Delta T with a Low Loss Header
My installer told me that the Delta T attaining 5 degrees was not so critical when employing an LLH, I have been tinkering with the speed of the secondary pump in our Daikin based system and would appreciate the views of members in this forum.
I have a Wilo Pico pump and have been trying to achieve DT 5 but find generally that with the pump at mid speed, I achieve approx DT 2.5; slowing the pump makes little difference on most of the 10 radiators (plus a dual fuel towel rail) though one achieves approx 5.2, the others are still 2-3 at best. I would like to know two things:
1. Does the degree of ‘openess’ (i.e. how much constriction the lockshield valve applies) affect the DT across that radiator?
2. How critical is achieving a DT of 5 when using an LLH after all? Is my installer right?
Slightly Curious, Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodlesMy installer told me that the Delta T attaining 5 degrees was not so critical when employing an LLH, I have been tinkering with the speed of the secondary pump in our Daikin based system and would appreciate the views of members in this forum.
I have a Wilo Pico pump and have been trying to achieve DT 5 but find generally that with the pump at mid speed, I achieve approx DT 2.5; slowing the pump makes little difference on most of the 10 radiators (plus a dual fuel towel rail) though one achieves approx 5.2, the others are still 2-3 at best. I would like to know two things:
1. Does the degree of ‘openess’ (i.e. how much constriction the lockshield valve applies) affect the DT across that radiator?
2. How critical is achieving a DT of 5 when using an LLH after all? Is my installer right?
Slightly Curious, Regards, Toodles.
1. yes (provided that its open enough for some flow!). The more open, the bigger the flow through the rad, the lower the DT on that rad.
2. I don't think it is critical. with the LLH its more important to try to balance the flow rates on each side of the LLH (for which the primary tool is pump speed) to optimise for LLH distortion (see heatgeek). Are you able to do that?
balancing for same DT across all radiators is really a boiler thing.
In a HP setup (unless you have perfect plumbing and perfect radiator sizing), your DT across each rad will be slightly different : you want to balance the radiators so they all get the right amount of flow to output the amount of heat that the room needs when HP is running constantly. which will inevitably mean not all radiator DT's are the same.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thank you Ian, I’ll look for that heat geek presentation later; I have watched many of Adam’s presentations and they are very informative - even if his flamboyance does run away with him occasionally! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I have had a look at Heat Geek’s presentations and articles that I could find and the nearest to the topic of llh distortion was a quote “Another issue that might arise from the process of hydraulic separation is distortion. This is when higher temperatures are needed at the boiler as a means of getting the emitters (e.g., radiators or/and underfloor heating) to an appropriate temperature should the flow rates differ on either end of the low loss header.” I’m not quite sure how to interpret this but assume one should aim to balance rather than distort (i.e., reduce any difference in temperature differences between the heat pump input to the LLH and the emitter-side of the LLH) I have probably got this completely wrong! Am I aiming to set the secondary pump speed to reduce the differential on the LLH ‘sides’ or set speed to achieve a certain difference please? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodlesI have had a look at Heat Geek’s presentations and articles that I could find and the nearest to the topic of llh distortion was a quote “Another issue that might arise from the process of hydraulic separation is distortion. This is when higher temperatures are needed at the boiler as a means of getting the emitters (e.g., radiators or/and underfloor heating) to an appropriate temperature should the flow rates differ on either end of the low loss header.” I’m not quite sure how to interpret this but assume one should aim to balance rather than distort (i.e., reduce any difference in temperature differences between the heat pump input to the LLH and the emitter-side of the LLH) I have probably got this completely wrong! Am I aiming to set the secondary pump speed to reduce the differential on the LLH ‘sides’ or set speed to achieve a certain difference please? Regards, Toodles.
If my understanding of the theory is correct, the flow from the heat pump into the LLH needs to be slightly higher than the flow coming out of the LLH and going to the heat emitters. That way the temperature of the water going to the heat emitters should be the same as that coming from the heat pump, and the heat pump controller will regulate the quantity of thermal energy it produces to match the heat demand from the heat emitters.
