Posted by: @editorPosted by: @heacolHere is a picture from one of my customenrs controllers, taken today, the external temperature is 3 Deg C and the house is 21 Deg C. The system is piped and controlled exactly as I have described above. COP of 7.4.
@heacol, that is the highest COP I have ever seen registered from any user in the UK. Is this a Panasonic air to water unit and what is the model because that is extremely impressive indeed.
Mars, this is not exceptional, it is normal. Yours could be similar to this if you listened to me. I thought I would post some evidence as I could clearly see I was being ignored.
Posted by: @heacolPosted by: @editorPosted by: @heacolHere is a picture from one of my customenrs controllers, taken today, the external temperature is 3 Deg C and the house is 21 Deg C. The system is piped and controlled exactly as I have described above. COP of 7.4.
@heacol, that is the highest COP I have ever seen registered from any user in the UK. Is this a Panasonic air to water unit and what is the model because that is extremely impressive indeed.
Mars, this is not exceptional, it is normal. Yours could be similar to this if you listened to me. I thought I would post some evidence as I could clearly see I was being ignored.
@heacool
You aren't being ignored. It's very difficult having found a installer, which isn't easy in itself, it's very difficult to then argue with said installer and demand he installs as per your design and not his. Surely the installer simply walks away. I moved in here to my present address that had no CH in February. It was absolutely freezing. We could not have gone through that again for a full winter. So we have what we have even if the system will require changes to make it better in the future. So, no, you aren't being ignored. It is what it is.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@heacol, I struggle to see how our heat pump could run at a COP of over 7 as the pump’s badge states a maximum of 4.76.
Maybe you can correct me, but most (if not all) off-the-shelf heat pumps will deliver maximum COPs in the 4s. What are the ratings for the Panasonic heat pump you’ve used in this installation? Is it marketed at delivering COPs in excess of 7?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor I decided to do a bit of maths here as this claim also bothers me. So here we go and hopefully I haven't messed this up somehow.
COP = [1/ eff] = 7.4
solving for eff we get eff = 0.135135
3 degrees is 276.15 Kelvin so we can now solve the unknown flow temperature using the formula 1 - [ 276.15 / x ] = 0.135135
Solving for x we get the unknow flow temperature as 319 kelvin, or 46.55 degrees centigrade
So the claim is that 3 degrees ambient at 46.5 degrees flow is working on a COP at 7.4. This isn't impossible, the maximum theoretical COP for 3 degrees and 21 degrees is 16.3 [294.15 / (294.15 / 276.15) = 16.3]
Posted by: @batalto@editor I decided to do a bit of maths here as this claim also bothers me. So here we go and hopefully I haven't messed this up somehow.
COP = [1/ eff] = 7.4
solving for eff we get eff = 0.135135
3 degrees is 276.15 Kelvin so we can now solve the unknown flow temperature using the formula 1 - [ 276.15 / x ] = 0.135135
Solving for x we get the unknow flow temperature as 319 kelvin, or 46.55 degrees centigrade
So the claim is that 3 degrees ambient at 46.5 degrees flow is working on a COP at 7.4. This isn't impossible, the maximum theoretical COP for 3 degrees and 21 degrees is 16.3 [294.15 / (294.15 / 276.15) = 16.3]
Batalto,
I'm afraid I find your maths very confusing. If you look at the table for your heat pump, that you provided, you will see that the manufacturer states that the anticipated COP value at an outdoor temperature of 3C and water flow temperature of 46.55C would be in the region of 3.
To consistently produce a COP value of 7.4, would require the water flow temperature to be in the region of 25C.
@derek-m its not my heat pump, so I wanted to see what was possible using just raw physics. Like I said, its theoretically possible to get that COP, but it seems very high without low flow temperatures. Ultimately heat pumps are limited in their efficiency by the refrigerant they use and its ability to boil under a certain pressure/temperature. If Heacol can achieve those COPs then he is 100% doing something right and we should all be listening. But I would very much like to know all the details of a system before I believe a claim of 7.4 COP at 3 degrees ambient.
@heacol, it's not about ignoring your experience or insights. What you have to take into consideration is that you are a professional and this is what you do for a living. Most heat pump installations in the UK have a buffer tank, so saying that we should bypass the buffer tank is a huge deal and it's daunting to most homeowners in the UK, us included. It's not something that can be DIYed in a morning because the pipework on our system is complex.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
As an Instrumentation and Control Systems Engineer, my career has been spent ensuring that the correct information is being supplied to the control systems and operators.
Based on the data supplied by ASHP manufacturers, for an ASHP to produce a COP of 7.4 would require a water flow temperature of 30C at an ambient air temperature of approximately 15C. For each kW of electrical energy used the heat pump would need to extract 6 kW of energy from the outside air, which becomes more and more difficult at low ambient air temperatures.
It is the laws of Physics and Thermodynamics, energy cannot be created or destroyed, it can only be changed in form.
@editor Hi, The figure you see in the plate is a figure based on lab test results and bears no resemblance to real life performance figgures what spo ever, you unit will get a COP of arround 115 in the summer and arround 2 at the peak of whinter. The COP figures do not take de-frost in to account and if you fun your system flat out like you do, all the time this will sunstantually reduce your COP, I have seen daily avsrage COP levels on Mitsubushi units below 1.
Here is the spwcf for the 12 Kw unit installed.
@batalto, thanks for the doing maths, which is not my strongest point.
Heat pump manufacturers must provide data that shows the pump's performance at different temperatures and flow rates. I'm sure you can achieve high COPs with low flow rates (as you've stated). So it comes down to insulation. If my house is passivhaus standard, I can get away with 25C flow rate. But most houses are not that well insulated so we need to run at 35-45C. Brendon says there's nothing special about the house in Glasgow that he installed the system in, so I don't see how you'd get away with a really flow rate.
I've also not seen any heat pumps on the UK market that make a COP claim of 7 at 3C ambient. If this COP can simply be achieved with any heat pump by simply bypassing the buffer tank and disabling all thermostats and TRVs, then the UK installation industry has a lot to answer for because they will have installed hundreds of thousands of heat pumps incorrectly.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@derek-m You are wrong, there are a lot more peramiters involved than you think, the inverter system running at low load is increadably efficient as the collector can be up to 6 times larger than at peak. All measurements are done at peak. In addition,the inverter it'self can reduce efficiency by up to 60 % from most efficient point to worst (just like an engine as it goes up the rev rainge).
The manufacturers do not give you this data, I have spent many years working it out in rela life scenarios to get the best possible output and performance for my customers.
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
22 hours ago
-
Rodents! A word of warning for heat pump owners
3 weeks ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
1 month ago
-
Running my new Nibe ASHP efficiently
1 month ago
-
Weather compensation- why you should use it
1 month ago
Currently viewing this topic 1 guest.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 217 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Electricity price predictions
@transparent Triggered by the various commen...
By JamesPa , 17 minutes ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 47 minutes ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 53 minutes ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 1 hour ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
I've found that generally the humidity in the house is ...
By IRMartini , 1 hour ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 2 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 5 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 6 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 17 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 19 hours ago
-
RE: Setback savings - fact or fiction?
I also need to correct something I said by mistake earl...
By cathodeRay , 19 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 22 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 22 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 22 hours ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 24 hours ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago