Air Changes per Hour - ACH and the MCS requirement
I am falling foul of the MCS "requirement" for their BUS £7,500 grant to use high ACHs (bath/loo 3, kitchen/hall 2, living 1.5, bed 1) which makes a 25% increase to the total heat loss calcs.
My installer insists on pump size 9.2kW which is 25% larger than the 7.4kW sizing if the ACH is taken as 1.
The actual gas consumption rule of thumb suggests 7.7kW while the gas/Heating Degree Days calculation gives 5kW for my house.
I broached this subject on my introduction posts (thank you to @jamespa) but feel that while fabric loss is beautifully calculatable the ventilation heat loss using the MCS's spurious ACHs is a major contribution to pump and system oversizing leading to extra costs and lesser SCOPs.
So I think it would be helpful (especially for those new to heat pumps) to know:
- can you get the MCS £7,500 grant if you dont use their ACHs?
- is there an easy way to measure your house's ACH?
- what are the calculatable downsides of installing a heat pump that is 25% too big for your house?
thank you for any partial contributions to these big asks!
Hi, @matwin
There are a couple of other things, I think, to add into the mix as well.
In your previous posts in the intro thread, @jamespa rightly said that a small oversizing is not the big issue gross oversizing would be. It's also the case that some brands/ranges of heat pumps modulate better than others. When we got our heat pump installed, the company we used originally spec'd a 7kW Vaillant but, as a result of supply chain issues, gave us the option of an 8.5kW Mitsubishi that was in stock. Knowing what I know now, I suspect I would have chosen to wait but we decided on the Mitsi unit so we could press ahead and in fact it has been fine; reliable and economical. My guess is that this is at least in part because Mitsubishi kit is recognised as able to modulate down quite well, thereby mitigating the short cycling issues we might have seen if we'd gone for another brand.
The big question, of course, is whether a jump from 7.4kW to 9.2kW is a moderate or a gross oversizing. My (heavily underlined) AMATEUR feeling is that it may well still be within reasonable bounds depending on the brand. I would, however, happily defer to anyone else with any kind of reasonable claim to an expert opinion.
As for air changes per hour, I found an article that gives some information on the MCS standard on which the calculation is based. It seems using air changes per hour is the bread and butter of the 2003 standard whereas the 2017 standard requires more ventilation data per room. It also says that, from 2nd June 2025, the 2003 model will no longer be permitted. Given that's less than two weeks away and your potential installers should be up to speed with the new calculation tools and measurements, I wonder if it may be worth asking them to demonstrate their answer won't change under the new MCS standards. Either you'll get confirmation or a new answer.
As I said, I'm no expert so take all that with a pinch of salt but it's a start.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@matwin I'm going through a similar quotation journey currently (& hopefully nearing the end of it now). One relevant piece of information I had from one provider on sizing was that Vaillant (and I assume other manufacturers will have similar rules) insist on there being 120% coverage for their pumps, so this has to be factored into the solution proposed by anyone quoting one of their systems to ensure that the warranty is effective. It was a relevant issue for the quote in question, as the calculation based on a 7kW heat pump maxed out at 102%, meaning that the proposal had to use the next model up, in this case a 10kW unit.
Consequently, modest over-sizing is likely to be present in most designs, if all manufacturers apply similar criteria. The issue, as previously noted, is to avoid gross oversizing.
Also, based on my experience so far of seeing the results of heat loss surveys, the potential for error from ACH assumptions is no different to the potential for error in material U-value assumptions (in my case, I've had the same polycarbonate conservatory roof assessed with U values of 0.4 and 5.11 in two separate surveys). Ultimately, the heat loss surveys, even at a room by room level, are a calculation, and are only as good as the data used within them. Consequently, there will be an (unknown) margin of error within them that needs to be allowed for. In my case I've sense checked the calculations I received and did my own sensitivities on them based on where I felt I could reasonably question the data. This gave me a best/worst case range for the heat loss figure that I could use to assess the various proposals, rather than being wedded to a single number. I've found it helpful doing so, particularly as our property appears to be right within the 8-10kWh assessed heat loss range that falls in the gap of many manufacturers heat pump sizing ranges.
It's still only a sense check, at the end of the day, but it's enabling me to have sensible discussions with the providers and I'm finding that their responses and attitudes to such are a much more relevant indicator as to my overall assessment of them.
Currently viewing this topic 1 user ( trebor12345 ) .
Recently viewed by users: JamesPa 15 minutes ago, Scalextrix 27 minutes ago, Sheriff Fatman 43 minutes ago.
- 22 Forums
- 2,067 Topics
- 45.2 K Posts
- 51 Online
- 3,336 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: How accurate was your heat loss survey?
@scalextrix I think what you are describing is exactly ...
By bontwoody , 3 minutes ago
-
RE: Home energy storage & battery register
By the end of next month... 8 kW PV + Tesla Powerwall...
By Algienon , 32 minutes ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
@sheriff-fatman thanks and good luck with your installa...
By MatWin , 1 hour ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
@grahamh-uk Yes, I have the same Samsung controller p...
By Old_Scientist , 2 hours ago
-
RE: Various different approaches to battery storage.
I thought I'd share my story/journey and experiences he...
By Old_Scientist , 2 hours ago
-
RE: Nibe F2040 periodic warm water increase fails
I think the NIBE uses both the ASHP and the element to ...
By ASHP-BOBBA , 5 hours ago
-
RE: Commencing on an ASHP Installation Process
It varies by room, but the conservatory is assumed at 2...
By Sheriff Fatman , 6 hours ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@editor @sallyl As Mars said, there are 2 different typ...
By Brendon Uys , 21 hours ago
-
-
RE: Renewables & Heat Pumps in the News
Here on the Forum we're going to need to be increasingl...
By Transparent , 1 day ago
-
What I Wish I Knew Before Installing a Heat Pump
I’m putting together the next Homeowners Q&A episod...
By Mars , 1 day ago
-
RE: Load Compensation and Weather Compensation
@jamespa anytime. you would not believe how many times ...
By ASHP-BOBBA , 1 day ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
In Scotland they still follow the MCS rules, so the noi...
By Johnmo , 1 day ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo and @benson Thanks! I was aware there was a p...
By MarcT , 2 days ago
-
RE: Is your heat pump insured?
My insurer just asks the question: "Is your home heated...
By AndrewJ , 2 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Slippery slope starting
By Johnmo , 2 days ago
-
RE: Say hello and introduce yourself
@cathoderay Ah yes, that’s the name! The Heat Pimp, It’...
By Toodles , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@editor Oh come on…. it’ll only take him 10 or 15 minut...
By Toodles , 3 days ago
-
By the way, I also think our industry need to get on bo...
By ASHP-BOBBA , 4 days ago