My "installation" was fitted with a 50 l Volumising tank some six months after it was "installed".
I was given at least four opinions from Five different "experts" as to Why I needed a Volumising tank......
Why I need a volumising tank................
1 To protect the HEAT PUMP.
A Volumising tank would provide "Hydraulic Isolation" between the Radiators and the Heat Pump .
Any changes in water pressure or Flow rate on the radiators would be isolated from the HEAT PUMP. ( from SAMSUNG Service)
Â
2 . To protect the Heat PUMP during de-Icing.
During sharp frosts the Heat Pump should be protected from the ICE accumulation.
A Volumising tank should store enough Energy to "allow the De-ICing to Complete during severe frosts." ( from SAMSUNG DALLIUM , )
Â
3. To prevent Rapid Cycling , or Hyper Cycling.
A increased volume of water in a volumising tank will reduce rate of temperature fall ...................... and increase the Cycle time.
 See Buffer Sizing .....from MCS
After a dispute between my "installer" and SAMSUNG, my "installer" was fired , and a 50 L Volumising tank was ordered..
Two engineers appeared to install the Volumising tank but explained "that they did not know why I needed a tank nor where to fit it!.
Â
Â
ian
Â
Â
Posted by: @cathoderayThis is important information! Context means a lot when interpreting COPs.
I thought I did put enough context in place with my chart - re posted below. I was showing clearly the COP as labelled for short periods of time. I think with an average of 5.3 over a longer period of time (7 hours) the very high efficiency periods are not far from reality.Â
Based on observations by others regarding Samsung Gen6 [specifically the poor insulation on the temperature probes], I may actually have an even higher COP than I do.
In short, I think that there are times in the year, when a well designed system coupled with good emitter characteristics (mine has some way to go on both) you can get and should be getting a high COP.
Hi Derek,
No , I am still hyper-Cycling!
YES, I am still loosing lots of energy across the Heat Exchanger , pipes et al.!
After nearly of year of problems caused by my "installers" incompetence followed by the endless denials of responsibility from the NIC,MCS and the RECC ..........
I have been advised by the "charitable " MCS and NIC to get a lawyer...............impossible for a 75 year old OAP.
Which is worse ....my "installer" or the Toothless Tigers of the "Charities" supposedly operating as regulators?
I should have installed this myself!
ian
Â
Â
Â
Â
@iantelescope what you've described is what is usually referred to as a buffer tank , due to the fact that its providing hydraulic isolation. A cylinder (which may well be exactly the same part) when installed as in the way that is commonly described as a "volumiser", doesn't provide hydraulic isolation, but does provide the other points you mentioned.
see diagrams on pages 1 and 2 in here(yep, midsummer wholesale again)
Are you able to draw up a detailed system schematic so we can understand your system better with the goal of improving it?
if they didn't know where to fit it, there's at least a possibility that its not doing the right thing.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @william1066Â Â
I tried to find Samsung's equivalent to Midea's Engineering data book which has detained outputs (and COPs) at different ambients and LWTs but didn't have any luck - maybe you have the data? It would provide another benchmark to compare your figures to.
Â
Â
first result, page 29 of the pdf
Â
Â
@transparent on the "what sort of meter to use" point:Â there's no reason for me to need larger screen of the 220, as I'll be reading it purely over modbus.Â
I currently have this:
and intend to modify it to thisÂ
does that make sense?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iantelescopeHi Derek,
No , I am still hyper-Cycling!
YES, I am still loosing lots of energy across the Heat Exchanger , pipes et al.!
After nearly of year of problems caused by my "installers" incompetence followed by the endless denials of responsibility from the NIC,MCS and the RECC ..........
I have been advised by the "charitable " MCS and NIC to get a lawyer...............impossible for a 75 year old OAP.
Which is worse ....my "installer" or the Toothless Tigers of the "Charities" supposedly operating as regulators?
I should have installed this myself!
ian
Â
Â
Â
Â
Are you using Weather Compensation (WC) mode?
What is the present Leaving Water Temperature (LWT) on your system?
Â
Posted by: @iantelescopeHi Derek,
No , I am still hyper-Cycling!
YES, I am still loosing lots of energy across the Heat Exchanger , pipes et al.!
After nearly of year of problems caused by my "installers" incompetence followed by the endless denials of responsibility from the NIC,MCS and the RECC ..........
I have been advised by the "charitable " MCS and NIC to get a lawyer...............impossible for a 75 year old OAP.
Which is worse ....my "installer" or the Toothless Tigers of the "Charities" supposedly operating as regulators?
