Boiling Mad: Exposing Radiatorgate
Imagine buying a car advertised as reaching 30 miles per gallon, only to discover it barely manages 10. Now, imagine that happening not just with your car, but with your radiators, and that the "overstated mileage" translates to higher heating bills and missed climate goals. This shocking reality is playing out right now across the UK.
Misleading Metrics
Many consumers assume UK regulations safeguard against false advertising. Unfortunately, when it comes to radiator heat output, that's not the case. Millions of radiators are sold annually with inflated heat claims, often exceeding 25% of the actual output. This discrepancy isn't a minor quibble; it impacts heating efficiency, leading to higher bills and missed Net Zero targets.
The Investigation Begins
To uncover the truth, we purchased five radiators from five different UK websites, each acclaimed for their high heat outputs. The objective was simple: test these radiators at a regulated lab and compare their actual heat outputs to those advertised.
We drove the rads to BSRIA (Building Services Research and Information Association), a leading authority in testing, who conducted the evaluations. Their testing environment – a specialised, unventilated booth with water-cooled surfaces – ensures accuracy, free from external environmental influences. Radiators were measured and tested over an 8-hour period, with continuous data collection.
Spoiler Alert
The results, when they arrived, were as bad as we had anticipated, and in some cases, even worse, leaving us unsurprised yet deeply concerned:
- Radiator 1: Advertised output: 953 Watts (3250 BTUs); Actual output: 760 Watts (2592 BTUs); Overstated by 25%
- Radiator 2: Advertised output: 1026 Watts (3500 BTUs); Actual output: 786 Watts (2680 BTUs); Overstated by 31%
- Radiator 3: Advertised output: 927 Watts (3160 BTUs); Actual output: 738 Watts (2517 BTUs); Overstated by 26%
- Radiator 4: Advertised output: 988 Watts (3371 BTUs); Actual output: 716 Watts (2442 BTUs); Overstated by a whopping 38%
- Radiator 5: Advertised output: 889 Watts (3034 BTUs); Actual output: 712 Watts (2428 BTUs); Overstated by 25%
A Widespread Issue Beyond Sample Size
The results from these five radiators are a small representation of a much larger issue plaguing the UK radiator market. With millions of units potentially sold with exaggerated heat outputs, the economic and environmental impact is profound. Consumers face higher bills, and the nation's Net Zero targets become harder to achieve due to increased energy wastage.
These findings also raise critical questions about regulatory enforcement and consumer protection. The overstated outputs not only lead to financial losses for consumers but also betray the trust placed in regulatory compliances and standards.
The Need for Urgent Action
Our investigation underscores a pressing necessity for government and regulatory intervention. It's imperative that regulations are not just present, but vigorously upheld to safeguard consumer interests and maintain the integrity of the market. This issue transcends mere deceptive sales practices; it touches upon the wider ramifications for energy efficiency and the stewardship of our environment.
The radiator heat output scandal in the UK is a wake-up call for consumers, businesses and regulators alike. It underscores the importance of rigorous testing and transparent marketing. As consumers, it's vital to stay informed and demand accountability. Sharing this article, supporting the petition below and calling for regulatory action are steps we can take to bring about change. Together, we can confront this issue, protect consumer interests and contribute to a more sustainable future.
We would like to call upon the readers and members of Renewable Heating Hub to actively spread the word about this vital concern. Please share this article and support our petition for regulatory reform at UK Radiators.com. Your voice can make a difference in bringing an end to this deceitful practice and paving the way for a more honest and efficient market.
Disgraceful situation, especially when using heat pumps as they runt at a lower temperature, has this been sent to the ASA , Trading Standards or Government? well done for doing the testing.
Just wanted to highlight that there is a petition you can sign at UK Radiators.com
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Unfortunately we have a situation at present where the various bodies are pointing fingers at each other as to who is responsible. Our petition aims to address this by going to the DBT and DESNZ directly, as they have the authority to determine who needs to take action. If you could sign it would be very much appreciated 🙏 https://ukradiators.com/blogs/buying-guides/the-lie-costing-britain-billions#signpetition
Sorry, but where exactly is it possible to sign the petition? URL please. I can't find it; certainly not at the link you already gave - that seems to just link to a PDF.
@Dave, this link takes you a page with the petition at the bottom: UK Radiators.com
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi Dave, the petition form is just above where the letter is but it does take a second to load.
Both flow rates and temperatures affect output, and I doubt BSRIA has the technology to match them to design specifications.
Manufactures have failings but distorting the truth is not one of them.
their failings are that they don’t explain themselves, the “intellectual capital” around radiators performance is not explained. And people jump to the wrong conclusions.
Professional installer
Hi Alec, thanks for your comment, I appreciate your perspective on this and you are correct that flow temperature affects output. This is why radiators are delta rated, so that it's clear that the radiator outputs different amounts at different temperatures.
BSEN442 - the regulation that governs the manufacturer and sale of radiators, dictates that radiators must be tested by a notified body (BSRIA is the only one in the UK) and advertised using the rated thermal outputs at both Delta 50 and Delta 30.
The problem with these radiators is that they are being advertised with heat outputs that far exceed the rated thermal outputs achieved during testing. So in these cases (and many others), yes the manufacturers are distorting the truth.
If you have not done so, please watch the 7 minute documentary we produced (available on our website on the link above) as the evidence speaks for itself.
Happy to chat further or answer any questions you may have.
Thanks again
Rob
-
What is this white plastic ring on my radbots?
2 weeks ago
-
Reusing existing radiators
2 months ago
-
Eskimo Column Radiator – Fronze Finish
1 year ago
-
Convector options for a small kitchen
2 years ago
-
Stelrad radiators
4 years ago
- 21 Forums
- 1,959 Topics
- 42.5 K Posts
- 21 Online
- 2,272 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
SolarPV tables / online calculator
Is there some table or an online calculator that I can ...
By MichelleC , 3 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
Same here @jamespa - we have a 12kW Samsung ASHP, solar...
By Old_Scientist , 6 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 6 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 7 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 8 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 10 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 12 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 14 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 15 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 16 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 19 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 20 hours ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 1 day ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 1 day ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 1 day ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@editor But do you wear your peaked cap the right way r...
By Toodles , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I’d be interested to hear the feedback and consensus on...
By Mars , 2 days ago
Latest Topics
-
SolarPV tables / online calculator
By MichelleC 3 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 15 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 18 hours ago
-
By Toodles 2 days ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago
-
Towel rails. An unexpected final hurdle
By Davesoa 2 days ago
-
By big_si 2 days ago