help sizing rads based on room by room heat loss
scratching my head a bit as to what size rad i need for a given room based on its heat loss. the system is designed to 40c flow @-3.1c outside. lots of sites list rad outputs based on delta t50, is this the flow temp? so if i can find out the output at dt40 for instance is that the output i need to match to this chart?
With a flow of 40C the dT for a 20C room temp is 20 it’s the difference in temp between flow and room. The output of a rad at dT 20 is 0.3 of its output at dT50
so why dont sites list the output based on flow temp? cause most seem to use dt.
Posted by: @adamkso why dont sites list the output based on flow temp? cause most seem to use dt.
Because they don't know your room temperature and it's only (average) DT that matters
Posted by: @adamkso does that mean at a dt of 50 the actual flow is 70c for a 20c room temp?
Not strictly I think. It's 20 plus half the DT between flow and return so that the average dt rad to room is 50
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @garyYep exactly that
jees ive got 2 hopes of heating my bathroom then. someone suggested an standard design aluminium rad, instead of a towel rad, but im worried in a copper and steel setup ill get galvanic corrosion.
I just left the old towel rail which is now way underpowered. I am relying on heat transfer from the adjacent hallway, which has excess capacity, together with steam when you run a bath/shower. It works just fine - the level of thermal separation between rooms is quite modest in practice.
Obviously this is house dependent but more than one prospective installer remarked to me that they frequently do not install a 'fully compliant' radiator in a bathroom (because of the low output of and desire for towel rails).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
can i ask then if i have a heat loss for a room of 1079w and a flow of 40c@-3.1c what wattage rad do i need to hit? cause at the moment im struggling to find one big enough that would fit in the space.
The output of a rad is proportional to DT to the power 1.3, where DT is the average temperature difference between rad and room.
At a flow temperature of 40, and assuming a room temperature of 20 and a temp drop across the radiator of 5, DT is 37.5-20=17.5
Radiators are usually specified for a DT of 50. So you will need a rad with an output at DT 50 of (50/17.5) to the power 1.3 x 1079W = 3.9x1079W=4.2kW.
That's a mighty big radiator. What room is this in? Consider more than one radiator or a fan radiator if the loss really is that high.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Posted by: @adamk@jamespa thanks for the info but I think I must have something wrong. The heat loss for the whole house is about 7.5kw. The room is only 3.756m x 3.686m. Current rad is a P+ 1450mm 380mm.
Have you got the loss calculations, if so perhaps you could post?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,096 Topics
- 46.1 K Posts
- 73 Online
- 3,383 Members
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Mitsubishi cycling while on chilled water output
Yes, but hopefully only for a few days of the year. If...
By JamesPa , 1 hour ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 3 hours ago
-
RE: Weather compensated secondary circuits with Biomass
Hi @andycoo we do an LK 110 standalone weather compensa...
By Sune , 4 hours ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 22 hours ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 22 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
Can we have some links to those you're considering plea...
By Transparent , 23 hours ago
-
RE: Commencing on an ASHP Installation Process
That outside pipework would concern me. Surely rigid se...
By benson , 2 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 2 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 3 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 3 days ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
@m1kegibson If you are able to access the service me...
By HarriUp , 3 days ago
-
RE: When will heat pumps and install prices come down?
... which of course is impossible because the world mov...
By JamesPa , 3 days ago
-
RE: Battery storage to run Heat Pump.
I would be surprised if the battery chemistry is going ...
By Transparent , 4 days ago