Solar panels not working correctly? what checks can I make?
I should mention one of the difficulties I had was the way the app updates with inverter & optmiser information every 15 minutes. Afaik I could not see a live output in real time
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@derek-m 🤣 🤣 too late!! I should have... especially I a couple of g&t in....
Sadly not fully conclusive. Not sure if it was me... g&t...or what!
For most part covering one panel dropped all others from say 40 to 50w down to single digits. I used cardboard that covered probably 90% of panel.... so not entirely decisive with such small outputs.
One panel was always on 0w whichever panel was covered. Odd? But if all panels uncovered was similar output as others.
We know the failed optimiser is not even registering. Can't help but wonder if I've more than one fault.
Will try again... but main thing is to replace the known failed optimiser
Have you seen the following document?
@derek-m thanks for that. No, I had not seen it before. Looks like that will help guide me on things to check.
As I previously had no monitoring setup it was near impossible. But now monitoring is basically working I feel I'm in with a chance.
- Hopefully the replacement optimiser arrives soon. I will also take the opportunity of checking the physical location of all optmisers as I've currently got them allocated randomly. All the right serial numbers... in the wrong order! Waiting for wind to drop and helper so I can remove each panel.
Plan is to test each optimiser and panel with a multimeter as well as check all connections (as you suggested earlier). Updating & correcting the physical layout.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
for good order... here is the official advice from Solaredge on the ethernet connection:
====================
Our advice will be to perform a power-cycle to both the inverter and the router first:
= Move the inverter's red toggle switch (on the bottom left) to the OFF position
= Wait 5 minutes and after that shut down the AC supply to the inverter (there should be an AC disconnect close to the inverter)
= Shut down the power supply to your house router
= Wait 5 minutes, then turn ON the power supply to the router
= Turn ON the inverter's AC supply
= Move the inverter's toggle switch to ON position
Then, if you are still not seeing all 1's, please verify the following with a call to your internet provider:
= Ensure there is no Firewall rule applied that might be blocking the inverter from communicating.
= Ensure that the following TCP ports: 22222 and 22221 have a 2-way communication open to:
http://prod.solaredge.com&source=gmail&ust=1685445391726000&usg=AOvVaw11Tb4imGeRBekq_Yb7-Po q">prod.solaredge.com
http://prod2.solaredge.com&source=gmail&ust=1685445391726000&usg=AOvVaw1uhpeY7WK11e72f-nkqkI h">prod2.solaredge.com
==================
i've tried that shutdown & restart too but so far no success so then I moved to the firewall rule.
Not sure what i'm doing!! But have gone into advanced settings for my BT hub router and added a "port forwarding rule" for external ports 22221 - 22222
not sure what internal ports should be set so just chose a couple of random ones.
so far no change. But almost certainly I've done something wrong?
also tried internal ports as 22221 - 22222 but no success so far
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
various updates:
- Solaredge pushed an inverter firmware update. Resulting in LAN connection now being seen including pings
11111111
I'm not sure if the firewall "issue" was just a red herring? probably ... as i think the firmware update made the difference not any other changes - Had a friend round to help me check all panels. Checked connections as suggested and tested any faulty looking optimisers (based on app monitoring). Took note of true physical layout of optimisers and updated app to show correct layout and serial numbers. Faulty optimiser moved to last (#8) in string. So 7 out of 8 working more or less correctly.
- With info from app I can see 7 panels producing around 1.45kwh in full sun soon after midday. With 7 x 285w panels the max in theory would be 2kwh. Does that seem reasonable?
- The 7 panels are operating with optimiser voltage 54 - 55v (most around 55v) and with output of 202 - 213w each (mostly around 210w)
does that seem reasonable?
for now my plan is to continue to monitor and then update the failed optimiser once replacement received
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
interesting to note that it was just after noon yesterday that system was running normally and production for the day was 9kw. Recent days had typically been between 3 and 4kw. So I'm hopeful that a full day in sun will be nearer 15kw. Maybe a bit more even. I will monitor in coming days.
I'm surprised that simply moving the faulty optimiser to last in string made such a difference? Not a problem obviously - but slightly interested to understand why that would be?!
Solaredge have confirmed replacement is shipped and will be here in around 1 week so will see what the impact is then. As the 8th panel is heavily shaded it may not add a lot.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
replacement optimiser arrived today. Installed and immediately significant jump in production compared to previous day at same time and same conditions. Even though the added panel is shaded. I guess the optimisers all like to "see" each other to play nicely. I expect peak production and full day production to also jump.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 This is something of a speculation, but with the faulty one in the middle, it may have been pulling the output down for all of those downstream of it. the optimisers (when working) are there to make sure that the post-optimisation output voltage of all panels is the same . you can see this if you walk around your panels in the monitoring portal - voltage will be the same for all, amps and watts will be lower if shaded.
really glad to see you got the solaredge monitoring working and are seeing the benefit. there are so many benefits to monitoring of all the forms of renewable energy tech that I think it should be mandatory with any and all of them.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Looking good! Yes, I will use the monitoring in coming days to get a good feel of how it should be working
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441replacement optimiser arrived today. Installed and immediately significant jump in production compared to previous day at same time and same conditions. Even though the added panel is shaded. I guess the optimisers all like to "see" each other to play nicely. I expect peak production and full day production to also jump.
The optimisers are DC to DC converters, though I am not certain if it is the voltage from each panel that they are trying to balance or the current. Do you know if they are wired in parallel or series?
I don't think that optimisers were available when my panels were installed over 10 years ago, but I do believe that each of my panels contain bypass diodes, which are designed to prevent each string being affected by a shaded panel. The panels are configured as two parallel strings, of 8 panels in series, which can develop a voltage of 400v DC at the input of the inverter, when each panel produces a nominal voltage of 50v DC.
I was therefore surprised to read, when you stated previously, that shading each panel in turn affected the output from all the other panels, which is not what I would have expected.
mine is the same type of system as tim's. here's snapshot of one of my panels just now (its not sunny).
current is more or less the same for all panels. optimised voltage is a different value to panel voltage in pretty much all panels.
they are in series, they vary voltage to achieve nominal 400v for the string and to balance current. actual DC voltage at the inverter right now is 390v despite no sun.
some decent wiring diagrams and explanations here
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
i'm wondering if I've still got a fault... currently cloudy here
#8 was the faulty one that was recently replaced
Perhaps #1 is also faulty?
Optimiser Current Optimiser voltage Power Voltage
1 1.14 36.75 36.97 32.5
2 1.83 51.12 55.89 30.62
3 1.92 54.75 59 30.75
4 2.06 55.38 62.46 30.38
5 1.92 56.12 58.28 30.38
6 2.04 53.75 61.31 30
7 1.94 53.38 59.28 30.5
8 0.59 15.62 19.52 32.88
Notes:
Optimiser 8 is shaded most of the day
A chimney & gable to the east part shades 1-7 and gradually clears so that #1 is finally unshaded by midday
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
-
Cleaning solar PV panels? to increase output
2 years ago
-
PV without battery storage?
3 years ago
-
Solar PV quotes - 4.9 kW system but 3.6 kW inverter?
3 years ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 591 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Setback savings - fact or fiction?
@sunandair I don't want to get embroiled in an argument...
By JamesPa , 2 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
I think most heat pumps have this mode but I cant see h...
By JamesPa , 23 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa cannot find loss calculation. When they get i...
By BAMi , 40 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 1 hour ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 4 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 5 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 7 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 18 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 20 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 22 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 7 hours ago
-
SolarPV tables / online calculator
By MichelleC 14 hours ago
-
By Toodles 2 days ago