Error on Immersun – Error 8 Load Short Circuit
We've had a persistent error on our Immersun today – I've restarted it several times, and the cabling has remained untouched, so not sure what's causing it. No such error in the manual. Any thoughts anyone?
Error 8
LOAD SHORT-CIRCUIT
Check: Heater
Could it be telling me the immersion heater has stopped working?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Having a short circuit would cause the output current to increase to a high level, hence the Immersun unit shuts down the output to protect both the unit and the external circuitry. The cause could be a short circuit within the wiring or the immersion heater, or possibly within the Immersun unit itself.
If you have a isolation switch between the Immersun unit and the immersion heater then switch this off and see if the fault clears. This would indicate that the fault is at the immersion heater or the wiring connected to it.
If the fault is still present then switch off the power supply to the Immersun unit and disconnect the output cabling. Switch the power back on to the Immersun unit and if the fault is cleared then the short circuit is on the wiring from the Immersun unit to the isolation switch, or the isolation switch itself.
If the fault is still present then the problem is within the Immersun unit.
@derek-m, I left the unit off overnight (disconnected from power).
I turned it on this morning with the immersion connector removed, so only the Immersun was starting up. Within 2 minutes the same is back. Looks like I'll have to send a message to Immersun.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
As an update to this, Immersun's customer support was excellent. I ran some diagnostics at our end and the error persisted. Immersun organised for the unit to be collected by DPD – a week later it was returned, and it's working perfectly. So the error was related to the Immersun unit, not the immersion heater.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Yesterday, my Immersun screen started flashing with the same error message. 'ERROR 8. LOAD SHORT CCT, CHECK: HEATER.
Unfortunately my unit is 16months old and I have discovered is now out of warranty.
I contacted IMMERSUN, they say that is is unlikely to be the unit itself, and I should check the external equipment. I have checked the supply from the MCB @240v, I have checked the resistance of the load circuit from the (disconnected) plug at the Immersun and with the thermostat contact made, it is 20 Ohm which is correct for a 3kW heating element. Resistance to ground is 'OL' on my multimeter. What else could be externally wrong that might cause this to happen.
Any ideas would be greatly received.
Do you still get the fault when the immersion heater is disconnected or the thermostat contact is open? If the fault is still present, then it could be a cable fault or the Immersun unit itself.
@julesmp8 that’s not great news. We did a bunch of “tests” connecting and disconnecting the unit from the immersion. Throughout the process, we were in touch with Immersun, and they requested we send the unit back because there was a hardware issue, but they never disclosed what the problem was; contrary info to what they told you.
I would, however, work through Derek’s processes. He’s very good at getting to the root of the issue.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Thanks for the info.
As mentioned I have checked all the wiring and I cannot find any issue which would suggest an external short cct.
I have also powered the unit up with the load connector disconnected inside the Immersun but the exact same fault appears. Immersun have provided me with a procedure that performs a Factory Reset of the unit but that doesn't help either.
It seems to me that the fault has to be inside the unit but at a starting price of £169 for testing/ repairing this negates the whole reason for fitting the unit in the first place - to save money !
@julesmp8 we did the factory reset too, which didn't help. I really like the Immersion units because they look really well built (far prefer them to the Solar iBoost) but there does sadly appear to be an issue with the units.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editor@julesmp8 we did the factory reset too, which didn't help. I really like the Immersion units because they look really well built (far prefer them to the Solar iBoost) but there does sadly appear to be an issue with the units.
Did you get your faulty unit repaired? What was the fault?
Hi
So there appears to be only 2 options left available. Prepay Immersun £179, send the unit to them and hope they can fix it (they quote a 85 - 90% success rate; charging either way).
Buy something else to do the same thing.
Posted by: @derek-mDid you get your faulty unit repaired? What was the fault?
Yes, they repaired it. I enquired what the issue was but they said that they didn’t get a report from the repair team - it was clear they didn’t want to share what the cause was.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 32 Online
- 5,662 Members
Podcast Picks
Latest Posts
-
RE: Ecodan & MelCloud scheduling
I put the above question to Mitsu UK at the sme time as...
By DavidAlgarve , 17 minutes ago
-
@ashp-bobba interesting insights. We also chatted after...
By Mars , 1 hour ago
-
RE: Why so many sigenergi installer recommendations?
I’ve not come across this brand, but then again I don’t...
By Mars , 1 hour ago
-
Sanity check please. Battery storage and inverter sizing.
I had one installer essentially wanting to install a ti...
By AdamK , 11 hours ago
-
RE: Rodents! A word of warning for heat pump owners
The gaps and holes have reduced on heat pumps over the ...
By dgclimatecontrol , 16 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: EGP01 Manufacturer: Samsung Model: 8K...
By EGP01 , 19 hours ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 21 hours ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 22 hours ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 2 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 3 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 4 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 4 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 5 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 6 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 7 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 7 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 1 week ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 1 week ago