12kW Samsung gen 6 short cycling
Posted by: @craig1980A quick update on my system.Â
I'm running at a COP of around 3.3-3.4 at around 3 degrees outside temp including water heating for an hour at midnight. I'm still messing with settings so hopefully this will increase. Once the cold weather arrives the COP definitely drops.Â
LWT at around 28-29 degrees and WC is on.Â
Derek got to the bottom of the issue. I was running the WC settings incorrectly. There are 3 options which run the pump in different ways whilst WC is on and one of those tells the pumps to turn off after 7 mins then back on. That's why it was short cycling.Â
I still need to contact Samsung and I'll let them know about this thread. My Teva out sensor is showing -50 so I may need a new sensor there. I've checked the outside heat pump and it is all plugged in properly. I'll reply on here with any updates.Â
Craig (@craig1980) would you be kind enough to provide @iantelescope with details of the changes that you made to the controller settings to stop the short cycling.Â
Â
Hi Derek,
Many thanks for the data.
I have tried the Samsung Field bits 2091 Options 1 to 4Â on several occasions.
I too found the field bit 2091 option 4 was suspiciously near to my original 8 minute Cycle time.
Samsung field bit 2091, Water Pump 3 subroutine :
1) Delay for 3 minutes
2) OFF for 7 minutes .
3) ON for 3 minutes.
4) OFF for 7 minutes.
However, I, and the French Samsung Engineer tried all of these settings , multiple times, without any great effect.
The pulsing briefly increases the water temperature, and cycle time during the water cycle .
I Do currently use Water Pump 3 given the 2 C thermostat Hysteresis and the slight resultingincrease in cycle time caused by the extra, mid cycle, Motor pulse.
I have , however tried setting Field bit 2091 , Water Pump 2 subroutine again. given that many other parameters, and settings have changed in the interim.
Samsung field bit 2091, Water Pump 2 subroutine has however a 1 C Hysteresis.
Many thanks to you and Craig.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 210 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: Benefits of an extra horizontal loop for GSHP
I have no direct knowledge of GSHP ground loops but it ...
By Abernyte , 1 hour ago
-
RE: No-code, plug-and-play monitoring for your heat pump
It's an attractive idea but I fear neat all-in-one solu...
By cathodeRay , 1 hour ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 3 hours ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 4 hours ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 19 hours ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 20 hours ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 20 hours ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 1 day ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 2 days ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 2 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 3 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 5 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 5 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 5 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 5 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 1 week ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 1 week ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 1 week ago