help sizing rads based on room by room heat loss
scratching my head a bit as to what size rad i need for a given room based on its heat loss. the system is designed to 40c flow @-3.1c outside. lots of sites list rad outputs based on delta t50, is this the flow temp? so if i can find out the output at dt40 for instance is that the output i need to match to this chart?
With a flow of 40C the dT for a 20C room temp is 20 it’s the difference in temp between flow and room. The output of a rad at dT 20 is 0.3 of its output at dT50
so why dont sites list the output based on flow temp? cause most seem to use dt.
Posted by: @adamkso why dont sites list the output based on flow temp? cause most seem to use dt.
Because they don't know your room temperature and it's only (average) DT that matters
Posted by: @adamkso does that mean at a dt of 50 the actual flow is 70c for a 20c room temp?
Not strictly I think. It's 20 plus half the DT between flow and return so that the average dt rad to room is 50
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @garyYep exactly that
jees ive got 2 hopes of heating my bathroom then. someone suggested an standard design aluminium rad, instead of a towel rad, but im worried in a copper and steel setup ill get galvanic corrosion.
I just left the old towel rail which is now way underpowered. I am relying on heat transfer from the adjacent hallway, which has excess capacity, together with steam when you run a bath/shower. It works just fine - the level of thermal separation between rooms is quite modest in practice.
Obviously this is house dependent but more than one prospective installer remarked to me that they frequently do not install a 'fully compliant' radiator in a bathroom (because of the low output of and desire for towel rails).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
can i ask then if i have a heat loss for a room of 1079w and a flow of 40c@-3.1c what wattage rad do i need to hit? cause at the moment im struggling to find one big enough that would fit in the space.
The output of a rad is proportional to DT to the power 1.3, where DT is the average temperature difference between rad and room.
At a flow temperature of 40, and assuming a room temperature of 20 and a temp drop across the radiator of 5, DT is 37.5-20=17.5
Radiators are usually specified for a DT of 50. So you will need a rad with an output at DT 50 of (50/17.5) to the power 1.3 x 1079W = 3.9x1079W=4.2kW.
That's a mighty big radiator. What room is this in? Consider more than one radiator or a fan radiator if the loss really is that high.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Posted by: @adamk@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Have you got the loss calculations, if so perhaps you could post?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,367 Topics
- 53.7 K Posts
- 243 Online
- 6,042 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Interesting question. To be frank, since I have no inte...
By Majordennisbloodnok , 2 hours ago
-
RE: Changing from 4-port buffer to volumizer
@andy1618 see the very sage advice from @editor above. ...
By JamesPa , 12 hours ago
-
RE: New Fogstar 15.5kWh upright solution
The video shows the JK balancer, but the connection of ...
By Batpred , 14 hours ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 Hi, yes this is the issue with every (stand alon...
By ASHP-BOBBA , 15 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk FWIW I managed unintentionally to 'coax' mine in...
By JamesPa , 16 hours ago
-
RE: Help needed with Grant Aerona 3 issues
Ok please post back once experiment complete. Give it ...
By JamesPa , 16 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
You are in essence right. Adia only works with selecte...
By JamesPa , 17 hours ago
-
No, you haven’t missed out, @batpred. This thread’ll st...
By Majordennisbloodnok , 17 hours ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
Also, though they weren’t prepared to match the price t...
By Toodles , 18 hours ago
-
RE: How long will your energy contract last?
My INTELLI-FIX-12M-25-08-29 has less than 12 months to ...
By Batpred , 18 hours ago
-
RE: GivEnergy 2025 forthcoming batteries and inverters
Then, perhaps @toodles , you should've made a submissio...
By Transparent , 19 hours ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I am wondering if anyone with an EV could find the 7p/k...
By Batpred , 19 hours ago
-
Possibly, but it would also reduce DeltaT across the em...
By JamesPa , 19 hours ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@cathoderay It was reminiscent of the BBC Open Universi...
By Toodles , 19 hours ago
-
-
@morgan They are unsupervised these days, can’t get the...
By Toodles , 4 days ago
-
RE: Setback savings - fact or fiction?
Exactly. We only need to compare conditions, to decide ...
By cathodeRay , 5 days ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Welcome @mickamills We too have an oversized 12kW Sa...
By Old_Scientist , 5 days ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
@caron I can confirm that the power usage of the PW3 is...
By Old_Scientist , 5 days ago