Delta T with a Low Loss Header
My installer told me that the Delta T attaining 5 degrees was not so critical when employing an LLH, I have been tinkering with the speed of the secondary pump in our Daikin based system and would appreciate the views of members in this forum.
I have a Wilo Pico pump and have been trying to achieve DT 5 but find generally that with the pump at mid speed, I achieve approx DT 2.5; slowing the pump makes little difference on most of the 10 radiators (plus a dual fuel towel rail) though one achieves approx 5.2, the others are still 2-3 at best. I would like to know two things:
1. Does the degree of ‘openess’ (i.e. how much constriction the lockshield valve applies) affect the DT across that radiator?
2. How critical is achieving a DT of 5 when using an LLH after all? Is my installer right?
Slightly Curious, Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodlesMy installer told me that the Delta T attaining 5 degrees was not so critical when employing an LLH, I have been tinkering with the speed of the secondary pump in our Daikin based system and would appreciate the views of members in this forum.
I have a Wilo Pico pump and have been trying to achieve DT 5 but find generally that with the pump at mid speed, I achieve approx DT 2.5; slowing the pump makes little difference on most of the 10 radiators (plus a dual fuel towel rail) though one achieves approx 5.2, the others are still 2-3 at best. I would like to know two things:
1. Does the degree of ‘openess’ (i.e. how much constriction the lockshield valve applies) affect the DT across that radiator?
2. How critical is achieving a DT of 5 when using an LLH after all? Is my installer right?
Slightly Curious, Regards, Toodles.
1. yes (provided that its open enough for some flow!). The more open, the bigger the flow through the rad, the lower the DT on that rad.
2. I don't think it is critical. with the LLH its more important to try to balance the flow rates on each side of the LLH (for which the primary tool is pump speed) to optimise for LLH distortion (see heatgeek). Are you able to do that?
balancing for same DT across all radiators is really a boiler thing.
In a HP setup (unless you have perfect plumbing and perfect radiator sizing), your DT across each rad will be slightly different : you want to balance the radiators so they all get the right amount of flow to output the amount of heat that the room needs when HP is running constantly. which will inevitably mean not all radiator DT's are the same.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thank you Ian, I’ll look for that heat geek presentation later; I have watched many of Adam’s presentations and they are very informative - even if his flamboyance does run away with him occasionally! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I have had a look at Heat Geek’s presentations and articles that I could find and the nearest to the topic of llh distortion was a quote “Another issue that might arise from the process of hydraulic separation is distortion. This is when higher temperatures are needed at the boiler as a means of getting the emitters (e.g., radiators or/and underfloor heating) to an appropriate temperature should the flow rates differ on either end of the low loss header.” I’m not quite sure how to interpret this but assume one should aim to balance rather than distort (i.e., reduce any difference in temperature differences between the heat pump input to the LLH and the emitter-side of the LLH) I have probably got this completely wrong! Am I aiming to set the secondary pump speed to reduce the differential on the LLH ‘sides’ or set speed to achieve a certain difference please? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodlesI have had a look at Heat Geek’s presentations and articles that I could find and the nearest to the topic of llh distortion was a quote “Another issue that might arise from the process of hydraulic separation is distortion. This is when higher temperatures are needed at the boiler as a means of getting the emitters (e.g., radiators or/and underfloor heating) to an appropriate temperature should the flow rates differ on either end of the low loss header.” I’m not quite sure how to interpret this but assume one should aim to balance rather than distort (i.e., reduce any difference in temperature differences between the heat pump input to the LLH and the emitter-side of the LLH) I have probably got this completely wrong! Am I aiming to set the secondary pump speed to reduce the differential on the LLH ‘sides’ or set speed to achieve a certain difference please? Regards, Toodles.
If my understanding of the theory is correct, the flow from the heat pump into the LLH needs to be slightly higher than the flow coming out of the LLH and going to the heat emitters. That way the temperature of the water going to the heat emitters should be the same as that coming from the heat pump, and the heat pump controller will regulate the quantity of thermal energy it produces to match the heat demand from the heat emitters.
