Good morning all,
After months of problems and complaints, I finally have a formal report from LG categorically stating that our 9kw heat pump is undersized for our 2700 sqft home - which is why we cannot heat the rooms in weather with temperatures below 4° and why the pump is so horribly noisy in those conditions as it is under significant strain and working at full capacity 24/7 to try to do so.
This is fantastic progress, but what now? I'm about to approach the developer who built my new build property, but does anyone have any advice or knowledge of laws concerning sufficient heating systems? I need to make sure the builder and Omnie, who designed the underpowered system and have always maintained there's nothing wrong with it (although could never explain why my home wouldn't heat above 16.5° all winter) have no wriggle room and recognise their legal obligations.
Do I need to engage a solicitor? What should I do in the first instance?
Help!
Sam.
Sam,
do you know if RHI is being claimed by the developer (I assume it isn't by you)? If so they would have to have filled in an MCI calculation and submitted it to OFGEM. That should ensure the sizing is correct. It'd be worth asking them for this or anything else they used to size the system.
Kev
Have LG confirmed what size ASHP is suitable?
Do you have access to the system data showing flow rates/temps etc? It would be interesting to see the flow temp when the ambient temp is sub 4 degrees to see when every zone is calling for heat what it is actually flowing at.
If I switch on every single zone/radiator on our system it will only flow at 37-40 max. Is your property all radiators or a mix of UFH and radiators?
Mitsubishi Ecodan 14kw ASHP + 500l Cylinder
@kev-m, do you know if there's a way of searching the MCS database?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi Sam,
As suggested previously, have you been in touch with trading standards or consumer protection? They would probably be able to point you in the correct direction.
You should also get in touch with MCS, their helpline number is 0333 103 8130.
Personally I would not go down the route of getting a solicitor just yet, keep that as a last resort.
Your local MP may also be of assistance, since the government want us all go 'green'.
Hope this helps.
Regards,
Derek.
@derek-m, I completely agree with you. The first point of attack would be MCS, but the only thing I'm unsure of (which I think Sam informed me of) is that the installers weren't MCS accredited. If they're not, there's not much recourse there. Sam can correct me if I've remembered this incorrectly. A phone call should clarify this. Also, if they were MCS accredited, there'll be insurance in play which Sam can use to get the matter resolved. Our MCS certificate states that we're insured by HEIS, and they'll put right any problems.
Trading standards and consumer protection is also a good course of action to pursue as a next step.
The solicitors play is a last resort in most cases, because of the money involved, but negligence and incompetence shouldn't be that difficult to prove, given that LG have now issued a formal report stating the incorrect size heat pump was installed.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
A quick looks suggests the MCS data is available but you need to ask for a login
Hi,
Mars, unfortunately you are correct. We do not have an MCS certificate. I've been advised to contact the builder with the report quoting the 2015 consumer rights act.
I suppose my main concern is that Omnie will simply write a report stating it is big enough.
Sam
I don't know about the flow data, although the technician has attached a data report that will hopefully mean something to the right people.
It's all underfloor heating and he's recommended a UN3 CHASSIS 12-16KW 1Ph.
He has calculated a heat loss of 8.61kw based on 0.035kw/m2 , leaving only a heating capacity of .39kw
@sam, I would demand the heat loss and emitter calculation from Omnie. If they say that the heat pump is the correct size, they must provide the evidence to back that up, and the only way to do that is to share the aforementioned calculations.
I can't remember if you told me this, but have you called MCS and verified from them that there isn't a MCS certificate for your property?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @samI don't know about the flow data, although the technician has attached a data report that will hopefully mean something to the right people.
It's all underfloor heating and he's recommended a UN3 CHASSIS 12-16KW 1Ph.
He has calculated a heat loss of 8.61kw based on 0.035kw/m2 , leaving only a heating capacity of .39kw
I missed this earlier comment. Is the calculation from the LG technician, not Omnie?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
Surface mount or bury primaries for heat pump installation?
1 month ago
-
UFH and ASHPs
3 months ago
-
Installing your own ASHP - DIY
4 months ago
-
ASHP install contract and BUS grant money
5 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
5 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,123 Topics
- 46.7 K Posts
- 89 Online
- 4,531 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Is your heat pump insured?
My home insurance renewal is due soon meaning I am doin...
By cathodeRay , 10 hours ago
-
New Vaillant aroTherm Plus in black - When will it come to the UK?
It looks like Vaillant are updating the aroTherm plus l...
By Sandy , 12 hours ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 12 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Ive called most of them over the years. By far the best...
By dgclimatecontrol , 13 hours ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 17 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
I've certainly seen that on their Ts & Cs page but ...
By Majordennisbloodnok , 1 day ago
-
RE: ASHP heat output monitoring
@carlo - not much better, is it. It looks more like a u...
By cathodeRay , 2 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 2 days ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 3 days ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 3 days ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 3 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
Cross references for @martingale Background discussi...
By Transparent , 3 days ago
-
@ecobaker May I ask a question of you please. I too hav...
By Papahuhu , 3 days ago
-
It's unclear to me how the Smart Control project work b...
By Transparent , 4 days ago
-
RE: Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
@pavel, this isn't about discrediting Chinese products....
By Mars , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 6 days ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 7 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 7 days ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 7 days ago