IHi Derek, will try a load resistor on the SIG/REF pins.
Given contradictory information from GRUNDFOS about the Black and Brown PWM wires is it possible that the PCB output was damaged by being connected to the input PWM on the motor?
Why is the Return from the Motor going to a pin labelled REFERENCE ? What REFERENCE?
Would my connecting my scope earth to REFERENCE damage the REFERENCE /SIGNAL ?
The Grundfos specs give an amplitude of between 4 and 24 Volts, and , I used 12 Volts for my tests with the pulse generator.
ian
Without knowing what components are on the Samsung PCB, it is difficult to say if it may have been damaged. Are there any cautionary notes in the documentation that stipulate care in connecting the wiring?
It would appear that power for the PWM input circuitry on the pump, is being supplied from the Samsung PCB, with pin 3 acting as a reference for both the input signal and the feedback signal on pin 2. The reference will be connected to some common point on the PCB, which may or may not be at 0v. The Grundfos document states that pin 3 is not connected to protective earth, but does not state where it is connected.
Applying a positive DC voltage to pin 3 could possibly cause a current flow through the 36v zenner diode to pin 2.
Connecting a scope that is earthed can sometimes cause problems.
Where are you measuring the signal using the scope? What happens if you connect the cable to a pump? How does the waveform change if you vary the DeltaT?
The Signal output from my Control PCB on SIG/REF appears to be faulty or incompatible with the motor load.
The Scope is connected to SIG with REF connected to the scope earth..
The "Signal" SIG drops to 1.6 V olts DC when the Pump is connected to the PWM input to the motor, the Brown wire.
A 1k resistor across the SIG/REF also kills the signal.
The Output impedance of the SIG/REF is far to high causing the motor to kill the signal.
The Output "signal" is also offset by 6.5 Volts DC .
I do not know but I may have damaged the output chip in following the conflicting wire colour advice. Possible , but unlikely ....the circuit should easily withstand the wire reversal.!
With no displays of any kind, the unsuspecting User has no way of determining if the PWM system is working or not!
When the PWM does not work the user is presented with an apparently working system defaulting to the Maximum Flow rate..
I have decided to abandon the SAMSUNG PWM Signal and implement my own PWM Signal using an Arduino to control and balance the flow through , in my case, BOTH PWM Motors.
The Balancing , or positioning the flow rate into the centre of the control signal width , as shown in the Piping Installation instructions on page 58 of the new installation instructions will be my starting point.
Something is amiss with the SAMSUNG Explanation as to why SAMSUNG alone, of the HEAT PUMP Manufacturers, does not automatically install PWM controlled pumps.
disagree. documentation from at least one samsung supplier shows how to do this and its clearly documented in Samsung manuals. I said this before already.
The fact yours doesn't have it is a different issue.
one more thing, I don't understand why you won't just go through warranty with samsung. It does seem that you have evidence that your PCB's PWM output is bust. But that's up to you.