@toodles this diagram
flow rates the same = temperatures the same.
flow rate higher on the radiator side: has to pull from one of the lower (cold) inputs to serve the rads -> rad temps lower - > heat to house lower - > have to run higher LWT on heat pump -> much lower efficiency in the HP
flow rate higher on the heat pump side: RWT to heat pump goes up so heat pump may back off (stop producing heat) as it "sees" a reduced load and so think its has no work to do. But so long as they are not too close, and flow rate is high enough , it won't back off.
optimal: the same
next best thing (given that optimal is nigh on impossible) : bit higher on the heat pump side.
i.e. what derek-m said
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Ok, I get the gist of the requirement now, ideally matching - probably impossible, especially as the primary pump is variable speed itself. Slightly lower flow on the emitter side should produce a reasonable compromise that keeps efficiency near the ideal. Looks like I need to see what flow rate the primary pump produces (on average) and set the secondary just below this figure. ‘`fun for the whole family’ might ensue! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles so the other gotcha with dropping the pump power on the secondary side is that it will run at lower head , which means your "harder to reach" radiators become less likely to stay in the active circuit. there might not be enough push for the flow to reach them. unless you have really well balanced rads and low head-loss plumbing this can be a factor. one to be aware off. if you know which rads is the "furthest away in plumbing terms" (a.k.a index radiator) make sure you check that if/when you lower pump power.
I'm actually tuning my own system to a slightly higher flow rate at the moment (I have no LLH of course) for this exact reason.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank I’m reasonably confident this won’t be a problem on my system; the furthest point has had to be throttled well back on the lockshield valve to the point that it is perhaps an eighth of a turn from fully shut. Some radiators are fully open* and others at various degrees (pun intended!) of open. I have spent some hours over the months tweaking these radiators and none are near straining to heat the area fortunately. Of course, I have had umpteen changes as the system was commissioned in mid-February in mild weather so I have had a number of rounds of tweaks, no radiator runs out of puff so to speak. Homely has probably noticed some of my tweaks and so time is allowed to elapse between tweaking and evaluation of the results!
*We like a warm bathroom, so this radiator is totally unrestricted providing us with 24.5 - 25.5 degrees in the evenings. ‘Fun’ will be had! Regards and Thanks, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Fun has been had, and the Daikin pump reports that it is pumping ~ 15 litres/min. The Wilo pump works in cubic metres/h so….. taking 60 x 15 litres =900 litres so I have set the secondary pump (radiator side of the LLH) for 0.8 cubic metres/hour for the present. Strange though it may seem, this is the speed I had set the pump after the commissioning and I was balancing the radiators initially! Some may wonder why me not the installlers? Well, I wanted the settings ‘finessed’ to my own satisfaction and they were commissioning late on a Friday afternoon - need I say more? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I've been bending my brain trying to balance my LLH (Grant install one by default these days it seems - I suspect to ease the installer's job from what I've read) and didn't really follow the Heat Geek article. I've found this web-page easier to understand (maybe Heat Geek borrowed from it, or vice versa) and it explains how the ratio of temperatures on either side are affected by the flow rates.
Grant Aerona 3 10kW
- 22 Forums
- 2,030 Topics
- 44.2 K Posts
- 57 Online
- 3,235 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 By way of further explanation, in coolin...
By Heatgeek , 1 hour ago
-
I'm just trying to imagine this construction approach @...
By Transparent , 1 hour ago
-
Yes, can do that, though I ran the heating again from c...
By rhh2348 , 1 hour ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 2 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 2 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 5 hours ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 15 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
I since checked the magnetic filter again and there was...
By Phoenix15 , 15 hours ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 23 hours ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 2 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@old_scientist As another example of errors / differenc...
By Toodles , 2 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
Is this something you are thinking of doing? Or has thi...
By Cliff-Arnold , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@agentgeorge Not with Eon Next. The only reson I left O...
By Andris , 3 days ago
-
Is this normal? Click of the DHW returning to space heating
This has been bugging me for a while and I just wanted ...
By Grantmethestrength , 4 days ago
-
@sandman1600 you need to measure whats going on real...
By davidnolan22 , 5 days ago
-
@brandon-r is this a project that you could assist with...
By Mars , 5 days ago
-
Has anyone installed these on their ASHP fed radiator s...
By Grantmethestrength , 6 days ago