help sizing rads based on room by room heat loss

17 Posts
3 Users
2 Reactions
291 Views
(@adamk)
Estimable Member Member
Joined: 2 months ago
Posts: 68
Topic starter  

scratching my head a bit as to what size rad i need for a given room based on its heat loss. the system is designed to 40c flow @-3.1c outside. lots of sites list rad outputs based on delta t50, is this the flow temp? so if i can find out the output at dt40 for instance is that the output i need to match to this chart?

image

   
Quote
 Gary
(@gary)
Prominent Member Member
Joined: 2 years ago
Posts: 336
 

With a flow of 40C the dT for a 20C room temp is 20 it’s the difference in temp between flow and room.  The output of a rad at dT 20 is 0.3 of its output at dT50


   
ReplyQuote
(@adamk)
Estimable Member Member
Joined: 2 months ago
Posts: 68
Topic starter  

so why dont sites list the output based on flow temp? cause most seem to use dt.


   
ReplyQuote



(@adamk)
Estimable Member Member
Joined: 2 months ago
Posts: 68
Topic starter  

@gary so does that mean at a dt of 50 the actual flow is 70c for a 20c room temp?


   
ReplyQuote
 Gary
(@gary)
Prominent Member Member
Joined: 2 years ago
Posts: 336
 

Yep exactly that 


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2350
 

Posted by: @adamk

so why dont sites list the output based on flow temp? cause most seem to use dt.

Because they don't know your room temperature and it's only (average) DT that matters

Posted by: @adamk

so does that mean at a dt of 50 the actual flow is 70c for a 20c room temp?

Not strictly I think.  It's 20 plus half the DT between flow and return so that the average dt rad to room is 50

 

 

This post was modified 3 weeks ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@adamk)
Estimable Member Member
Joined: 2 months ago
Posts: 68
Topic starter  

Posted by: @gary

Yep exactly that 

jees ive got 2 hopes of heating my bathroom then. someone suggested an standard design aluminium rad, instead of a towel rad, but im worried in a copper and steel setup ill get galvanic corrosion.

 


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2350
 

I just left the old towel rail which is now way underpowered.  I am relying on heat transfer from the adjacent hallway, which has excess capacity, together with steam when you run a bath/shower.  It works just fine - the level of thermal separation between rooms is quite modest in practice. 

Obviously this is house dependent but more than one prospective installer remarked to me that they frequently do not install a 'fully compliant' radiator in a bathroom (because of the low output of and desire for towel rails).

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@adamk)
Estimable Member Member
Joined: 2 months ago
Posts: 68
Topic starter  

can i ask then if i have a heat loss for a room of 1079w and a flow of 40c@-3.1c what wattage rad do i need to hit? cause at the moment im struggling to find one big enough that would fit in the space.


   
ReplyQuote



(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2350
 

The output of a rad is proportional to DT to the power 1.3, where DT is the average temperature difference between rad and room.

At a flow temperature of 40, and assuming a room temperature of 20 and a temp drop across the radiator of 5, DT is 37.5-20=17.5

Radiators are usually specified for a DT of 50.  So you will need a rad with an output at DT 50 of (50/17.5) to the power 1.3 x 1079W = 3.9x1079W=4.2kW.

That's a mighty big radiator.  What room is this in?  Consider more than one radiator or a fan radiator if the loss really is that high.

This post was modified 5 days ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@adamk)
Estimable Member Member
Joined: 2 months ago
Posts: 68
Topic starter  

@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2350
 

Posted by: @adamk

@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.

Have you got the loss calculations, if so perhaps you could post?

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Page 1 / 2
Share:

Join Us!

Trusted Installers

Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.

✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available

👉 Find your installer now!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security