@sheriff-fatman 

It appears Output Power = 0kW because there was a DeltaT of 0
Which doesn't appear correct because it was 4C according to the data.

Like you say, i presume this is a timing/capture thing, in particular with the Home Assistant firmware which has different refresh rates for different parameters giving higher resolution when viewed there.

 

 

Just a note on the Thermo. Diff setting - it only applies in Auto Adapt. It appears you are in Compensation and therefore overshoot is only +1.0
This is the classic Flow Temp overshooting Flow Setpoint issue

The Ecodan was initially set to a +5/-5 tolerance, which is it's default option.  I've subsequently adjusted this to +3/-7, but it still works around a 10°C tolerance around the flow temperature currently.


This post was modified 2 hours ago by F1p

   
ReplyQuote
 F1p
(@f1p)
Trusted Member Member
Joined: 3 months ago
Posts: 40
 

Posted by: @majordennisbloodnok

I wonder, @sheriff-fatman, if Mitsi have chosen to use a shared parameter between defrost cycle and freeze protection. If that were the case, we’d see a software-induced correlation rather than a physics correlation, but a correlation nonetheless.

“Curiouser and curiouser”, said Alice…

Frost Protect/Freeze Stat is an operation mode, where Defrost is a multi-stage status flag (however i only see two used).

In the firmware i inject defrosts to the Operation Mode status for easier viewing and understanding of users.

 