help sizing rads based on room by room heat loss
scratching my head a bit as to what size rad i need for a given room based on its heat loss. the system is designed to 40c flow @-3.1c outside. lots of sites list rad outputs based on delta t50, is this the flow temp? so if i can find out the output at dt40 for instance is that the output i need to match to this chart?
With a flow of 40C the dT for a 20C room temp is 20 it’s the difference in temp between flow and room. The output of a rad at dT 20 is 0.3 of its output at dT50
so why dont sites list the output based on flow temp? cause most seem to use dt.
Posted by: @adamkso why dont sites list the output based on flow temp? cause most seem to use dt.
Because they don't know your room temperature and it's only (average) DT that matters
Posted by: @adamkso does that mean at a dt of 50 the actual flow is 70c for a 20c room temp?
Not strictly I think. It's 20 plus half the DT between flow and return so that the average dt rad to room is 50
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @garyYep exactly that
jees ive got 2 hopes of heating my bathroom then. someone suggested an standard design aluminium rad, instead of a towel rad, but im worried in a copper and steel setup ill get galvanic corrosion.
I just left the old towel rail which is now way underpowered. I am relying on heat transfer from the adjacent hallway, which has excess capacity, together with steam when you run a bath/shower. It works just fine - the level of thermal separation between rooms is quite modest in practice.
Obviously this is house dependent but more than one prospective installer remarked to me that they frequently do not install a 'fully compliant' radiator in a bathroom (because of the low output of and desire for towel rails).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
can i ask then if i have a heat loss for a room of 1079w and a flow of 40c@-3.1c what wattage rad do i need to hit? cause at the moment im struggling to find one big enough that would fit in the space.
The output of a rad is proportional to DT to the power 1.3, where DT is the average temperature difference between rad and room.
At a flow temperature of 40, and assuming a room temperature of 20 and a temp drop across the radiator of 5, DT is 37.5-20=17.5
Radiators are usually specified for a DT of 50. So you will need a rad with an output at DT 50 of (50/17.5) to the power 1.3 x 1079W = 3.9x1079W=4.2kW.
That's a mighty big radiator. What room is this in? Consider more than one radiator or a fan radiator if the loss really is that high.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Posted by: @adamk@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Have you got the loss calculations, if so perhaps you could post?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,227 Topics
- 49.5 K Posts
- 96 Online
- 5,892 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa tonight I’ve set the senso to 21 (it’s set to ...
By AdamK , 2 hours ago
-
So my plans when installing the 8kw solis and 16kwh sep...
By Batpred , 5 hours ago
-
RE: Electricity price predictions
I forgot to comment on the government referring to Sili...
By Batpred , 7 hours ago
-
RE: Options on flushing my system
@editor Yeah I watched the episode and am probably goin...
By Grantmethestrength , 7 hours ago
-
RE: Rate the quality of your heat pump design and installation
@bimbleuk good to hear a good install story!
By Grantmethestrength , 8 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
@toodles Useful reply and because Heat Geek mentioned i...
By bimbleuk , 11 hours ago
-
RE: How good is the app support for your heat pump?
Yes. Personally I would only use a heating control app ...
By Batpred , 12 hours ago
-
RE: Replacing knackered oil boiler with Samsung ASHP - Perthshire
The Legionella disinfection is done by the immersion he...
By Mike H , 12 hours ago
-
RE: Renewables & Heat Pumps in the News
@transparent Yup, should have been better to say, wh...
By Batpred , 13 hours ago
-
RE: Forum updates, announcements & issues
@editor Hardly worth taking up the memory space for a p...
By Toodles , 13 hours ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
@bubuontheweb Very useful to know, and I can feel th...
By Batpred , 14 hours ago
-
RE: How to add a new topic to the forums & unsubscribe from forum email notifications
@old_scientist, that doesn't exist presently... I will ...
By Mars , 14 hours ago
-
When will fusion be producing energy?
We got on a sidetrack elsewhere but best to create it h...
By Batpred , 14 hours ago
-
RE: Rodents! A word of warning for heat pump owners
Useful and timely reminder!
By Tim441 , 15 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@lucia, I appreciate the feedback, and we’ve received a...
By Mars , 21 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
I hope out of all of this that I can run the system at ...
By Crimson , 21 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Daikin Altherma 3M - 4kW (R32 2022 Release) (EDLA04E2V3...
By bimbleuk , 22 hours ago
-
RE: Twin 10kw Grant Aerona Volumiser Tanks using lots of power
The Grant Aerona3 external volumisers are insulated uni...
By Grantmethestrength , 1 day ago