Boiling Mad: Exposing Radiatorgate
Imagine buying a car advertised as reaching 30 miles per gallon, only to discover it barely manages 10. Now, imagine that happening not just with your car, but with your radiators, and that the "overstated mileage" translates to higher heating bills and missed climate goals. This shocking reality is playing out right now across the UK.
Misleading Metrics
Many consumers assume UK regulations safeguard against false advertising. Unfortunately, when it comes to radiator heat output, that's not the case. Millions of radiators are sold annually with inflated heat claims, often exceeding 25% of the actual output. This discrepancy isn't a minor quibble; it impacts heating efficiency, leading to higher bills and missed Net Zero targets.
The Investigation Begins
To uncover the truth, we purchased five radiators from five different UK websites, each acclaimed for their high heat outputs. The objective was simple: test these radiators at a regulated lab and compare their actual heat outputs to those advertised.
We drove the rads to BSRIA (Building Services Research and Information Association), a leading authority in testing, who conducted the evaluations. Their testing environment – a specialised, unventilated booth with water-cooled surfaces – ensures accuracy, free from external environmental influences. Radiators were measured and tested over an 8-hour period, with continuous data collection.
Spoiler Alert
The results, when they arrived, were as bad as we had anticipated, and in some cases, even worse, leaving us unsurprised yet deeply concerned:
- Radiator 1: Advertised output: 953 Watts (3250 BTUs); Actual output: 760 Watts (2592 BTUs); Overstated by 25%
- Radiator 2: Advertised output: 1026 Watts (3500 BTUs); Actual output: 786 Watts (2680 BTUs); Overstated by 31%
- Radiator 3: Advertised output: 927 Watts (3160 BTUs); Actual output: 738 Watts (2517 BTUs); Overstated by 26%
- Radiator 4: Advertised output: 988 Watts (3371 BTUs); Actual output: 716 Watts (2442 BTUs); Overstated by a whopping 38%
- Radiator 5: Advertised output: 889 Watts (3034 BTUs); Actual output: 712 Watts (2428 BTUs); Overstated by 25%
A Widespread Issue Beyond Sample Size
The results from these five radiators are a small representation of a much larger issue plaguing the UK radiator market. With millions of units potentially sold with exaggerated heat outputs, the economic and environmental impact is profound. Consumers face higher bills, and the nation's Net Zero targets become harder to achieve due to increased energy wastage.
These findings also raise critical questions about regulatory enforcement and consumer protection. The overstated outputs not only lead to financial losses for consumers but also betray the trust placed in regulatory compliances and standards.
The Need for Urgent Action
Our investigation underscores a pressing necessity for government and regulatory intervention. It's imperative that regulations are not just present, but vigorously upheld to safeguard consumer interests and maintain the integrity of the market. This issue transcends mere deceptive sales practices; it touches upon the wider ramifications for energy efficiency and the stewardship of our environment.
The radiator heat output scandal in the UK is a wake-up call for consumers, businesses and regulators alike. It underscores the importance of rigorous testing and transparent marketing. As consumers, it's vital to stay informed and demand accountability. Sharing this article, supporting the petition below and calling for regulatory action are steps we can take to bring about change. Together, we can confront this issue, protect consumer interests and contribute to a more sustainable future.
We would like to call upon the readers and members of Renewable Heating Hub to actively spread the word about this vital concern. Please share this article and support our petition for regulatory reform at UK Radiators.com. Your voice can make a difference in bringing an end to this deceitful practice and paving the way for a more honest and efficient market.
Disgraceful situation, especially when using heat pumps as they runt at a lower temperature, has this been sent to the ASA , Trading Standards or Government? well done for doing the testing.
Just wanted to highlight that there is a petition you can sign at UK Radiators.com
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Unfortunately we have a situation at present where the various bodies are pointing fingers at each other as to who is responsible. Our petition aims to address this by going to the DBT and DESNZ directly, as they have the authority to determine who needs to take action. If you could sign it would be very much appreciated 🙏
Sorry, but where exactly is it possible to sign the petition? URL please. I can't find it; certainly not at the link you already gave - that seems to just link to a PDF.
@Dave, this link takes you a page with the petition at the bottom: UK Radiators.com
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi Dave, the petition form is just above where the letter is but it does take a second to load.
Both flow rates and temperatures affect output, and I doubt BSRIA has the technology to match them to design specifications.
Manufactures have failings but distorting the truth is not one of them.
their failings are that they don’t explain themselves, the “intellectual capital” around radiators performance is not explained. And people jump to the wrong conclusions.
Professional installer
Hi Alec, thanks for your comment, I appreciate your perspective on this and you are correct that flow temperature affects output. This is why radiators are delta rated, so that it's clear that the radiator outputs different amounts at different temperatures.
BSEN442 - the regulation that governs the manufacturer and sale of radiators, dictates that radiators must be tested by a notified body (BSRIA is the only one in the UK) and advertised using the rated thermal outputs at both Delta 50 and Delta 30.
The problem with these radiators is that they are being advertised with heat outputs that far exceed the rated thermal outputs achieved during testing. So in these cases (and many others), yes the manufacturers are distorting the truth.
If you have not done so, please watch the 7 minute documentary we produced (available on our website on the link above) as the evidence speaks for itself.
Happy to chat further or answer any questions you may have.
Thanks again
Rob
-
What is this white plastic ring on my radbots?
5 months ago
-
Reusing existing radiators
6 months ago
-
Eskimo Column Radiator – Fronze Finish
1 year ago
-
Convector options for a small kitchen
2 years ago
-
Stelrad radiators
4 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 45 Online
- 3,393 Members
Latest Posts
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
Short video from Greg on the announcement
By Jeff , 2 hours ago
-
@bart That is terrible and a clear breach of the buildi...
By Brendon Uys , 4 hours ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@editor If it is of any interest, we had the BUS grant,...
By Toodles , 11 hours ago
-
Sorry to hear that @bruce. Sadly I’ve heard from multip...
By Mars , 21 hours ago
-
RE: Crystal Ball Time: Communal or even Area Energy Storage?
I am invested in a couple of listed energy storage fund...
By Old_Scientist , 23 hours ago
-
RE: Who's your electricity provider and what's your tariff?
That would be my biggest commitment -time to gain great...
By SUNandAIR , 1 day ago
-
RE: Who has a V2G EV installation
As has been discussed on other threads, trying to justi...
By Majordennisbloodnok , 2 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks @mikeh. Then I will also go back to non smart ta...
By ChandyKris , 2 days ago
-
RE: Location of hot water isolation valve on cylinder
@transparent Thank you so much and very helpful. Earlie...
By rossowheels , 3 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
It does indeed look like that, @skyefarmer. There is ...
By Majordennisbloodnok , 3 days ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 4 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 4 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 5 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 5 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 6 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 6 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 6 days ago