@toodles this diagram
flow rates the same = temperatures the same.
flow rate higher on the radiator side: has to pull from one of the lower (cold) inputs to serve the rads -> rad temps lower - > heat to house lower - > have to run higher LWT on heat pump -> much lower efficiency in the HP
flow rate higher on the heat pump side: RWT to heat pump goes up so heat pump may back off (stop producing heat) as it "sees" a reduced load and so think its has no work to do. But so long as they are not too close, and flow rate is high enough , it won't back off.
optimal: the same
next best thing (given that optimal is nigh on impossible) : bit higher on the heat pump side.
i.e. what derek-m said
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Ok, I get the gist of the requirement now, ideally matching - probably impossible, especially as the primary pump is variable speed itself. Slightly lower flow on the emitter side should produce a reasonable compromise that keeps efficiency near the ideal. Looks like I need to see what flow rate the primary pump produces (on average) and set the secondary just below this figure. ‘`fun for the whole family’ might ensue! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles so the other gotcha with dropping the pump power on the secondary side is that it will run at lower head , which means your "harder to reach" radiators become less likely to stay in the active circuit. there might not be enough push for the flow to reach them. unless you have really well balanced rads and low head-loss plumbing this can be a factor. one to be aware off. if you know which rads is the "furthest away in plumbing terms" (a.k.a index radiator) make sure you check that if/when you lower pump power.
I'm actually tuning my own system to a slightly higher flow rate at the moment (I have no LLH of course) for this exact reason.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank I’m reasonably confident this won’t be a problem on my system; the furthest point has had to be throttled well back on the lockshield valve to the point that it is perhaps an eighth of a turn from fully shut. Some radiators are fully open* and others at various degrees (pun intended!) of open. I have spent some hours over the months tweaking these radiators and none are near straining to heat the area fortunately. Of course, I have had umpteen changes as the system was commissioned in mid-February in mild weather so I have had a number of rounds of tweaks, no radiator runs out of puff so to speak. Homely has probably noticed some of my tweaks and so time is allowed to elapse between tweaking and evaluation of the results!
*We like a warm bathroom, so this radiator is totally unrestricted providing us with 24.5 - 25.5 degrees in the evenings. ‘Fun’ will be had! Regards and Thanks, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Fun has been had, and the Daikin pump reports that it is pumping ~ 15 litres/min. The Wilo pump works in cubic metres/h so….. taking 60 x 15 litres =900 litres so I have set the secondary pump (radiator side of the LLH) for 0.8 cubic metres/hour for the present. Strange though it may seem, this is the speed I had set the pump after the commissioning and I was balancing the radiators initially! Some may wonder why me not the installlers? Well, I wanted the settings ‘finessed’ to my own satisfaction and they were commissioning late on a Friday afternoon - need I say more? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I've been bending my brain trying to balance my LLH (Grant install one by default these days it seems - I suspect to ease the installer's job from what I've read) and didn't really follow the Heat Geek article. I've found this web-page easier to understand (maybe Heat Geek borrowed from it, or vice versa) and it explains how the ratio of temperatures on either side are affected by the flow rates.
Grant Aerona 3 10kW
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 77 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
It's a known technique and heat pump manufacturers even...
By JamesPa , 1 hour ago
-
My Samsung Gen6 (probably same controller as yours) onl...
By Old_Scientist , 3 hours ago
-
@drei When I was in local government we were of cours...
By JamesPa , 3 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 5 hours ago
-
RE: Boiling Mad: Exposing Radiatorgate
@rob-nezard you can see more of Drei's rad dramas here ...
By Mars , 5 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@drei I will say again that Im sorry to heat about your...
By JamesPa , 6 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 17 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 18 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 19 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 21 hours ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 22 hours ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 1 day ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 1 day ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 2 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 2 days ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 2 days ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 3 days ago