Convert Pt1000 to NTC 20 kΩ?
Posted by: @derek-mWhat is the problem with the old controller?
It works fine but the integration with the rest of the system is rather clumsy. For solar back off, a relay in the SKSC2 drives a contactor which adds a resistor that makes the the thermal store appear to the system controller to be hotter than it really is. Also the RESOL DL2 data logger attached to the SKSC2 has died. Both the SKSC2 and RESOL DL2 were installed around 15 years ago.
My current thoughts are to replace my existing Viessmann Vitodens 200-W (type WB2C) with the latest version (type B2HF). The existing uses KM Bus and the latest version uses PlusBus so the wall mounted mixer extension will need to change. It seems like a good time to also change the solar controller to achieve better integration. I'm considering a Vitotrol 300-E as well. Might also replace the solar pump (how long do they last?). The upgrade should be straightforward, apart from the solar collector sensor ...
Posted by: @djhPosted by: @john-connettThe Pt1000 Resistance Table is straightforward. NTC Thermistors, Resistance/Temperature Conversion is more complex. I know it should measure 20 kΩ at 25°C but I'm not sure which of the 17 curves to apply?
Using the curve in the Viessmann guide you can see that the resistance at 140°C is about 0.5. So Rt/R25 is 0.025. You can then look at your 17 curves and see what the best match is. You could just estimate an approximate equation to match the Viessmann curve instead of trying to emulate an actual device. Or ask Viessmann what device it is?
Good suggestion. I am in the process of doing something similar to see which of the 15 (1-14, 17) Vishay curves is a good fit (It will also be interesting to see how the Ohmigo NTC 20 kΩ table compares). A table from Viessmann would have been more convenient for the comparison than the log/linear graph. However, solar thermal doesn't need as high precision as some other processes.
There are also some Vishay Tools that might be useful.
I asked OHMIGO® what curve they used for their NTC 20 kΩ table and received a very swift and useful reply:
There are small variations between suppliers and control manufacturers - most of the NTC values were created from 3rd party suppliers like Produal... the differences in ohms and even so in 'C are small.
Ohmonwifi allows you to set your own table between 'C and ohm. There is an excel spreadsheet on ohmonwifi
A reply from Vishay:
your inquiry: "Are you aware of a device or method of converting the resistance output from a Pt1000 sensor to the equivalent resistance output of an NTC 20 kΩ sensor? Background. The existing solar thermal system in my house has a Pt1000 sensor in a solar thermal collection on the roof. I am considering replacing the solar controller with a Viessmann model which uses an NTC 20 kΩ sensor. The Pt1000 sensor on the roof is difficult to access so I am investigating if it will be possible to reuse it with something to convert its resistance to the NTC 20 kΩ equivalent. My background is in systems software so this is well outside my comfort zone! Vishay's answer: if those circuits are out of your comfort zone, I suggest you do not start to modify them and take contact with the suppliers of those systems and ask them for advice. Converting RTD sensors (Pt1000) signals to be read as an NTC is not advisable.
- 26 Forums
- 2,242 Topics
- 49.9 K Posts
- 131 Online
- 5,903 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Precisely my view and why I use the term 'sense check'....
By JamesPa , 7 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@judith This is very interesting. I've located and prin...
By Mike Patrick , 7 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
@radwhisperer Thanks but that is definitely not a mixer...
By Jancold , 10 hours ago
-
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
OK thats cheap, the commercial price seems to be £400 p...
By JamesPa , 15 hours ago
-
RE: Solar inverters - where does the energy go when clipping?
I think I must query the sources on which Greenmatch ha...
By Transparent , 18 hours ago
-
RE: Replacing knackered oil boiler with Samsung ASHP - Perthshire
This is how I run my Samsung 12kW ASHP with a 3rd party...
By Old_Scientist , 20 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay thanks- yes will keep an eye out for the de...
By benson , 1 day ago
-
RE: Renewables & Heat Pumps in the News
Hoping so as well! I am no specialist. The language use...
By Batpred , 1 day ago
-
Do you need the DHW tank as high as 50°C @egp01 ? Ha...
By Transparent , 1 day ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@old_scientist Just to say that during our retrofit, we...
By Toodles , 2 days ago
-
RE: Daikin Altherma 3M ASHP and British Gas Hive Home
We have a Daikin EDLA08 8kW monobloc (DHW is handled se...
By Toodles , 2 days ago
-
@old_scientist @jamespa So this was last nights DHW r...
By bontwoody , 2 days ago
-
-
@springswood we install these nationwide and I have the...
By dgclimatecontrol , 2 days ago
-
RE: DESNZ doing a survey which asks the right questions!
Fair comment. I have a feeling that ratings more gen...
By JamesPa , 2 days ago
-
Thanks! My consumer unit collection is ready with the W...
By Batpred , 2 days ago
-
RE: Designing my house system with a mix of air to air and air to water
@jamespa Cheers James, it's great reading. In quite a f...
By pipebaron , 2 days ago
-
RE: PV Panels on roof in Conservation Area
If there is any way you can determine daily oil consump...
By JamesPa , 2 days ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
attached is prelagged in case indicates anything. &nb...
By Crimson , 2 days ago