Battery Storage Wiring Gauge Question
I'm looking to get an Seplos Mason 280/LF304 battery bundle (15kwh) and I want to place it in a little outhouse attached to the side of the main house - mainly for fire prevention reasons but it's also damned heavy! The Solis inverter is in the loft...
What is the maximum length of cable I can run between the two please? I'll obviously get the correct gauge but can't get my head around what that gauge needs to be.
Posted by: @puffWhat is the maximum length of cable I can run between the two please?
As long as you like, you have to watch overall voltage drop on the DC side less than the AC. (Assume you are running in DC). I am running PV cables 40m in DC no issue, in AC it would have been quite costly and I may have had voltage drop issues.
Posted by: @puffI'm looking to get an Seplos Mason 280/LF304 battery bundle (15kwh) and I want to place it in a little outhouse attached to the side of the main house - mainly for fire prevention reasons but it's also damned heavy! The Solis inverter is in the loft...
What is the maximum length of cable I can run between the two please? I'll obviously get the correct gauge but can't get my head around what that gauge needs to be.
As far as the gauge or thickness of the cable is concerned, this will depend upon the maximum quantity of power to be moved and the voltage.
If you wish to supply 3kW of power at 240 Volts AC, then the maximum current would be 3000/240 = 12.5 Amps.
To move the same 3kW at 50 Volts DC would require a current flow of 3000/50 = 60 Amps.
If you look at the current carrying capacity of different sized cable you should find the one that would meet the task.
Posted by: @derek-mAs far as the gauge or thickness of the cable is concerned, this will depend upon the maximum quantity of power to be moved and the voltage.
If you wish to supply 3kW of power at 240 Volts AC, then the maximum current would be 3000/240 = 12.5 Amps.
To move the same 3kW at 50 Volts DC would require a current flow of 3000/50 = 60 Amps.
If you look at the current carrying capacity of different sized cable you should find the one that would meet the task.
It's a Solis 3.6kw hybrid inverter, so has a nominal 5kw max output at 48/50 vDC, which from the above would imply 100 Amps/thereabouts.
I need about 8m of length so a 1AWG or 0 AWG to be on the safe side?
25mm² cable would give 2.56% (1.23 volts) drop based on 48V, 100A and 8m.
35mm² 1.87% (0.896 volts) drop
Doesn't look like you need (50mm²)
Posted by: @puff1AWG or 0 AWG to be on the safe side?
Check your manual for max volt drop.
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 516 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
Thanks and apologies if I was a bit lazy...I have not p...
By Batpred , 1 hour ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@plasfron Hi there! Yes your Mitsubishi heat pump needs...
By HCas , 3 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
The recent ZeroDisrupt discussions reminded me to take ...
By Mars , 3 hours ago
-
RE: What is the Heat Geek Guarantee?
@colinc, that’s a very fair and well-balanced comment, ...
By Mars , 4 hours ago
-
@toodles Thanks. I will assume they have made som...
By Papahuhu , 4 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Oh come on, that's a ridiculous argument by an installe...
By JamesPa , 5 hours ago
-
RE: Say hello and introduce yourself
I've seen photos of other people placing the tank in a ...
By Transparent , 6 hours ago
-
RE: PV Panels on roof in Conservation Area
@colinc Do your own due diligence re reviews etc but...
By Morgan , 6 hours ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
So true, possibly with the exception of people you woul...
By JamesPa , 7 hours ago
-
RE: Isolating the system for a planned power cut
I hadn't realised your reason for a 100mA trip was due ...
By Transparent , 7 hours ago
-
RE: Midea ASHP – how to set weather compensation
Some things worth mentioning: (1) the Headroom Heat P...
By cathodeRay , 7 hours ago
-
RE: Heating Turned Off but Radiators Still Warm
@9jwr9 I didn't get an answer at the time and there has...
By Pipcart , 8 hours ago
-
RE: Battery storage to run Heat Pump.
@majordennisbloodnok I’m not sure you will be able to r...
By Toodles , 8 hours ago
-
RE: Renewables & Heat Pumps in the News
You've completely missed the point. Old, unpatched so...
By Majordennisbloodnok , 9 hours ago
-
RE: Ecodan Energy Monitoring Pack
@batpred that’s an idea yes. Will look into it
By Carpenterstation , 9 hours ago
-
-
PUHZ SW120Y & EHSC-VM2D - Buffer tank to Volumiser
Eventually I was able to find someone here in the Algar...
By DavidAlgarve , 9 hours ago
-
RE: Anyone still weathering it out with Agile?
We are still on agile and it works ok'ish to charge the...
By Batpred , 9 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Ah... now I can see a photo,and that changes the advice...
By Transparent , 12 hours ago