Delta T with a Low Loss Header
My installer told me that the Delta T attaining 5 degrees was not so critical when employing an LLH, I have been tinkering with the speed of the secondary pump in our Daikin based system and would appreciate the views of members in this forum.
I have a Wilo Pico pump and have been trying to achieve DT 5 but find generally that with the pump at mid speed, I achieve approx DT 2.5; slowing the pump makes little difference on most of the 10 radiators (plus a dual fuel towel rail) though one achieves approx 5.2, the others are still 2-3 at best. I would like to know two things:
1. Does the degree of ‘openess’ (i.e. how much constriction the lockshield valve applies) affect the DT across that radiator?
2. How critical is achieving a DT of 5 when using an LLH after all? Is my installer right?
Slightly Curious, Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodlesMy installer told me that the Delta T attaining 5 degrees was not so critical when employing an LLH, I have been tinkering with the speed of the secondary pump in our Daikin based system and would appreciate the views of members in this forum.
I have a Wilo Pico pump and have been trying to achieve DT 5 but find generally that with the pump at mid speed, I achieve approx DT 2.5; slowing the pump makes little difference on most of the 10 radiators (plus a dual fuel towel rail) though one achieves approx 5.2, the others are still 2-3 at best. I would like to know two things:
1. Does the degree of ‘openess’ (i.e. how much constriction the lockshield valve applies) affect the DT across that radiator?
2. How critical is achieving a DT of 5 when using an LLH after all? Is my installer right?
Slightly Curious, Regards, Toodles.
1. yes (provided that its open enough for some flow!). The more open, the bigger the flow through the rad, the lower the DT on that rad.
2. I don't think it is critical. with the LLH its more important to try to balance the flow rates on each side of the LLH (for which the primary tool is pump speed) to optimise for LLH distortion (see heatgeek). Are you able to do that?
balancing for same DT across all radiators is really a boiler thing.
In a HP setup (unless you have perfect plumbing and perfect radiator sizing), your DT across each rad will be slightly different : you want to balance the radiators so they all get the right amount of flow to output the amount of heat that the room needs when HP is running constantly. which will inevitably mean not all radiator DT's are the same.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thank you Ian, I’ll look for that heat geek presentation later; I have watched many of Adam’s presentations and they are very informative - even if his flamboyance does run away with him occasionally! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I have had a look at Heat Geek’s presentations and articles that I could find and the nearest to the topic of llh distortion was a quote “Another issue that might arise from the process of hydraulic separation is distortion. This is when higher temperatures are needed at the boiler as a means of getting the emitters (e.g., radiators or/and underfloor heating) to an appropriate temperature should the flow rates differ on either end of the low loss header.” I’m not quite sure how to interpret this but assume one should aim to balance rather than distort (i.e., reduce any difference in temperature differences between the heat pump input to the LLH and the emitter-side of the LLH) I have probably got this completely wrong! Am I aiming to set the secondary pump speed to reduce the differential on the LLH ‘sides’ or set speed to achieve a certain difference please? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodlesI have had a look at Heat Geek’s presentations and articles that I could find and the nearest to the topic of llh distortion was a quote “Another issue that might arise from the process of hydraulic separation is distortion. This is when higher temperatures are needed at the boiler as a means of getting the emitters (e.g., radiators or/and underfloor heating) to an appropriate temperature should the flow rates differ on either end of the low loss header.” I’m not quite sure how to interpret this but assume one should aim to balance rather than distort (i.e., reduce any difference in temperature differences between the heat pump input to the LLH and the emitter-side of the LLH) I have probably got this completely wrong! Am I aiming to set the secondary pump speed to reduce the differential on the LLH ‘sides’ or set speed to achieve a certain difference please? Regards, Toodles.
If my understanding of the theory is correct, the flow from the heat pump into the LLH needs to be slightly higher than the flow coming out of the LLH and going to the heat emitters. That way the temperature of the water going to the heat emitters should be the same as that coming from the heat pump, and the heat pump controller will regulate the quantity of thermal energy it produces to match the heat demand from the heat emitters.
@toodles this diagram
flow rates the same = temperatures the same.
flow rate higher on the radiator side: has to pull from one of the lower (cold) inputs to serve the rads -> rad temps lower - > heat to house lower - > have to run higher LWT on heat pump -> much lower efficiency in the HP
flow rate higher on the heat pump side: RWT to heat pump goes up so heat pump may back off (stop producing heat) as it "sees" a reduced load and so think its has no work to do. But so long as they are not too close, and flow rate is high enough , it won't back off.
optimal: the same
next best thing (given that optimal is nigh on impossible) : bit higher on the heat pump side.
i.e. what derek-m said
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Ok, I get the gist of the requirement now, ideally matching - probably impossible, especially as the primary pump is variable speed itself. Slightly lower flow on the emitter side should produce a reasonable compromise that keeps efficiency near the ideal. Looks like I need to see what flow rate the primary pump produces (on average) and set the secondary just below this figure. ‘`fun for the whole family’ might ensue! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles so the other gotcha with dropping the pump power on the secondary side is that it will run at lower head , which means your "harder to reach" radiators become less likely to stay in the active circuit. there might not be enough push for the flow to reach them. unless you have really well balanced rads and low head-loss plumbing this can be a factor. one to be aware off. if you know which rads is the "furthest away in plumbing terms" (a.k.a index radiator) make sure you check that if/when you lower pump power.
I'm actually tuning my own system to a slightly higher flow rate at the moment (I have no LLH of course) for this exact reason.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank I’m reasonably confident this won’t be a problem on my system; the furthest point has had to be throttled well back on the lockshield valve to the point that it is perhaps an eighth of a turn from fully shut. Some radiators are fully open* and others at various degrees (pun intended!) of open. I have spent some hours over the months tweaking these radiators and none are near straining to heat the area fortunately. Of course, I have had umpteen changes as the system was commissioned in mid-February in mild weather so I have had a number of rounds of tweaks, no radiator runs out of puff so to speak. Homely has probably noticed some of my tweaks and so time is allowed to elapse between tweaking and evaluation of the results!
*We like a warm bathroom, so this radiator is totally unrestricted providing us with 24.5 - 25.5 degrees in the evenings. ‘Fun’ will be had! Regards and Thanks, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Fun has been had, and the Daikin pump reports that it is pumping ~ 15 litres/min. The Wilo pump works in cubic metres/h so….. taking 60 x 15 litres =900 litres so I have set the secondary pump (radiator side of the LLH) for 0.8 cubic metres/hour for the present. Strange though it may seem, this is the speed I had set the pump after the commissioning and I was balancing the radiators initially! Some may wonder why me not the installlers? Well, I wanted the settings ‘finessed’ to my own satisfaction and they were commissioning late on a Friday afternoon - need I say more? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I've been bending my brain trying to balance my LLH (Grant install one by default these days it seems - I suspect to ease the installer's job from what I've read) and didn't really follow the Heat Geek article. I've found this web-page easier to understand (maybe Heat Geek borrowed from it, or vice versa) and it explains how the ratio of temperatures on either side are affected by the flow rates.
Grant Aerona 3 10kW
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 77 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
It's INSANE how wrong they have the sizing (and even sh...
By BAMi , 46 seconds ago
-
RE: Towel rails. An unexpected final hurdle. Resolved
@jamespa Solved thanks to your help. I found a ladder t...
By Davesoa , 50 seconds ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 58 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 1 hour ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 3 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 4 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 15 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 18 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 19 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 22 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 23 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 24 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 4 hours ago
-
SolarPV tables / online calculator
By MichelleC 11 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 23 hours ago
-
By Toodles 2 days ago