@transparent Your picture of a volumizer is correct, you must be careful that you have 10-15 liters of open zone (free flowing without control) water volume per Kw and a flow rate of between 2 and 2,5 liters/min of peak heat pump power.
Below are some cutouts describing distortion and the implications within a buffer.
Director at Heacol Consultants ltd
Thanks @heacol
Let me check I've understood those diagrams...
Is the ASHP on the left and the radiator(s) on the right like this?
Posted by: @editor[...] a 4-port buffer, with proper balancing on both sides of the hydraulic separation to minimise distortion (aka, blending).
I take this comment to mean:
"If the flow through the radiator loop is too great, then the cold/return water to the buffer would get mixed into the radiator flow;
but it should be mixing only into the return to the HP."
That would appear to take a lot of skill to optimise.
Save energy... recycle electrons!
Posted by: @transparentThat would appear to take a lot of skill to optimise.
... particularly if you have TRVs and zone valves randomly switching on and off, which may well have been part of the 'justification' for the buffer tank in the first place.
I believe that one way to balance a buffer tank is to have temperature sensors one third and two thirds up the tank. The pumps can then be controlled to keep the thermocline between the sensors, thus balancing the tank. I don't know if any heat pumps build this functionality in natively, or whether installers who put in buffer tanks enable it. However I can see that this closed loop control could work, whereas I cant personally see how an open loop system ever could.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@transparent You are correct on both accounts, the picture is correct, and it is exceptionally difficult to balance a buffer in normal circumstances.
Director at Heacol Consultants ltd
@jamespa correct, but why make things complicated when a system without a buffer works so well? In my experience, simplicity is always the best option.
Director at Heacol Consultants ltd
Posted by: @heacol@jamespa correct, but why make things complicated when a system without a buffer works so well? In my experience, simplicity is always the best option.
100% agreed, I am a firm believer in the liberal use of occams razor!. I was just saying it (balancing a buffer) can be done, although it seems, judging by the posts on this forum, that it rarely is done.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa You are again correct, you can balance a buffer tank, just like you can go to the moon 🤣
Director at Heacol Consultants ltd
You can balance a buffer by simply having two flow controller installed either side of it.
One should have already been installed on the ashp side, unless your HP can control the flow rate.
@uk_pete_2000 on Wednesday our next podcast episode will be out and @heacol explains why (and how difficult it is) to monitor the flow on the heating side of the circuit, which makes it incredibly difficult to balance both sides.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor I agree it can be difficult to get it correct and i came to this site just for that help.
Once I realised that most people had no idea other than to say remove it / you don't need it / should not have been fitted have this etc etc. I took it to find out about them and how to get them running.
I also found that nearlly all HP manufacturers say you should have one otherwise the warranty is invalid. Hopefully this will change as they too come to grips with HP
In the meantime we could have 500,000 HP installed, with buffer, all looking for answers other than - remove it etc.
So by just saying it can't be done, does not mean we can not find some solutions that will help mitigate the problem. Simply things like flow controls, ensure all open zones, correct size CH pumps etc. All can help.
In order to keep within my HP warranty (i hope), I expect to switch to a three port buffer. Thus allowing the seperate sides to still work independently of each other.
I would go fully open and remove the buffer but with 3 manifolds, 24 zones and not running it 24 hrs, I would be taking heat out from my house when the HP does a anti freeze cycle.
Posted by: @uk_pete_2000I also found that nearly all HP manufacturers say you should have one otherwise the warranty is invalid. Hopefully this will change as they too come to grips with HP
Do they? That's not what I observe from the several manuals I have read (albeit in some cases fairly quickly, I admit) over the past 2 years. I wonder if @heacol would like to comment about the 'nearly all HP manufacturers say you should have one', given he is so strongly opposed.
Posted by: @uk_pete_2000So by just saying it can't be done, does not mean we can not find some solutions that will help mitigate the problem.
In general I would support the principle of finding practical solutions except that the fix (based on adding additional flow controls in I think you said) seems usually to involve plumbing, and thus for most people their installer. If the installer is coming back they should just remove the buffer unless there is an objectively justifiable reason not to do so.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@uk_pete_2000 I can’t disagree with anything you’ve said. But it’s a big and growing problem, and the main motivation in fitting heat pumps was to get efficient heating systems into UK homes, and buffer tanks are often working against that goal.
The issue isn’t just that buffers are unnecessary in most modern heat pump setups – it’s that they actively reduce efficiency in ways that many homeowners don’t realise. Distortion, increased running costs and reduced heat emitter output all mean that a system with a buffer often performs worse than one without.
You’re absolutely right that manufacturers have historically insisted on buffers to protect warranties, but that’s largely because many systems were being installed with inadequate volume or poor flow control. The industry is slowly catching up, but in the meantime, homeowners like you (who have inherited or been advised to install buffer tanks) are left trying to make the best of a less-than-ideal setup.
Your approach, ensuring correct flow rates, keeping zones open where possible and switching to a three-port buffer, is sensible given your constraints. However, the challenge remains that even with careful mitigation, the fundamental inefficiencies of buffer tanks still apply.
For homeowners with existing buffer tanks, the best course of action is to explore ways to improve the system’s efficiency, as you’re doing. But for new installs, the focus should be on getting the system design right from the outset (sufficient volume in the system, proper flow control and weather-compensated operation) so that buffers aren’t needed in the first place.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 66 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 33 minutes ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 1 hour ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 1 hour ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 2 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 2 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 4 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 6 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 8 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 20 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 23 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 8 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 9 hours ago
-
SolarPV tables / online calculator
By MichelleC 16 hours ago
-
By Toodles 2 days ago