But at the beginning of the 8 min cycle they are both within 0.5 degree of each other at 22
Outside unit heat pump fans run for around 5 mins then it's quiet until 8 mins and 20 seconds then it starts again.Â
I will have a look at the data and get back to you tomorrow.
In the meantime, with the system running, measure the temperature in the central section of each radiator at both the top and the bottom, along with the relevant room temperature.
Posted by: @transparentLet's label a few bits:
-- Attachment is not available --
Am I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
Â
@mike-h I have two small tanks above the uvc but I'm assuming they aren't buffer tanks? I have a cold water header tank in the loft and the system outside. That's all I have so unless one of those two tanks are a buffer then I don't have one.
Did you measure and record the radiator temperatures?
Posted by: @mike-hAm I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
It doesn't have a buffer, no...
Which set of instructions say that the samsung needs a buffer?
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @craig1980@mike-h I have two small tanks above the uvc but I'm assuming they aren't buffer tanks? I have a cold water header tank in the loft and the system outside. That's all I have so unless one of those two tanks are a buffer then I don't have one.
-- Attachment is not available --
The white one is the expansion vessel for the domestic hot water (from the unvented cylinder) and the grey one is the expansion vessel for the heating/ashp circuit.
As you have an unvented cylinder, there is no need for any tanks in the loft, and also no need for that shower booster pump. I'm not sure why you still have those in your installation.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Below is a link for the controller instructions. Select the home screen and monitor the outdoor temperature whilst your system goes through its cycling process.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 25 Online
- 5,655 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 2 hours ago
-
RE: ASHP heat output monitoring
Agreed with the one qualification that increasing the n...
By JamesPa , 5 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 20 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 20 hours ago
-
RE: How much am I ‘saving’?
@old_scientist like for like comparisons are almost imp...
By Tim441 , 21 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 21 hours ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 21 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 3 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 3 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 3 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 4 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 4 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 5 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 7 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago