Battery Storage Wiring Gauge Question
I'm looking to get an Seplos Mason 280/LF304 battery bundle (15kwh) and I want to place it in a little outhouse attached to the side of the main house - mainly for fire prevention reasons but it's also damned heavy! The Solis inverter is in the loft...
What is the maximum length of cable I can run between the two please? I'll obviously get the correct gauge but can't get my head around what that gauge needs to be.
Posted by: @puffWhat is the maximum length of cable I can run between the two please?
As long as you like, you have to watch overall voltage drop on the DC side less than the AC. (Assume you are running in DC). I am running PV cables 40m in DC no issue, in AC it would have been quite costly and I may have had voltage drop issues.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @puffI'm looking to get an Seplos Mason 280/LF304 battery bundle (15kwh) and I want to place it in a little outhouse attached to the side of the main house - mainly for fire prevention reasons but it's also damned heavy! The Solis inverter is in the loft...
What is the maximum length of cable I can run between the two please? I'll obviously get the correct gauge but can't get my head around what that gauge needs to be.
As far as the gauge or thickness of the cable is concerned, this will depend upon the maximum quantity of power to be moved and the voltage.
If you wish to supply 3kW of power at 240 Volts AC, then the maximum current would be 3000/240 = 12.5 Amps.
To move the same 3kW at 50 Volts DC would require a current flow of 3000/50 = 60 Amps.
If you look at the current carrying capacity of different sized cable you should find the one that would meet the task.
Posted by: @derek-mAs far as the gauge or thickness of the cable is concerned, this will depend upon the maximum quantity of power to be moved and the voltage.
If you wish to supply 3kW of power at 240 Volts AC, then the maximum current would be 3000/240 = 12.5 Amps.
To move the same 3kW at 50 Volts DC would require a current flow of 3000/50 = 60 Amps.
If you look at the current carrying capacity of different sized cable you should find the one that would meet the task.
It's a Solis 3.6kw hybrid inverter, so has a nominal 5kw max output at 48/50 vDC, which from the above would imply 100 Amps/thereabouts.
I need about 8m of length so a 1AWG or 0 AWG to be on the safe side?
25mm² cable would give 2.56% (1.23 volts) drop based on 48V, 100A and 8m.
35mm² 1.87% (0.896 volts) drop
Doesn't look like you need (50mm²)
Posted by: @puff1AWG or 0 AWG to be on the safe side?
Check your manual for max volt drop.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
- 21 Forums
- 1,751 Topics
- 37.5 K Posts
- 36 Online
- 2,040 Members
Join Us!
Latest Posts
-
RE: Samsung E911 intermittent issue
Will do and thanks for all the help!!
By NetDonkey , 3 hours ago
-
RE: Watch Where Your Installer Fits Motorised Valves
The irony of this entire situation isn’t lost on me @tr...
By Mars , 3 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
We've had our Homely for a couple of months now. Comple...
By benson , 5 hours ago
-
If all we cared about was cost per kwh of heat, we can ...
By Ringi , 5 hours ago
-
RE: Post Buffer Tank DUCA Circulating Pump Settings
@editor Hi, yes it does, thank you
By Potatoman , 6 hours ago
-
RE: Questions and comments about annual heat pump maintenance and servicing
@toodles mine went and it was cheaper to get another, i...
By David999 , 8 hours ago
-
RE: Agile: average import cost vs other tariffs?
I don't know if you've taken a look at all, @ianmk13, b...
By Majordennisbloodnok , 8 hours ago
-
RE: What is a considered a decent weather curve for running weather compensation?
So with a flow temp maxing at 42C, managed to get livin...
By Crimson , 9 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor I purchased both books from Amazon and read th...
By ASHP-BOBBA , 13 hours ago
-
RE: New Samsung 12KW Heat Pump Help
@mike-h Oh, I am not sure I can answer accurately, When...
By ASHP-BOBBA , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Received an email today from British Gas informing me t...
By Mike Patrick , 1 day ago
-
RE: Mitsubishi Ecodan ASHP general set-up and efficiency
Maybe work out what brand they are and google the instr...
By Gary , 2 days ago
-
RE: The UK’s Heating Nightmare: Why Many Systems Fail Homeowners
"within a few years" is a pretty long timeframe within ...
By Transparent , 3 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
@dunlorn Good shout that buddy will give it a go at ...
By Burtis , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@bromide Thanks for the advice, doing it once but prope...
By ChandyKris , 4 days ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
I've created a separate thread to discuss WC settings a...
By Crimson , 4 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Thanks I will try that and look at results
By A E Deans , 4 days ago
-
RE: Excessive performance/system issues with GSHP
@johnr Thanks - the Buffer tank is in the integral gara...
By didjerama_uk , 4 days ago
-
RE: Do thick walls make for warm houses?
@robl Thanks, thats interesting 🙂
By bontwoody , 5 days ago
-
RE: Mitsubishi EcoDan ASHP Settings not saving.
@fez96 Who’d of thought.? 👍
By Westkent , 5 days ago
Latest Topics
-
Samsung E911 intermittent issue
By NetDonkey 3 days ago
-
Samsung HP secondary pump wiring
By Chris-in-Kemnay 7 days ago
-
Post Buffer Tank DUCA Circulating Pump Settings
By Potatoman 1 week ago
-
Baffled by heat pump size/ choice!
By zuluwarrior 1 week ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 2 weeks ago
-
By R0y124 2 weeks ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 2 weeks ago