But at the beginning of the 8 min cycle they are both within 0.5 degree of each other at 22
Outside unit heat pump fans run for around 5 mins then it's quiet until 8 mins and 20 seconds then it starts again.Â
I will have a look at the data and get back to you tomorrow.
In the meantime, with the system running, measure the temperature in the central section of each radiator at both the top and the bottom, along with the relevant room temperature.
Posted by: @transparentLet's label a few bits:
-- Attachment is not available --
Am I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
Â
@mike-h I have two small tanks above the uvc but I'm assuming they aren't buffer tanks? I have a cold water header tank in the loft and the system outside. That's all I have so unless one of those two tanks are a buffer then I don't have one.
Did you measure and record the radiator temperatures?
Posted by: @mike-hAm I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
It doesn't have a buffer, no...
Which set of instructions say that the samsung needs a buffer?
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @craig1980@mike-h I have two small tanks above the uvc but I'm assuming they aren't buffer tanks? I have a cold water header tank in the loft and the system outside. That's all I have so unless one of those two tanks are a buffer then I don't have one.
-- Attachment is not available --
The white one is the expansion vessel for the domestic hot water (from the unvented cylinder) and the grey one is the expansion vessel for the heating/ashp circuit.
As you have an unvented cylinder, there is no need for any tanks in the loft, and also no need for that shower booster pump. I'm not sure why you still have those in your installation.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Below is a link for the controller instructions. Select the home screen and monitor the outdoor temperature whilst your system goes through its cycling process.
- 26 Forums
- 2,123 Topics
- 46.7 K Posts
- 28 Online
- 4,531 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
I've certainly seen that on their Ts & Cs page but ...
By Majordennisbloodnok , 5 hours ago
-
RE: Planning Permission May 2025
Where does it state this please? Im genuinely interest...
By JamesPa , 8 hours ago
-
RE: ASHP heat output monitoring
@carlo - not much better, is it. It looks more like a u...
By cathodeRay , 10 hours ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 13 hours ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 day ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 day ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
Cross references for @martingale Background discussi...
By Transparent , 2 days ago
-
@ecobaker May I ask a question of you please. I too hav...
By Papahuhu , 2 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@terry1812 Oh Good! Pleased to help if I can! Regards, ...
By Toodles , 3 days ago
-
It's unclear to me how the Smart Control project work b...
By Transparent , 3 days ago
-
RE: Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
@pavel, this isn't about discrediting Chinese products....
By Mars , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 5 days ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 5 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 5 days ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 5 days ago
-
RE: Who's your electricity provider and what's your tariff?
Aggregators have been recognised for many years, and it...
By Transparent , 6 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Great news I edited my previous post (probably af...
By JamesPa , 6 days ago