at.
If I switch on every single zone/radiator on our system it will only flow at 37-40 max. Is your property all radiators or a mix of UFH and radiators?
Mitsubishi Ecodan 14kw ASHP + 500l Cylinder
@kev-m, do you know if there's a way of searching the MCS database?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi Sam,
As suggested previously, have you been in touch with trading standards or consumer protection? They would probably be able to point you in the correct direction.
You should also get in touch with MCS, their helpline number is 0333 103 8130.
Personally I would not go down the route of getting a solicitor just yet, keep that as a last resort.
Your local MP may also be of assistance, since the government want us all go 'green'.
Hope this helps.
Regards,
Derek.
@derek-m, I completely agree with you. The first point of attack would be MCS, but the only thing I'm unsure of (which I think Sam informed me of) is that the installers weren't MCS accredited. If they're not, there's not much recourse there. Sam can correct me if I've remembered this incorrectly. A phone call should clarify this. Also, if they were MCS accredited, there'll be insurance in play which Sam can use to get the matter resolved. Our MCS certificate states that we're insured by HEIS, and they'll put right any problems.
Trading standards and consumer protection is also a good course of action to pursue as a next step.
The solicitors play is a last resort in most cases, because of the money involved, but negligence and incompetence shouldn't be that difficult to prove, given that LG have now issued a formal report stating the incorrect size heat pump was installed.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
A quick looks suggests the MCS data is available but you need to ask for a login
Hi,
Mars, unfortunately you are correct. We do not have an MCS certificate. I've been advised to contact the builder with the report quoting the 2015 consumer rights act.
I suppose my main concern is that Omnie will simply write a report stating it is big enough.
Sam
I don't know about the flow data, although the technician has attached a data report that will hopefully mean something to the right people.
It's all underfloor heating and he's recommended a UN3 CHASSIS 12-16KW 1Ph.
He has calculated a heat loss of 8.61kw based on 0.035kw/m2 , leaving only a heating capacity of .39kw
@sam, I would demand the heat loss and emitter calculation from Omnie. If they say that the heat pump is the correct size, they must provide the evidence to back that up, and the only way to do that is to share the aforementioned calculations.
I can't remember if you told me this, but have you called MCS and verified from them that there isn't a MCS certificate for your property?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @samI don't know about the flow data, although the technician has attached a data report that will hopefully mean something to the right people.
It's all underfloor heating and he's recommended a UN3 CHASSIS 12-16KW 1Ph.
He has calculated a heat loss of 8.61kw based on 0.035kw/m2 , leaving only a heating capacity of .39kw
I missed this earlier comment. Is the calculation from the LG technician, not Omnie?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
Surface mount or bury primaries for heat pump installation?
33 minutes ago
-
UFH and ASHPs
1 month ago
-
Installing your own ASHP - DIY
2 months ago
-
ASHP install contract and BUS grant money
4 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
4 months ago
Currently viewing this topic 1 guest.
- 22 Forums
- 2,090 Topics
- 46.1 K Posts
- 30 Online
- 3,383 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Surface mount or bury primaries for heat pump installation?
What about those pipes that include conduits for electr...
By tomasmcguinness , 33 minutes ago
-
RE: Say hello and introduce yourself
Welcome You have already done the most important thin...
By JamesPa , 38 minutes ago
-
RE: Weather compensated secondary circuits with Biomass
If anyone’s going to know the answer to this it’s @sune...
By Mars , 3 hours ago
-
RE: Commencing on an ASHP Installation Process
That outside pipework would concern me. Surely rigid se...
By benson , 15 hours ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 18 hours ago
-
RE: Adding battery storage to SolarEdge PV system
Sadly I fear that they may well be right to do so. ...
By JamesPa , 20 hours ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 2 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 2 days ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
@m1kegibson If you are able to access the service me...
By HarriUp , 2 days ago
-
RE: When will heat pumps and install prices come down?
... which of course is impossible because the world mov...
By JamesPa , 2 days ago
-
My advice is reject unless they will delete the buffer ...
By JamesPa , 3 days ago
-
RE: Battery storage to run Heat Pump.
I would be surprised if the battery chemistry is going ...
By Transparent , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@dowallydrifter OK. I would recommend you read t...
By JamesPa , 4 days ago
-
RE: Solar to power Heat Pump for DHW
Wow, how big is your heat pump that it is pulling 6kW d...
By Old_Scientist , 4 days ago