Error on Immersun – Error 8 Load Short Circuit
We've had a persistent error on our Immersun today – I've restarted it several times, and the cabling has remained untouched, so not sure what's causing it. No such error in the manual. Any thoughts anyone?
Error 8
LOAD SHORT-CIRCUIT
Check: Heater
Could it be telling me the immersion heater has stopped working?
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Having a short circuit would cause the output current to increase to a high level, hence the Immersun unit shuts down the output to protect both the unit and the external circuitry. The cause could be a short circuit within the wiring or the immersion heater, or possibly within the Immersun unit itself.
If you have a isolation switch between the Immersun unit and the immersion heater then switch this off and see if the fault clears. This would indicate that the fault is at the immersion heater or the wiring connected to it.
If the fault is still present then switch off the power supply to the Immersun unit and disconnect the output cabling. Switch the power back on to the Immersun unit and if the fault is cleared then the short circuit is on the wiring from the Immersun unit to the isolation switch, or the isolation switch itself.
If the fault is still present then the problem is within the Immersun unit.
@derek-m, I left the unit off overnight (disconnected from power).
I turned it on this morning with the immersion connector removed, so only the Immersun was starting up. Within 2 minutes the same is back. Looks like I'll have to send a message to Immersun.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
As an update to this, Immersun's customer support was excellent. I ran some diagnostics at our end and the error persisted. Immersun organised for the unit to be collected by DPD – a week later it was returned, and it's working perfectly. So the error was related to the Immersun unit, not the immersion heater.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Yesterday, my Immersun screen started flashing with the same error message. 'ERROR 8. LOAD SHORT CCT, CHECK: HEATER.
Unfortunately my unit is 16months old and I have discovered is now out of warranty.
I contacted IMMERSUN, they say that is is unlikely to be the unit itself, and I should check the external equipment. I have checked the supply from the MCB @240v, I have checked the resistance of the load circuit from the (disconnected) plug at the Immersun and with the thermostat contact made, it is 20 Ohm which is correct for a 3kW heating element. Resistance to ground is 'OL' on my multimeter. What else could be externally wrong that might cause this to happen.
Any ideas would be greatly received.
Do you still get the fault when the immersion heater is disconnected or the thermostat contact is open? If the fault is still present, then it could be a cable fault or the Immersun unit itself.
@julesmp8 that’s not great news. We did a bunch of “tests” connecting and disconnecting the unit from the immersion. Throughout the process, we were in touch with Immersun, and they requested we send the unit back because there was a hardware issue, but they never disclosed what the problem was; contrary info to what they told you.
I would, however, work through Derek’s processes. He’s very good at getting to the root of the issue.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Thanks for the info.
As mentioned I have checked all the wiring and I cannot find any issue which would suggest an external short cct.
I have also powered the unit up with the load connector disconnected inside the Immersun but the exact same fault appears. Immersun have provided me with a procedure that performs a Factory Reset of the unit but that doesn't help either.
It seems to me that the fault has to be inside the unit but at a starting price of £169 for testing/ repairing this negates the whole reason for fitting the unit in the first place - to save money !
@julesmp8 we did the factory reset too, which didn't help. I really like the Immersion units because they look really well built (far prefer them to the Solar iBoost) but there does sadly appear to be an issue with the units.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editor@julesmp8 we did the factory reset too, which didn't help. I really like the Immersion units because they look really well built (far prefer them to the Solar iBoost) but there does sadly appear to be an issue with the units.
Did you get your faulty unit repaired? What was the fault?
Hi
So there appears to be only 2 options left available. Prepay Immersun £179, send the unit to them and hope they can fix it (they quote a 85 - 90% success rate; charging either way).
Buy something else to do the same thing.
Posted by: @derek-mDid you get your faulty unit repaired? What was the fault?
Yes, they repaired it. I enquired what the issue was but they said that they didn’t get a report from the repair team - it was clear they didn’t want to share what the cause was.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,199 Topics
- 48.4 K Posts
- 87 Online
- 5,854 Members
Join Us!
Podcast Picks
Latest Posts
-
I really like this angle… it’s perfect for Installer, b...
By Mars , 2 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson - getting there - you need to put all the varia...
By cathodeRay , 2 hours ago
-
@old_scientist that was my feeling so long as the unuse...
By bontwoody , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
Thanks Lucia. I'll set aside some time to go through th...
By Transparent , 4 hours ago
-
RE: How to Understand Wiring Up a Heat Pump
@renewables345 you say you are 18 and I’m assuming you ...
By Judith , 6 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
Seems to be settling better now I'll leave it alone
By Jancold , 12 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
We do like the exhaust air heat pump as a centralised M...
By Steelbadger , 21 hours ago
-
RE: Solar Thermal DHW and ASHP
@kenbone how is your battery holding up Ken? Still goin...
By Mars , 22 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Old Samsung R410a unit 9kw, modbused controlled, let Ha...
By KenBone , 23 hours ago
-
RE: Replacement Inverter for old FIT system
@bontwoody I have a single string 3kW solar AC inverter...
By Old_Scientist , 1 day ago
-
Octopus removed our gas meter for free a couple of year...
By robl , 1 day ago
-
-
-
RE: Why Air Release Valves and Deaerators are Non-Negotiable
I think that's a key point. An air-release valve shou...
By Transparent , 1 day ago
-
RE: Say hello and introduce yourself
Hello everyone. My partner and I recently had a Bosch C...
By Steelbadger , 1 day ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
@pirate-rich there’s a lot to do and plan, and the wish...
By Mars , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk Its a bit complex: My 28mm primaries run for a...
By JamesPa , 2 days ago
-
Can you separate out the scop data between hot water an...
By Andrew J H , 2 days ago