I should have installed this myself!
ian
Â
Â
Â
Â
This link was posted on the forum yesterday which you may find of use.
https://www.theheatinghub.co.uk/articles/raise-complaint-about-heat-pump-installation
Â
Posted by: @iantelescopeTwo engineers appeared to install the Volumising tank but explained "that they did not know why I needed a tank nor where to fit it!.
Pretty much par for the course, though my installer was better, he not only suggested the volumiser in the first place when I mentioned the short cycling and showed him the charts with the short cycling clearly visible, he also knew what it did and where it could be fitted (in practice, wherever there is space in the heated areas in the house so its losses contribute to space heating).
Posted by: @william1066In short, I think that there are times in the year, when a well designed system coupled with good emitter characteristics (mine has some way to go on both) you can get and should be getting a high COP.
I am sure that's right, but for my part, I like to reassure myself I am not getting Maoist tractor production is up figures. Thanks to @dandee, I managed to have a look at the Samsung performance data, and it looks as though in favourable conditions COPs in the region of 6 are indeed possible with your unit. I think that means you can have more confidence in your results, but again, if it was me, I would be wary of being too pleased with myself. COPs of around 6 are extremely good, and most heat pumps won't get there most of the time. It will be interesting to hear what your SCOP is once the heating season is over, if you plan to calculate it. I think mine will be between 3.0 and 3.5, and although I now trust the energy in figure a bit more, I am still wary of the energy out. Now that I have found out that I do have an inline flow meter, I do have the option of verifying the modbus flow rates, which as previously noted tend to remain in a small range, meaning the only extra data I need to collect independently is the LWT and RWT. But that is probably something that will have to wait until the start of the next heating season, though I can set up the hardware over the summer.
Â
Midea 14kW (for now...) ASHP heating both building and DHW
I now control of my Primary Water loop as a function of the room Temperature. Yet another Arduino, A new function "yetaarduino".
The Control measures the room temperature and sets the PWM Signal to the primary water loop circuit.
The Multiplying factor setting the change in Flow rate against the Temperature change will have to be found by experiment. with an initial setting of 1 lpm per degree C.
The Secondary water loop , on the other side of the Heat Exchanger remains , for the present under control of an oscillator.
ian
Â
Â
Posted by: @iantelescopeI now control of my Primary Water loop as a function of the room Temperature. Yet another Arduino, A new function "yetaarduino".
The Control measures the room temperature and sets the PWM Signal to the primary water loop circuit.
The Multiplying factor setting the change in Flow rate against the Temperature change will have to be found by experiment. with an initial setting of 1 lpm per degree C.
The Secondary water loop , on the other side of the Heat Exchanger remains , for the present under control of an oscillator.
ian
Â
Â
The normal method of controlling the indoor temperature would be by varying the LWT, in conjunction with changes made by WC. I suppose varying the flow rate may also work.
I seem to remember someone asking whether your heat exchanger is actually a buffer tank. Could you provide a photo?
Did you resolve the cycling issue?
Â
My Volumising tank was originally designed and selected by Samsung Dallium , Samsung's own service depot at Wigan .
My "installer's technical designer " then described the Samsung proposal to install the volumising tank as "ludicrous" and that "their own engineers would complete the job".
My "installer's technical designer "was then fired "for Technical incompetence!".
The Volumising tank was then "discovered under the former Technical designer's desk .....some two months later!
Two "Engineer's" then appeared to install the "Volumising tank " but "did not know where the tank was to be installed within the pipework.
The "Volumising tank " was designed by Samsung-Dallium to "allow the Heat pump to complete DE-icing on Cold Scottish nights".
The MCS also provided information about controlling short Cycling.........with a different size of volumising tank in a different pipework location!
The "Volumising tank was fitted across the Primary ports of my Heat Exchanger .......total confusion!
The DE-icing works very well during winter.
The Short-Cycling on the primary water loop has also stopped.
However, the Secondary water loop, the radiator loop , is now hyper-cycling ..........
Presumably another volumising tank should be fitted to my secondary , radiator water loop?
ian
Â
Â
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 70 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
Water pump will certainly make a hum (which could conce...
By JamesPa , 1 hour ago
-
@jamespa Thanks. Yeah any adjustments Ive made at pr...
By cliffhanger , 2 hours ago
-
RE: Mitsu PAR-WT60R Wireless Controller - options
I have been running mine in auto adapt since 2019 and i...
By Abernyte , 3 hours ago
-
RE: Powerwall 3 or Myenergi or something else?
Many of those tariffs are simple time of use tariffs, w...
By Temperature_Gradient , 14 hours ago
-
So far as I can tell designing for DT5, which is 'the n...
By JamesPa , 14 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 2 days ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 2 days ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 3 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 3 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 3 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 3 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 4 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 4 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 6 days ago