Battery Storage Wiring Gauge Question
I'm looking to get an Seplos Mason 280/LF304 battery bundle (15kwh) and I want to place it in a little outhouse attached to the side of the main house - mainly for fire prevention reasons but it's also damned heavy! The Solis inverter is in the loft...
What is the maximum length of cable I can run between the two please? I'll obviously get the correct gauge but can't get my head around what that gauge needs to be.
Posted by: @puffWhat is the maximum length of cable I can run between the two please?
As long as you like, you have to watch overall voltage drop on the DC side less than the AC. (Assume you are running in DC). I am running PV cables 40m in DC no issue, in AC it would have been quite costly and I may have had voltage drop issues.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @puffI'm looking to get an Seplos Mason 280/LF304 battery bundle (15kwh) and I want to place it in a little outhouse attached to the side of the main house - mainly for fire prevention reasons but it's also damned heavy! The Solis inverter is in the loft...
What is the maximum length of cable I can run between the two please? I'll obviously get the correct gauge but can't get my head around what that gauge needs to be.
As far as the gauge or thickness of the cable is concerned, this will depend upon the maximum quantity of power to be moved and the voltage.
If you wish to supply 3kW of power at 240 Volts AC, then the maximum current would be 3000/240 = 12.5 Amps.
To move the same 3kW at 50 Volts DC would require a current flow of 3000/50 = 60 Amps.
If you look at the current carrying capacity of different sized cable you should find the one that would meet the task.
Posted by: @derek-mAs far as the gauge or thickness of the cable is concerned, this will depend upon the maximum quantity of power to be moved and the voltage.
If you wish to supply 3kW of power at 240 Volts AC, then the maximum current would be 3000/240 = 12.5 Amps.
To move the same 3kW at 50 Volts DC would require a current flow of 3000/50 = 60 Amps.
If you look at the current carrying capacity of different sized cable you should find the one that would meet the task.
It's a Solis 3.6kw hybrid inverter, so has a nominal 5kw max output at 48/50 vDC, which from the above would imply 100 Amps/thereabouts.
I need about 8m of length so a 1AWG or 0 AWG to be on the safe side?
25mm² cable would give 2.56% (1.23 volts) drop based on 48V, 100A and 8m.
35mm² 1.87% (0.896 volts) drop
Doesn't look like you need (50mm²)
Posted by: @puff1AWG or 0 AWG to be on the safe side?
Check your manual for max volt drop.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 15 Online
- 3,312 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@damon thank you for posting. Would you care to tell ...
By JamesPa , 6 hours ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
Braver person than me. No way I would go down that rout...
By Johnmo , 8 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Well my switch from eon is tomorrow/Monday so I’ll soon...
By Westkent , 12 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 15 hours ago
-
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@johnmo I have been looking at the daily Agile rates fo...
By Toodles , 18 hours ago
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 19 hours ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 1 day ago
-
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 3 days ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 3 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 4 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 4 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 4 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 4 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 5 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 5 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 5 days ago