We are looking to install ASHP for our Edwardian detached home. Had a few heat surveys which tend to recommend a 12kW ASHP. However, rule of thumb from Dr Modesta and our annual 22MWh gas consumption indicates only 5kW heat loss. (Our home is well insulated, EPC = B). So my question is...What is the disadvantages of oversizing and would it be smart to compromise at say 8kW ASHP?
Thank you for any ideas and to Mars for this excellent resource.
Rules of thumb are generally pretty rubbish for heat pump sizing and your gas usage patterns may or may not be a good indication.
Common theme seems to be you need 12kW. But the average house in the UK actually only needs sub 6kW.
I would ask to see the heat loss calculation and review it and pass comments back. Number of air changes per hour can be just daft for example, taking no notice of fabric improvements also. Do you have evidence of fabric improvements - without they may have just ignored etc.
General disadvantage of oversizing
Heat pump cycling
Large heat pumps need very high flow rates, so end up with big pipes, or a buffer (not good for efficiency), bigger radiators than needed etc. So everything gets bigger than needed, you also get a bigger bill than needed, to pay for all that bigger stuff.
The correct size is max heat loss plus an allowance for DHW heating. So if your heat loss was 5kW, or 120kWh a day being able to deliver 120kWh in say 22 hrs. So 5.5kW being able to be delivered at your outside design temperature.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
In addition to the above oversizing means you are likely to be running the compressor at an inefficient point on it's modulation curve for much of the time, reducing COP.
My personal view, which differs a bit from @johnmo, is that gas readings, properly interpreted, can (but won't always) provide the only solid upper bound on heat loss available, so are well worth factoring in in addition to surveys, possibly only as a sense check but possibly as the prime source (depending on circumstances such as how the house is currently heated)
However I agree rules of thumb aren't sufficient, you need a bit more. Do you have smart meter readings, they can tell you a lot more. What's your pattern of heating and how old is your boiler, that can help interpret the has readings more intelligently.
I would also do what @johnmo suggests regarding the surveys.
Once you have that data put it all together to get the best data available.
Feel free to ask for more advice/post some of your data.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@johnmo thanks @johnmo that is great info - I will be discussing this with our best prospect installer.
I just needed some ideas to make it a discussion instead of a lecture!
So far I have just too much conflicting information:
1. Dr Modesta of the National Physics Lab in Teddington recommends using annual gas consumption (20MW) required to heat the house divided by Heating Degree Days at the local weather station - gives our heat loss 5kW
2. The "B" EPC estimates 18.5MWh to heat the house and water and the two surveyors are broadly the same.
3. Surveyors have estimated 10kW heat loss. But in the surveys, the ACHs seem unreasonably high (3 in bathrooms, loo & utility, 2 in kitchen, hall & landing, 1.5 in living & dining rooms and 1.0 in the bedrooms). I would expect the average ACH for our well draught-proofed house, especially in winter when we are careful with opening doors etc, to be under 1 and not the approx. 2 that is being used to exaggerate the ASHP sizing.
So what is right - the real world historical heating MW data and a world leading scientist or a detailed fabric heat loss estimation multiplied by MCS nonsensical ACHs?
Is there a heat geek approach to ACH that might sort this out?
many thanks
@jamespa thanks @jamespa. I really appreciate your thoughts on this.
Especially the benefits of not oversizing!
Our boiler is a condensing Worcester almost 10 years old and it does fine. We do have gas meter readings per month but not anything smarter. Annual consumption is a steady 22MWh.
Another thing that bothers me is that if a well installed ASHP can deliver SCOP of 4, why cant a 5kW heat pump deliver 20kW?
Posted by: @matwinif a well installed ASHP can deliver SCOP of 4, why cant a 5kW heat pump deliver 20kW?
I love it !
That's an excellent question for the Welcome topic!
The maths works the other way around from what you suppose.
The kW figure for the heat-pump is its output.
Thus a 12kW heat-pump would draw 3kW of electricity if it was operating with a SCOP of 4.0
... but 4kW input if the SCOP was only 3.0.
Save energy... recycle electrons!
Currently viewing this topic 4 users ( Mars, Steam Powered, Transparent, MatWin ) and 3 guests.
Recently viewed by users: Sheriff Fatman 1 minute ago.
- 22 Forums
- 2,061 Topics
- 45.1 K Posts
- 48 Online
- 3,324 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Say hello and introduce yourself
I love it ! That's an excellent question for the Welc...
By Transparent , 16 minutes ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
That's interesting, @grantmethestrength. I'm a little s...
By Majordennisbloodnok , 1 hour ago
-
@allyfish That's impressive. We are on a similar journe...
By ChandyKris , 3 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@johnmo I appreciate your willingness to help, however ...
By TechnoGeek , 4 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Hi, good to hear. To be honest, I've given up with the ...
By Profzarkov , 5 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
I feel like a record is on it's way this month. Scotlan...
By Andris , 23 hours ago
-
RE: Discharging battery to grid whilst charging EV
@majordennisbloodnok Well, I tried it and nothing burne...
By AndrewJ , 1 day ago
-
RE: Using AI to optimise your system
@marvinator80 Two of the best resources on Youtube that...
By Grantmethestrength , 1 day ago
-
And here's a follow up article on the same subject that...
By Mars , 2 days ago
-
RE: Renewables & Heat Pumps in the News
@johnmo Ours is powered from solar energy (with grid ba...
By Toodles , 2 days ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
I'm curious who you think are the reluctant ears. Cert...
By JamesPa , 3 days ago
-
RE: Commencing on an ASHP Installation Process
If that is the case then I would add to my earlier post...
By JamesPa , 3 days ago
-
RE: Battery sizing - How low can you go!
The second 6.5 kWh Growatt battery was installed today....
By ChandyKris , 4 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
So… I called them this morning and I’m up and running o...
By Westkent , 4 days ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Your system seems to be more modern than mine, mine was...
By abbote , 4 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
Braver person than me. No way I would go down that rout...
By Johnmo , 5 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 5 days ago
-
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 5 days ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 6 days ago