Thanks Derek and Kev super impressed by your response.
In answer Derek we have 5 rads upstairs with Trv's 2 towel heaters without Trvs. All controlled by a wireless thermostat provided with the system. This is classed as zone 2. Down stairs the 7 thermostats in each room just call for heat for ufh, this is classed as zone 1.
Im going to increase by 1 deg, on each thermostat on zone 1 now to see how that goes.
Yes Kev M its counter intuitive to what we have known regards gas but more than willing to give it a try.
Â
Posted by: @sandThanks Derek and Kev super impressed by your response.
In answer Derek we have 5 rads upstairs with Trv's 2 towel heaters without Trvs. All controlled by a wireless thermostat provided with the system. This is classed as zone 2. Down stairs the 7 thermostats in each room just call for heat for ufh, this is classed as zone 1.
Im going to increase by 1 deg, on each thermostat on zone 1 now to see how that goes.
Yes Kev M its counter intuitive to what we have known regards gas but more than willing to give it a try.
Â
From you own personal experience I would recommend that in order to use the weather compensation correctly you should turn all your thermostats up to say 25ºC so they are calling for heat all the time.
And have all TVRs fully open.
Let the ASHP run using the curve for say 12 hours. After this time, if the downstairs temp is too low, notch the FTC controller display up, or if too high, notch it down and repeat the 12 hour test.
I have a similar setup as you, UFH downstairs which has 3 thermostats (but all on ASHP zone 1) and several rads upstairs with TRVs (on ASHP zone 2).
My thermostats are now purely there to tell me what the temp is, they do not control the ASHP.
Downstairs: office is usually 21ºC, hallway is usually 19ºC and living area/kitchen is usually 22ºC. The difference in temp is relative to the area of UFH piping in each area.
Upstairs is always around 20ºC.
It does sound scary I know, especially with the current cost of energy, but I too am a thrifty Yorkshireman and after almost a year of testing, experimenting with different heating regimes and settings, if someone is at home most of the time, this seems to be the most efficient way to run these systems.
But if you all go out to work, perhaps other settings/schedules might work better for you.
Great info Mark C, we are here most of the time. As we have only lived here 6 weeks its hard to get our heads around this. I just want it to be comfy not overly warm but i had visions of sitting in hat and coat all day if it was too expensive for hubby🙄 so trying to understand it get the best out of the system.
Hi @sandÂ
Actually I had forgotten that Mark also has a 2 zone system, so following his advice would probably be the easiest option for the present. My concern was how well balanced your system is and if all the thermostats and valves are actually connected to the controller.
The fundamental idea behind weather compensation, is that to maintain a reasonably constant temperature within your home, the heat energy supplied should closely match the total heat loss, and vary with changes in outside air temperature. Obviously, the heat loss compared to heat energy supply will vary from room to room, so you may find differences in temperature that possibly will need to be balanced, if they are found to be outside acceptable limits.
If like Mark, you can operate your system with no intervention from the thermostats and TRV's, but solely on weather compensation control then that would be much better.
Mark a question for you. Have you noticed how the FTC controller manages the opening and closing of the zone valves?
Posted by: @derek-mMark a question for you. Have you noticed how the FTC controller manages the opening and closing of the zone valves?
In a word, no!. Although on the FTC zone 1 is for UFH and zone 2 is for rads, I don't understand the relationship to the actual zoning throughout the property.
i.e. our UFH has 3 zones/thermostats which link to 6 manifold actuators. There is 1 synchron valve that controls flow to the manifold.
We then have 2 zones for radiators, each of which has it's own synchron valve.
This image shows ecodans kwh usage over last 4 wks. On 27th Dec changed settings to compensation curve, I know weather has been very mild, but very happy with results.Â
Followed Dereks advice re comp curve figs. the settings are currently -2 on the ftc. Upstairs a steady 19 and rooms downstairs 21 22 most of the time. On 24/7. I'm warm, husbands happy, thanks again for great advice.
Happy New Year.
So far so good then, it'll be intersting to see how the next couple of (colder) days go. I've done the complete opposite as you and switched from weather compensation to constant flow on Christmas day as an experiment. I'll post the results after the next couple of days but weather compensation is definitely winning so far.
 Â
@sand and others.
How do you get these figures and graphs/diagrams etc?  I too have Ecodan 11.2KW ASHP.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
I have the app, which i find clunky. I would've thought that a big brand name like Mitsubishi could come up with something a bit more advanced.
Posted by: @markcHave you got meters installed that monitor usage and delivery?Â
Known as MMSP Metering and Monitoring Service Package. Or access to the MelCloud app?
Hi Mark. I don't have MMSP but I do have access to MELCloud. Although that tells me I need a firmware update but won't update for some obscure reason. Also I understand the data from MELCloud isn't at all accurate. For example the shown set temp' is 24C which is correct but it shows the actual room temp' as that or very close also which is inaccurate. The temp is set at 24C to keep the setting for weather comp' curve but the room temp is a comfortable 21/22C.  It makes me wonder if the other readings are accurate.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 33 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: No-code, plug-and-play monitoring for your heat pump
By Grantmethestrength , 19 hours ago
-
@eliuccio good to hear you’re happy with the install. A...
By Mars , 1 day ago
-
RE: Is this just haze or something more?
I am not a scientist nor a meteorologist and I know the...
By Toodles , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
It will improve performance, but by how much depends on...
By Brendon Uys , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 3 days ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 3 days ago
-
Compressor and Evaporator Stratification
I have had a few issues with my Hitachi spilt heatpump ...
By trebor12345 , 3 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 4 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 4 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 4 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 4 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 5 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 6 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 1 week ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 1 week ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 1 week ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 1 week ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago