Posted by: @editorPosted by: @heacolHere is a picture from one of my customenrs controllers, taken today, the external temperature is 3 Deg C and the house is 21 Deg C. The system is piped and controlled exactly as I have described above. COP of 7.4.
@heacol, that is the highest COP I have ever seen registered from any user in the UK. Is this a Panasonic air to water unit and what is the model because that is extremely impressive indeed.
Mars, this is not exceptional, it is normal. Yours could be similar to this if you listened to me. I thought I would post some evidence as I could clearly see I was being ignored.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @heacolPosted by: @editorPosted by: @heacolHere is a picture from one of my customenrs controllers, taken today, the external temperature is 3 Deg C and the house is 21 Deg C. The system is piped and controlled exactly as I have described above. COP of 7.4.
@heacol, that is the highest COP I have ever seen registered from any user in the UK. Is this a Panasonic air to water unit and what is the model because that is extremely impressive indeed.
Mars, this is not exceptional, it is normal. Yours could be similar to this if you listened to me. I thought I would post some evidence as I could clearly see I was being ignored.
@heacool
You aren't being ignored. It's very difficult having found a installer, which isn't easy in itself, it's very difficult to then argue with said installer and demand he installs as per your design and not his. Surely the installer simply walks away. I moved in here to my present address that had no CH in February. It was absolutely freezing. We could not have gone through that again for a full winter. So we have what we have even if the system will require changes to make it better in the future. So, no, you aren't being ignored. It is what it is.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@heacol, I struggle to see how our heat pump could run at a COP of over 7 as the pump’s badge states a maximum of 4.76.
Maybe you can correct me, but most (if not all) off-the-shelf heat pumps will deliver maximum COPs in the 4s. What are the ratings for the Panasonic heat pump you’ve used in this installation? Is it marketed at delivering COPs in excess of 7?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor I decided to do a bit of maths here as this claim also bothers me. So here we go and hopefully I haven't messed this up somehow.
COP = [1/ eff] = 7.4
solving for eff we get eff = 0.135135
3 degrees is 276.15 Kelvin so we can now solve the unknown flow temperature using the formula 1 - [ 276.15 / x ] = 0.135135
Solving for x we get the unknow flow temperature as 319 kelvin, or 46.55 degrees centigrade
So the claim is that 3 degrees ambient at 46.5 degrees flow is working on a COP at 7.4. This isn't impossible, the maximum theoretical COP for 3 degrees and 21 degrees is 16.3 [294.15 / (294.15 / 276.15) = 16.3]
Posted by: @batalto@editor I decided to do a bit of maths here as this claim also bothers me. So here we go and hopefully I haven't messed this up somehow.
COP = [1/ eff] = 7.4
solving for eff we get eff = 0.135135
3 degrees is 276.15 Kelvin so we can now solve the unknown flow temperature using the formula 1 - [ 276.15 / x ] = 0.135135
Solving for x we get the unknow flow temperature as 319 kelvin, or 46.55 degrees centigrade
So the claim is that 3 degrees ambient at 46.5 degrees flow is working on a COP at 7.4. This isn't impossible, the maximum theoretical COP for 3 degrees and 21 degrees is 16.3 [294.15 / (294.15 / 276.15) = 16.3]
Batalto,
I'm afraid I find your maths very confusing. If you look at the table for your heat pump, that you provided, you will see that the manufacturer states that the anticipated COP value at an outdoor temperature of 3C and water flow temperature of 46.55C would be in the region of 3.
To consistently produce a COP value of 7.4, would require the water flow temperature to be in the region of 25C.
@derek-m its not my heat pump, so I wanted to see what was possible using just raw physics. Like I said, its theoretically possible to get that COP, but it seems very high without low flow temperatures. Ultimately heat pumps are limited in their efficiency by the refrigerant they use and its ability to boil under a certain pressure/temperature. If Heacol can achieve those COPs then he is 100% doing something right and we should all be listening. But I would very much like to know all the details of a system before I believe a claim of 7.4 COP at 3 degrees ambient.
@heacol, it's not about ignoring your experience or insights. What you have to take into consideration is that you are a professional and this is what you do for a living. Most heat pump installations in the UK have a buffer tank, so saying that we should bypass the buffer tank is a huge deal and it's daunting to most homeowners in the UK, us included. It's not something that can be DIYed in a morning because the pipework on our system is complex.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
As an Instrumentation and Control Systems Engineer, my career has been spent ensuring that the correct information is being supplied to the control systems and operators.
Based on the data supplied by ASHP manufacturers, for an ASHP to produce a COP of 7.4 would require a water flow temperature of 30C at an ambient air temperature of approximately 15C. For each kW of electrical energy used the heat pump would need to extract 6 kW of energy from the outside air, which becomes more and more difficult at low ambient air temperatures.
It is the laws of Physics and Thermodynamics, energy cannot be created or destroyed, it can only be changed in form.
@editor Hi, The figure you see in the plate is a figure based on lab test results and bears no resemblance to real life performance figgures what spo ever, you unit will get a COP of arround 115 in the summer and arround 2 at the peak of whinter. The COP figures do not take de-frost in to account and if you fun your system flat out like you do, all the time this will sunstantually reduce your COP, I have seen daily avsrage COP levels on Mitsubushi units below 1.
Here is the spwcf for the 12 Kw unit installed.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@batalto, thanks for the doing maths, which is not my strongest point.
Heat pump manufacturers must provide data that shows the pump's performance at different temperatures and flow rates. I'm sure you can achieve high COPs with low flow rates (as you've stated). So it comes down to insulation. If my house is passivhaus standard, I can get away with 25C flow rate. But most houses are not that well insulated so we need to run at 35-45C. Brendon says there's nothing special about the house in Glasgow that he installed the system in, so I don't see how you'd get away with a really flow rate.
I've also not seen any heat pumps on the UK market that make a COP claim of 7 at 3C ambient. If this COP can simply be achieved with any heat pump by simply bypassing the buffer tank and disabling all thermostats and TRVs, then the UK installation industry has a lot to answer for because they will have installed hundreds of thousands of heat pumps incorrectly.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@derek-m You are wrong, there are a lot more peramiters involved than you think, the inverter system running at low load is increadably efficient as the collector can be up to 6 times larger than at peak. All measurements are done at peak. In addition,the inverter it'self can reduce efficiency by up to 60 % from most efficient point to worst (just like an engine as it goes up the rev rainge).
The manufacturers do not give you this data, I have spent many years working it out in rela life scenarios to get the best possible output and performance for my customers.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@batalto Not as simple as that, you have left out most of the variables.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
Installing your own ASHP - DIY
3 weeks ago
-
ASHP install contract and BUS grant money
2 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
2 months ago
-
Savings - using Weather Compensation & Time of Use Tariffs
3 months ago
-
Heat Pump starting current
3 months ago
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 27 Online
- 3,312 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Advice for ground source heat pump in new build with PV and batteries
@johnmo no external air supply, just the room air. We ...
By Judith , 5 minutes ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@heatgeek Nibe also promote the two pipe buffer, I use ...
By Damon Blakemore , 45 minutes ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Well my switch from eon is tomorrow/Monday so I’ll soon...
By Westkent , 4 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 7 hours ago
-
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@johnmo I have been looking at the daily Agile rates fo...
By Toodles , 10 hours ago
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 11 hours ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 20 hours ago
-
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 2 days ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 2 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 3 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 3 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 4 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 4 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 4 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 5 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 5 days ago