4 port buffer tank connections
Hi. Just a quick question during my quest of identifying the reasons and possible remedies for the mixing i observe and the low- 1 degree Dt. Is there a certain way to connect the pipes to a buffer tank? In all the diagrams i have seen the flow moves in a straight and parallel direction for the top and bottom connections of the tank. On my system it seems that flows crosses the tanks and moves in the opposite direction. Can this be a reason for the issues i face? Please see the attached diagram
This is the way a 4-port buffer should look like. The flow and return, go in the same direction.
What you have described occurring in your buffer is referred to as distortion. Distortion happens when the cooler return water mixes with the hotter flow water inside the buffer tank, potentially lowering efficiency. Ideally, the system should maintain clear separation between these temperatures (hot water at the top, cooler water at the bottom) but that doesn’t always happen in practice. Why? I have no idea. We are recording another episode of the podcast on Friday about buffers, so I will raise your case.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@iraknic the connection diagram you provide looks very like it might be A cause (not necessarily the only one) of your poor performance. My reasoning is that there will certainly be mixing of warmer-cooler water, not the separation by height which is how they are supposed to work.
You don’t say any more about your system, is it in a different thread? If you’ve recently had the system installed get your installer back pronto to fix it to the conventional piping. If you’ve not described your system elsewhere please do.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @iraknic@jamespa i have 2 zones and 6 fan coils connected. I think a buffer tank is inevitable
Maybe
With 6 fan coils you probably do need a volumiser (2 port buffer) because of low system volume, but fan coils alone aren't sofaik an argument for a buffer (why would they be?)
Do you really need 2 zones, and even if you do does that really require a buffer? Not really any different to having a few rads on TRVs.
If you watch the video by @editor on this forum the installers who appear are pretty adamant that buffers are not needed in almost all domestic cases. Installers who advocated for buffers declined to appear, I wonder why?
That said I agree that the way your buffer is plumbed is absolutely bound to causing problems, but if the installer is coming back maybe its an opportunity to get him to take it out altogether/turn it into a 2 port volumiser!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
If the pipe work is connected as per your diagram, then you need to get the installer back and make them change it.
I would suspect it is more a flow problem and not having the two side balanced correctly.
If possible get 4 temperature guages, with probes, and attach them to each pipe into the buffer (about 3inch away from join). You will then get an idea of your flow temp around the pipes. If you only have one guage then place it on each pipe in turn (ashp out, ashp return, ch out, ch return). Making notes of each temp.
You are looking to get the ashp out to match the ch out (or within 1-2°).
If there is a larger temp difference, then look at the flow rate on both side. Your HP instructions should give you an idea of its flow rate. For the CH side you need to look at the pump and see what it's rated for (use the internet)
If one side is much greater, then you have a flow imbalance that needs correcting.
If flow the greater on the ashp then the ch, look at lowering the flow on hp, or increasing it on the ch side.
Note - ensure all emmitters are open and full flowing. It could be yhey have been turned down / off which has caused the imbalance
Why do buffers get such a bad press? They aren't evil, they're just not properly designed.
I buffer should hold a volume of heat and absorb swings in heating demand. Yes, running with weather compensation "low and slow" will help, but an ASHP will need to defrost in cold weather and then you're pumping cool / cold water into the feed to your radiators / underfloor heating. A properly designed buffer can prevent the cold water getting into the house.
Most of the designs I've seen on here and other forums (and online shops) are really just very large low loss headers. They have the primary return at the top, relatively small nozzles and no inlet distributor. A properly designed buffer would have the primary inlet about 1/3 to 1/2 way up from the bottom, and have an inlet distributor to maintain stratification. The "Large low loss header" design has too much turbulence inside which mixes everything up - you end up and tank of luke warm water.
It would be great to see a buffer design that has inlet distributors and can maintain stratification. This design does exist but they tend to be very large and very expensive. A smaller / cheaper option might be a good fit for homes with variable heat load.
Regards
Bob
Posted by: @bobtskutterWhy do buffers get such a bad press? They aren't evil, they're just not properly designed.
You have answered your own question, at least in part In addition the pumps either side often aren't balanced properly so you get mixing, resulting in often a 5C drop flow to flow, and thus a 15% performance penalty.
Volumisers (2port buffers) solve the defrost problem if there is one and are (almost) idiot proof.
I don't doubt that in properly designed commercial applications they work well, but we are in the realm of domestic heating systems.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaIf you watch the video by @editor on this forum the installers who appear are pretty adamant that buffers are not needed in almost all domestic cases. Installers who advocated for buffers declined to appear, I wonder why?
And it's happened again. We're recoding a second buffer tank episode tomorrow, and I've contacted scores of installers since the start of the year that I know install buffers (because I want to have a balanced conversation) and most have ignored my requests to come on the podcast and others have simply declined. But when I contact installers with a successful open-loop, buffer less installation track record they are more than happy to come on and speak.
Make of that as you will.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Even though we can see a reason to remove them, there's also a reason to keep then.
I've found that they can help greatly in reducing defrosting time and also stop the house emmitters cooling down as they get feed cold water. It also help in stopping the pipes from freezing, if the ASHP is not producing heat.
Without the buffer and just using an open loop, all the cold water from both those activities would flow around the emmitters and cool the house down.
I'm now looking at using a 3 way buffer, with a valve. So when just running water around to stop the pipes freezing and during a defrost cycle the valve closes and send all the cold water around the buffer. Once defrosting has completed and heating resumes to the right flow temperature the valve reopens and goes towards the emmitters.
- 26 Forums
- 2,113 Topics
- 46.4 K Posts
- 63 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: Wood burner with ASHP - direct air?
I love the new fully Viking look... best personal avata...
By Mars , 8 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 23 hours ago
-
RE: Buffers, hot water and cooling
@prunus, @jamespa is correct, but removing the buffer ...
By Brendon Uys , 1 day ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 2 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 2 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 2 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 2 days ago
-
RE: Say hello and introduce yourself
Hi @topher - you might be interested to see this very r...
By Transparent , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 4 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 4 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 5 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 5 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 5 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 5 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 5 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 1 week ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 1 week ago