I've got a Nibe F2040 ASHP which has been installed for over a year now.
Whilst trying to optimise the system I've wondered if the buffer is causing me issues.
See attached drawing of my system. I have noticed that the pipework at point '1' is cooler than at point '2' and '3'.
The PWM motor is controlled by the Heat Pump to maintain a deltaT and the other 2 pumps are fixed speed (currently setting 2).
Does anyone have any suggestions on how I can better match the circulation pumps to the HP, or how I can prevent the mixing in the buffer.
I'm tempted to ask my installer to add a couple of valves to the top and bottom of the buffer so I can try isolating this completely?
I would suggest that you check your schematic, since it appears to make little sense. A buffer tank would normally have at least 4 connections, 2 in and 2 out. I also don't understand why pipe '1' would be cooler than pipes '2' and '3', if the direction of flow is as shown.
There is often an arrow on the pump body to indicate the direction of flow.
The schematic is correct as drawn and the buffer is Tee'd off the pipework that then goes towards the other 2 pumps.
Apologies pipe '1' was meant to say warmer not cooler.
What is the temperature difference?
Looking at the schematic, I suspect that the combined flow rate through the two pumps on pipes '2' and '3' is greater than the pump on pipe '1'. This will probably have the effect of drawing the cooler water in the return pipe, through the buffer tank, and hence causing it to mix and cool the water from the heat pump. Try reducing the speed of the pumps on pipes '2' and '3' to see if this increases the temperature in the aforementioned pipes.
@luke remove the buffer and it will work properly. The schematic is not a Nibe 2040 configuration. There is no need for the buffer. If you have a blending valve and pump on your under floor manifold, this should be removed and, firstly, I would try to run the system on a single temperature with the internal sensor to control the house temperature, if that does not have adequate control, then set up 2 separate zones through the controller.
Posted by: @derek-mWhat is the temperature difference?
Looking at the schematic, I suspect that the combined flow rate through the two pumps on pipes '2' and '3' is greater than the pump on pipe '1'. This will probably have the effect of drawing the cooler water in the return pipe, through the buffer tank, and hence causing it to mix and cool the water from the heat pump. Try reducing the speed of the pumps on pipes '2' and '3' to see if this increases the temperature in the aforementioned pipes.
I have slowed the pumps down to speed 1 and will report back. I'm not sure of the temperature difference, but it was noticeable by hand. I have access to a thermal camera so I'll get hold of this.
Posted by: @heacol@luke remove the buffer and it will work properly. The schematic is not a Nibe 2040 configuration. There is no need for the buffer. If you have a blending valve and pump on your under floor manifold, this should be removed and, firstly, I would try to run the system on a single temperature with the internal sensor to control the house temperature, if that does not have adequate control, then set up 2 separate zones through the controller.
I agree that ultimately I want the buffer removed or at least put in series as I don't think it has any benefit and we should have sufficient volume in the circuits.
There is no blending valve on the UFH manifold and I run the whole system in WC using the internal sensor to 'adapt' the curve. All TRVS open and heating circulation pump thermostat set as a max stop limit only.
Looking at the below schematic, my system is I believe a similar setup to this, excluding CP6 and EB1 and any associated valves / pipework. CP5 is shown as the buffer vessel (which in my case is a Nibe UKV 20-40)
When looking at that installation manual for the UKV it doesn't actually show my configuration with the buffer, which I would say is different to the SMO20 installer manual screenshot?
Here are a couple of pictures of my setup before it was finished and insulated.
@luke Your valve is fine, remove the items circled and you will have very good performance. You have plenty of system volume for the heat pump.
@heacol thanks for this. I will take these comments back to my installer.
May I ask why you would remove the TF1 filter for a strainer? Is this just to improve flow? Will there be other detrimental effects?
Also I presume you are saying that the system will run from just the charge pump as you are suggesting removal of both heating medium circulation pumps. (I like this idea as it will reduce base load, but I expect my installer will be hesitant to recommend this considering he installed both!)
@luke TF1 filter for a strainer? Is this just to improve flow? Will there be other detrimental effects? just to improve flow and stop parasitic losses. It will have no detrimental effect. It can be put back in parallel with the strainer if you are worried.
The installer will probably balk at removing them, but you are the customer.
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 394 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
That doesnt seem quite the same description as the one ...
By JamesPa , 20 minutes ago
-
RE: Fan is clipping ice build up from the front of unit.
@transparent Perhaps we need some positive actions to t...
By Toodles , 29 minutes ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 34 minutes ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 58 minutes ago
-
RE: Setback savings - fact or fiction?
@sunandair I’m attaching a plot of January so far with ...
By Toodles , 1 hour ago
-
RE: Running from backup generaor in powercut?
@editor It is just as well that you possess some fossil...
By Toodles , 1 hour ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Great to hear! I just figured this out a day or tw...
By anotherdaveuk , 2 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 7 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 1 day ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 1 day ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
I hadn't spotted that there were two pumps in the UFH (...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 2 days ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 2 days ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 2 days ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 2 days ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 2 days ago