Posted by: @editorPosted by: @heacolHere is a picture from one of my customenrs controllers, taken today, the external temperature is 3 Deg C and the house is 21 Deg C. The system is piped and controlled exactly as I have described above. COP of 7.4.
@heacol, that is the highest COP I have ever seen registered from any user in the UK. Is this a Panasonic air to water unit and what is the model because that is extremely impressive indeed.
Mars, this is not exceptional, it is normal. Yours could be similar to this if you listened to me. I thought I would post some evidence as I could clearly see I was being ignored.
Posted by: @heacolPosted by: @editorPosted by: @heacolHere is a picture from one of my customenrs controllers, taken today, the external temperature is 3 Deg C and the house is 21 Deg C. The system is piped and controlled exactly as I have described above. COP of 7.4.
@heacol, that is the highest COP I have ever seen registered from any user in the UK. Is this a Panasonic air to water unit and what is the model because that is extremely impressive indeed.
Mars, this is not exceptional, it is normal. Yours could be similar to this if you listened to me. I thought I would post some evidence as I could clearly see I was being ignored.
@heacool
You aren't being ignored. It's very difficult having found a installer, which isn't easy in itself, it's very difficult to then argue with said installer and demand he installs as per your design and not his. Surely the installer simply walks away. I moved in here to my present address that had no CH in February. It was absolutely freezing. We could not have gone through that again for a full winter. So we have what we have even if the system will require changes to make it better in the future. So, no, you aren't being ignored. It is what it is.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@heacol, I struggle to see how our heat pump could run at a COP of over 7 as the pump’s badge states a maximum of 4.76.
Maybe you can correct me, but most (if not all) off-the-shelf heat pumps will deliver maximum COPs in the 4s. What are the ratings for the Panasonic heat pump you’ve used in this installation? Is it marketed at delivering COPs in excess of 7?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor I decided to do a bit of maths here as this claim also bothers me. So here we go and hopefully I haven't messed this up somehow.
COP = [1/ eff] = 7.4
solving for eff we get eff = 0.135135
3 degrees is 276.15 Kelvin so we can now solve the unknown flow temperature using the formula 1 - [ 276.15 / x ] = 0.135135
Solving for x we get the unknow flow temperature as 319 kelvin, or 46.55 degrees centigrade
So the claim is that 3 degrees ambient at 46.5 degrees flow is working on a COP at 7.4. This isn't impossible, the maximum theoretical COP for 3 degrees and 21 degrees is 16.3 [294.15 / (294.15 / 276.15) = 16.3]
Posted by: @batalto@editor I decided to do a bit of maths here as this claim also bothers me. So here we go and hopefully I haven't messed this up somehow.
COP = [1/ eff] = 7.4
solving for eff we get eff = 0.135135
3 degrees is 276.15 Kelvin so we can now solve the unknown flow temperature using the formula 1 - [ 276.15 / x ] = 0.135135
Solving for x we get the unknow flow temperature as 319 kelvin, or 46.55 degrees centigrade
So the claim is that 3 degrees ambient at 46.5 degrees flow is working on a COP at 7.4. This isn't impossible, the maximum theoretical COP for 3 degrees and 21 degrees is 16.3 [294.15 / (294.15 / 276.15) = 16.3]
Batalto,
I'm afraid I find your maths very confusing. If you look at the table for your heat pump, that you provided, you will see that the manufacturer states that the anticipated COP value at an outdoor temperature of 3C and water flow temperature of 46.55C would be in the region of 3.
To consistently produce a COP value of 7.4, would require the water flow temperature to be in the region of 25C.
@derek-m its not my heat pump, so I wanted to see what was possible using just raw physics. Like I said, its theoretically possible to get that COP, but it seems very high without low flow temperatures. Ultimately heat pumps are limited in their efficiency by the refrigerant they use and its ability to boil under a certain pressure/temperature. If Heacol can achieve those COPs then he is 100% doing something right and we should all be listening. But I would very much like to know all the details of a system before I believe a claim of 7.4 COP at 3 degrees ambient.
@heacol, it's not about ignoring your experience or insights. What you have to take into consideration is that you are a professional and this is what you do for a living. Most heat pump installations in the UK have a buffer tank, so saying that we should bypass the buffer tank is a huge deal and it's daunting to most homeowners in the UK, us included. It's not something that can be DIYed in a morning because the pipework on our system is complex.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
As an Instrumentation and Control Systems Engineer, my career has been spent ensuring that the correct information is being supplied to the control systems and operators.
Based on the data supplied by ASHP manufacturers, for an ASHP to produce a COP of 7.4 would require a water flow temperature of 30C at an ambient air temperature of approximately 15C. For each kW of electrical energy used the heat pump would need to extract 6 kW of energy from the outside air, which becomes more and more difficult at low ambient air temperatures.
It is the laws of Physics and Thermodynamics, energy cannot be created or destroyed, it can only be changed in form.
@editor Hi, The figure you see in the plate is a figure based on lab test results and bears no resemblance to real life performance figgures what spo ever, you unit will get a COP of arround 115 in the summer and arround 2 at the peak of whinter. The COP figures do not take de-frost in to account and if you fun your system flat out like you do, all the time this will sunstantually reduce your COP, I have seen daily avsrage COP levels on Mitsubushi units below 1.
Here is the spwcf for the 12 Kw unit installed.
@batalto, thanks for the doing maths, which is not my strongest point.
Heat pump manufacturers must provide data that shows the pump's performance at different temperatures and flow rates. I'm sure you can achieve high COPs with low flow rates (as you've stated). So it comes down to insulation. If my house is passivhaus standard, I can get away with 25C flow rate. But most houses are not that well insulated so we need to run at 35-45C. Brendon says there's nothing special about the house in Glasgow that he installed the system in, so I don't see how you'd get away with a really flow rate.
I've also not seen any heat pumps on the UK market that make a COP claim of 7 at 3C ambient. If this COP can simply be achieved with any heat pump by simply bypassing the buffer tank and disabling all thermostats and TRVs, then the UK installation industry has a lot to answer for because they will have installed hundreds of thousands of heat pumps incorrectly.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@derek-m You are wrong, there are a lot more peramiters involved than you think, the inverter system running at low load is increadably efficient as the collector can be up to 6 times larger than at peak. All measurements are done at peak. In addition,the inverter it'self can reduce efficiency by up to 60 % from most efficient point to worst (just like an engine as it goes up the rev rainge).
The manufacturers do not give you this data, I have spent many years working it out in rela life scenarios to get the best possible output and performance for my customers.
-
Where has Watson gone?
4 weeks ago
-
First time wall mounting an ASHP
1 month ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 months ago
-
Rodents! A word of warning for heat pump owners
2 months ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
3 months ago
- 26 Forums
- 2,356 Topics
- 53.4 K Posts
- 363 Online
- 6,017 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj Seeing they deleted both threads with the pict...
By HarrisonC , 6 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@mars I think your commentary is very fair and balanc...
By JamesPa , 7 hours ago
-
RE: External pipework insulation
That's great advice @transparent... thank you. @david...
By Mars , 7 hours ago
-
RE: Advice on internal circulation pump noise
Thanks @mikefl - I'll maybe have a look at the lock-shi...
By jtg , 8 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@toodles interesting suggestion, thanks. I will try to...
By GrahamF , 9 hours ago
-
RE: Mitsubishi Ecodan Auto Adaption trial to stop cycling.
The interval you talk of, i think, will be 60min for an...
By F1p , 12 hours ago
-
RE: Electricity price predictions
Does anyone have a current graphic, visual or breakdown...
By Mars , 16 hours ago
-
Agree with @majordennisbloodnok on the setbacks. We hav...
By ChandyKris , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
It is a matter of luck. 2ith Fogstar "instructions", to...
By Batpred , 1 day ago
-
RE: Speedcomfort radiator fans
@deltona the way the links were added broke the page. A...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
I agree! Even more so if we get an answer! But the chal...
By cathodeRay , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
This has been delayed from what I believe to be this ye...
By dgclimatecontrol , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
this is why I provided current flow temperatures in the...
By ksim , 2 days ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
There's many homes that would be quite a disruption for...
By dgclimatecontrol , 2 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@rhh2348 ...maybe this option is what you want? Alter...
By benson , 2 days ago
-
RE: Free Ecoheat Heat Pump Install
@old_scientist This does make the unit smaller as the b...
By dgclimatecontrol , 2 days ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
@old_scientist hiya mate, did you ever get to the botto...
By 9jwr9 , 2 days ago
-
RE: Configuring third party dongle for Ecodan local control
@majordennisbloodnok I think the HPDHD diagnosis may be...
By Sheriff Fatman , 2 days ago