Vaillant Arotherm Plus PCB Failure

11 Posts
5 Users
4 Likes
1,235 Views
(@pdfreeman)
Active Member Member
50 kWhs
Joined: 1 year ago
Posts: 3
Topic starter  

Hello all

I have a 5kw Arotherm Plus ASHP which was commissioned around 18 months ago however unused for around 9 months.

On restarting the system the ASHP was showing connected but wouldn't start then heat was requested (DHW or Heating) and after a few hours F.1117 Compressor Failure was shown.

Investigating further its evident that the 240vAC neutral on the PCB has failed - looks like it has overheated/melted.

Has anyone had similar issues and if so do you know the root cause? I've temporarily repaired the board which now means the ASHP is functional so I know this is the problem but before I replace the board I'd like to know why it happened and how to try and prevent it happening again!

I'll try and contact Vaillant directly also.

Thanks in advance for any advice!!

IMG 6951

 

IMG 6961

 

 

This topic was modified 1 year ago by pdfreeman

   
Quote
(@wimdeboysere)
Active Member Member
33 kWhs
Joined: 2 months ago
Posts: 3
 

Hi, I have the same problem. Same place, what was the cause of the problem? 

 

thx for the reply, 

wim


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13583 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4150
 

Your original post must have fallen into the 'black hole' that appears to exist in the website from time to time.

Looking at the photos I suspect that the cause may have been condensation, possibly due to the heat pump not being used for 9 months.

 

This post was modified 2 months ago by Mars

   
ReplyQuote
(@pdfreeman)
Active Member Member
50 kWhs
Joined: 1 year ago
Posts: 3
Topic starter  

@derek-m , @wimdeboysere - I've no idea what caused it - could see how potentially was condensation, didn't open the unit up prior to restarting it.

A new board is in and all has been fine since!


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13583 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4150
 

Posted by: @derek-m

Your original post must have fallen into the 'black hole' that appears to exist in the website from time to time.

Looking at the photos I suspect that the cause may have been condensation, possibly due to the heat pump not being used for 9 months.

 

It is difficult to tell from the photo's, but PCB's for outdoor use should be coated with a waterproof lacquer.

 


   
Mars reacted
ReplyQuote
(@wimdeboysere)
Active Member Member
33 kWhs
Joined: 2 months ago
Posts: 3
 

@pdfreeman 

I think the main board on the unistor is also Broken, screen shows connection failure and i cant measure power on the bus connection, Room thermostat is also dead.So the best thing tot do is put in a new main also of does it get power from the (dead)heatpump outside?

20240226 104718

 


   
Mars reacted
ReplyQuote



Mars
 Mars
(@editor)
Illustrious Member Admin
16595 kWhs
Veteran
Joined: 3 years ago
Posts: 2298
 

@pdfreeman did you have to pay for the replacement and did Vaillant offer any information on what may have caused this?

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU

Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
16595 kWhs
Veteran
Joined: 3 years ago
Posts: 2298
 

@wimdeboysere did you have your system installed after pdfreeman’s and how long has yours been installed?

Have you raised it with Vaillant?

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU

Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk


   
ReplyQuote
Abernyte
(@abernyte)
Reputable Member Member
2626 kWhs
Joined: 1 year ago
Posts: 143
 

Did the fried slug on the left have anything to do with the failure or was it collateral damage!


   
Mars reacted
ReplyQuote
(@wimdeboysere)
Active Member Member
33 kWhs
Joined: 2 months ago
Posts: 3
 

@editor it's installed in 2019 and worked fine untill now..


   
ReplyQuote
(@pdfreeman)
Active Member Member
50 kWhs
Joined: 1 year ago
Posts: 3
Topic starter  

@editor I didn't find Vaillant very helpful to be honest, so ended up purchasing the PCB and installing myself, pretty straightforward and it has been fine since. 

 


   