RE: ASHP and how it should run and potential kw consumption?

OK I did some very crude energy balance calculations attached. I had to make lots of assumptions, some of which matter to the outcome, many of which ...

8 months ago
Reply
RE: ASHP and how it should run and potential kw consumption?

@jeegnesh Thanks. One last question then I'll do some back of the envelope calculations tomorrow. Please confirm what times of day you are r...

8 months ago
Reply
RE: Hitachi Yutaki M efficient operation

I dont know, unless water is circulating in the UFH much faster than its coming out of the heat pump so basically its going round and round the UFH be...

8 months ago
Reply
RE: Hitachi Yutaki M efficient operation

@iraknic the buffer tank or pipe losses. It sounds like a classic case of excess mixing in the tank. That said not sure how accurate the or guns are...

8 months ago
Reply
RE: ASHP and how it should run and potential kw consumption?

@jeegnesh wow . exactly which rooms are too cold if you run at the 'downstairs' flow temperature.

8 months ago
Reply
RE: Totally bewildered with my ECO4 heat pump installation

The Vaillant WC interface is actually much more user friendly than most. You can do it without your installer (which doesnt excuse him not helping). ...

8 months ago
Reply
RE: ASHP and how it should run and potential kw consumption?

I was saying The latter not the former - pick a heat curve suited for upstairs, but see my final comment below before and please respond you do anythi...

8 months ago
Reply
RE: ASHP and how it should run and potential kw consumption?

Its a complex system, probably over complex to be sensible and certainly too complex to work out what might happen with any certainty if you change op...

8 months ago
Reply
RE: ASHP and how it should run and potential kw consumption?

You could be right. What do you know of the design/history of the heating system (not the heat pump, the emitter system). Its quite bizarre that the...

8 months ago
Reply
RE: How much radiator capacity do I need for an air source heat pump?

Agreed, Put another way it may sometimes be better to heat the house to a slightly higher temperature to avoid cycling. I can easily believe that is...

8 months ago
Reply
RE: ASHP and how it should run and potential kw consumption?

Im not surprised, two differnt heat curves will likely confuse it. I have only 1 and have turned off all autoadaption or room temp compensation and e...

8 months ago