10.5kW unit that needs a new compressor
Hi All - new to the forum, first post, so please be gentle. I'll provide my full journey to renewable redemption in due course, but to begin with Im looking for input from anyone that has had the recent misfortune of having to replace their GSHP compressor out of warranty. I couldnt see how to create as a new topic (?), or indeed an existing topic that was directly relevant, so please move if in the wrong place. Anyway, I have a 10.5kw unit that needs a new compressor - how much would you expect to pay including parts (compressor, R407C refrigerant/disposal, nitrogen, brazing materials, limescale remover), labour (technician time for problem diagnosis & replacement, & travel to South Cambs) and VAT (20%)?. Im trying to gauge the reasonableness of my current quote and to prep a short personal commentary on the potential repair and maintenance costs for heat pumps vs gas/oil, which I dont see well covered elsewhere. Thanks in advance for your thoughts, DelT
I'm not sure if you have enough information to expand on your description @delt ,
but why is it that brazing/welding/soldering would be required?
Is the nitrogen to facilitate that brazing in an oxygen-free environment, or because it's required to flush out the existing refrigerant?
Save energy... recycle electrons!
Thanks for the immediate reply. Short answer is I do not know - these are line items on the quote I have (I guess I should go back and ask for clarification). All I really know and understand is that the compressor unit has broken beyond repair and needs replacing - the company has listed these things as part of the job. Perhaps we should not get too distracted by the nitrogen & brazing materials since they are <3% of the total quote. I was hoping for some ball park estimates/range for comparison, but perhaps its not that easy?
Posted by: @transparentwhy is it that brazing/welding/soldering would be required?
When brazing copper refrigerant pipes, nitrogen is passed through the pipe to prevent oxidation (contamination) of the inside of the pipe, if I understand it correctly.
2021 built 2 storey detached house, 212 sq.m. / 2300 sq.ft. heated area. EPC 87B. Mitsubishi Ecodan 11.2Kw ASHP, weather compensated flow temp, UFH, MVHR.
OK. So we assume that the compressor can't be fitted using copper pipe connectors.
@delt - can you please tell us the GSHP manufacturer and model number?
We'll then be better able to assess the component price.
Save energy... recycle electrons!
The compressor is brazed to copper pipes - brazing is basically much higher temperature soldering, joining copper pipes together with a dissimilar metal (often high Silver content). It's stronger than soldering, which is important for the longevity of the compressor as it spends it's life vibrating. Starts and stops are especially abrupt, and cause fatigue on the joints. Often the whole lot of the heatpump is brazed, but so long as the pipes are long and have enough bends to absorb vibration, it's the compressor ones that really need it.
They'd have to vacuum pump the refrigerant out, safely store and likely dispose of it. Put nitrogen in the system. Cut the old compressor out. Bleed nitrogen (or other inert gas) through while brazing a new one back. Ideally swap out the dessicant filter (water reacts with compressor oil to form acid, kills the compressor). Vacuum again, check vac. maintained, refill with correct gas weight.
@transparent Ok so I intentionally did not include the manufacturer/model/ since they are sole supplied in the UK and I do not want this to become an exercise in highlighting the prices of a specific company. Without this info perhaps my ask is unrealistic, in the way that quotes would wildly differ for engine work on a Ferrari vs Ford. Maybe I should rather pose a more general question to owners of midsize (eg 10.5kw) GSHPs as to 'how much did you pay/would you expect to pay' if you woke up tomorrow and your compressor had failed? <£1k, 1-2K, 2-3K, 3-5K, >£5K?? Suffice to say I had an unpleasant surprise when this happened to me - I have not really seen these costs/risks baked in to GSHP ownership so looking to raise the question and awareness. Hope there is sufficient for you to punt a range but understand if not - many thanks for the comms
No, that's quite understandable @delt
Most ASHP models share common internal components, often across different manufacturers.
If you know what you're looking for, then you can buy almost anything you want directly from a Chinese warehouse on AliExpress.
GSHPs are different.
The very nature of the design means that they can't "borrow" components from the Air Conditioning market.
As I'm in West Devon, about 4 miles from 'the border' I took time to go and visit Kensa, who make GSHP units at the far end of Kernow.
They only manufacture GSHPs (no ASHPs) and they have a brilliant team of in-house design engineers.
I would certainly feel very happy buying into that product-range.
But I'd be very careful who I chose to install it.
There's no point investing in a well-engineered product unless it's also installed by someone who really does understand the system.
The downside of course, is that the sole source of replacement parts would be Kensa themselves.
For that reason I'd be looking at the feasibility of long-term maintenance contracts and/or insurance.
I might even insist that firmware upgrades were included in the package.
I would also want to have a control system which permits remote monitoring.
That would allow the installer, or Kensa themselves, to see how the pump is behaving without me paying to bring someone to site.
I don't yet have a heat-pump.
But I'm on the same piece of granite which allows Kensa to dominate the market which they've grown in SW England.
They don't need to advertise. Almost everyone buys on their reputation.
And part of the attraction is that there are several drill-teams who can sink boreholes in the area.
The legacy of Cornwall School of Mines at Camborne has given us some benefits not enjoyed elsewhere.
So I too am interested in hearing of the situation in which find yourself.
... and at this point I strongly suspect that @editor will move us off the Welcome Topic and into our own thread. Stand by!
Save energy... recycle electrons!
@delt I liked to make a stab at this, so some of the things to consider:
engineers travel time to site,
say 1 hour @ 65/hr
engineers travel time back home, again 1 hour
8 hrs on site @ £65/hr ( prepare, vac down, remove old compressor, fit new compressor, pressure test with nitrogen and hold, fill with refrigerant, run up and re-commission)
R407 scroll compressor £560+ carr £12
new dryer/filter £25
refrigerant gas £25/kg assume 2.5 kg system charge
sundries @ £40
total approx. £1600 inc VAT.
I'm sure you'll let me know if I'm close or off by a mile. 😁
Those labour charges look low to me @iaack
An engineer with the training, skills and equipment to undertake this work will have substantial overheads to meet.
Save energy... recycle electrons!
@transparent You could well be right. Current salary for a refrigeration engineer is in the region of £40k per annum ( £20/hr.) Cost of training tools van and other over-heads recouped by their employer, hence my stab @ £65/hr.(+Vat), but it could be nearer £85/hr
Difficult access to the compressor for swap out for instance will create extra work. And no doubt ideal time to carry some routine maintenance work on the system will mean potentially an extra day on site (extra £700 to budget).
- 21 Forums
- 1,960 Topics
- 42.5 K Posts
- 51 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@johnr Hadn't thought about secondary glazing - definit...
By BAMi , 19 minutes ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 48 minutes ago
-
RE: SolarPV tables / online calculator
By Gary , 1 hour ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 12 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 12 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 14 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 16 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 18 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 19 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 20 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 24 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@editor But do you wear your peaked cap the right way r...
By Toodles , 2 days ago
Latest Topics
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 48 minutes ago
-
SolarPV tables / online calculator
By MichelleC 8 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 20 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 22 hours ago
-
By Toodles 2 days ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago
-
Towel rails. An unexpected final hurdle
By Davesoa 2 days ago