Error on Immersun – Error 8 Load Short Circuit
We've had a persistent error on our Immersun today – I've restarted it several times, and the cabling has remained untouched, so not sure what's causing it. No such error in the manual. Any thoughts anyone?
Error 8
LOAD SHORT-CIRCUIT
Check: Heater
Could it be telling me the immersion heater has stopped working?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Having a short circuit would cause the output current to increase to a high level, hence the Immersun unit shuts down the output to protect both the unit and the external circuitry. The cause could be a short circuit within the wiring or the immersion heater, or possibly within the Immersun unit itself.
If you have a isolation switch between the Immersun unit and the immersion heater then switch this off and see if the fault clears. This would indicate that the fault is at the immersion heater or the wiring connected to it.
If the fault is still present then switch off the power supply to the Immersun unit and disconnect the output cabling. Switch the power back on to the Immersun unit and if the fault is cleared then the short circuit is on the wiring from the Immersun unit to the isolation switch, or the isolation switch itself.
If the fault is still present then the problem is within the Immersun unit.
@derek-m, I left the unit off overnight (disconnected from power).
I turned it on this morning with the immersion connector removed, so only the Immersun was starting up. Within 2 minutes the same is back. Looks like I'll have to send a message to Immersun.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
As an update to this, Immersun's customer support was excellent. I ran some diagnostics at our end and the error persisted. Immersun organised for the unit to be collected by DPD – a week later it was returned, and it's working perfectly. So the error was related to the Immersun unit, not the immersion heater.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Yesterday, my Immersun screen started flashing with the same error message. 'ERROR 8. LOAD SHORT CCT, CHECK: HEATER.
Unfortunately my unit is 16months old and I have discovered is now out of warranty.
I contacted IMMERSUN, they say that is is unlikely to be the unit itself, and I should check the external equipment. I have checked the supply from the MCB @240v, I have checked the resistance of the load circuit from the (disconnected) plug at the Immersun and with the thermostat contact made, it is 20 Ohm which is correct for a 3kW heating element. Resistance to ground is 'OL' on my multimeter. What else could be externally wrong that might cause this to happen.
Any ideas would be greatly received.
Do you still get the fault when the immersion heater is disconnected or the thermostat contact is open? If the fault is still present, then it could be a cable fault or the Immersun unit itself.
@julesmp8 that’s not great news. We did a bunch of “tests” connecting and disconnecting the unit from the immersion. Throughout the process, we were in touch with Immersun, and they requested we send the unit back because there was a hardware issue, but they never disclosed what the problem was; contrary info to what they told you.
I would, however, work through Derek’s processes. He’s very good at getting to the root of the issue.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Thanks for the info.
As mentioned I have checked all the wiring and I cannot find any issue which would suggest an external short cct.
I have also powered the unit up with the load connector disconnected inside the Immersun but the exact same fault appears. Immersun have provided me with a procedure that performs a Factory Reset of the unit but that doesn't help either.
It seems to me that the fault has to be inside the unit but at a starting price of £169 for testing/ repairing this negates the whole reason for fitting the unit in the first place - to save money !
@julesmp8 we did the factory reset too, which didn't help. I really like the Immersion units because they look really well built (far prefer them to the Solar iBoost) but there does sadly appear to be an issue with the units.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editor@julesmp8 we did the factory reset too, which didn't help. I really like the Immersion units because they look really well built (far prefer them to the Solar iBoost) but there does sadly appear to be an issue with the units.
Did you get your faulty unit repaired? What was the fault?
Hi
So there appears to be only 2 options left available. Prepay Immersun £179, send the unit to them and hope they can fix it (they quote a 85 - 90% success rate; charging either way).
Buy something else to do the same thing.
Posted by: @derek-mDid you get your faulty unit repaired? What was the fault?
Yes, they repaired it. I enquired what the issue was but they said that they didn’t get a report from the repair team - it was clear they didn’t want to share what the cause was.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 21 Forums
- 1,761 Topics
- 37.6 K Posts
- 88 Online
- 2,052 Members
Join Us!
Latest Posts
-
RE: Smart meter installation – seamless or a potential nightmare?
The incomer cable probably only has a size-rating once ...
By Transparent , 3 minutes ago
-
RE: Samsung E911 intermittent issue
@netdonkey No pushing down needed, just unscrew little ...
By ASHP-BOBBA , 4 minutes ago
-
RE: How Many ASHPs Work Correctly From Commissioning Date ( The resolution page)
@editor Do you post the poll? on that thread as people ...
By ASHP-BOBBA , 17 minutes ago
-
RE: Samsung ASHP scheduling help
@broadsman : I'd suggest most of us here are looking fo...
By morh , 35 minutes ago
-
RE: Battery...Full house back up
Where is you distribution board? In the I would have ex...
By JohnR , 56 minutes ago
-
RE: Fitting heat pump plumbing and pipes in advance?
One more thought if you are doing a bathroom refurb and...
By JamesPa , 2 hours ago
-
RE: Fitting emitters with output greater than room heat loss.
The proof, of course, will be in the heating! My ASH...
By JamesPa , 2 hours ago
-
RE: Which system is most efficient...
OK. Im not going to be able to answer the question, bu...
By JamesPa , 2 hours ago
-
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@lokisam I am following this with interest as I also ha...
By Odynsfee , 12 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you give us an update on your tests?
By Mars , 14 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@editor Yes, it's their "Aira Generation 1" 8kW model: ...
By trungdong , 16 hours ago
-
RE: Samsung heat pump has arrived with damaged fins – do I accept it or send it back?
Hi guys thanks for the replies. So it seems when the...
By AdamC001 , 18 hours ago
-
RE: Reducing heat pump vibrations through flat roof
@patrickvito Hi Patrick, thanks so much for taking the ...
By sten_super , 1 day ago
-
RE: Noise Issues with our Ecodan 8.5kW WM85VAA air source heat pump
@athlonoc Its unlikely the FTC is controlling a 3rd par...
By ASHP-BOBBA , 1 day ago
-
RE: Mitsubishi Ecodan Produced energy showing 'INVALID'
Hello! I tried your idea and disabled the cooling funct...
By sorin , 1 day ago
-
RE: What should we do with our Aga?
@RobinBennett We also have an AGA. Oil fired that we...
By Morgan , 1 day ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Many thanks Mars, this will be my Christmas rea...
By Odd_Lion , 2 days ago
-
RE: Anyone have experience with Clivet (Midea?)? And monoblocks vs Splits?
@benson Good to hear!
By bigvibes , 2 days ago
-
RE: Very noisy Daikin Altherma
@editor I did not find a solution, and have pretty much...
By Zogy , 2 days ago
Latest Topics
-
By Jeff 3 hours ago
-
Which system is most efficient...
By bigvibes 2 days ago
-
What should we do with our Aga?
By RobinBennett 2 days ago
-
Reducing heat pump vibrations through flat roof
By sten_super 2 days ago
-
Fitting heat pump plumbing and pipes in advance?
By RobinBennett 2 days ago
-
By Broadsman 2 days ago
-
How to Clean a Y-Strainer Filter
By Mars 2 days ago