Hi.
Long time reader, first time poster.
I've followed a lot of the threads on here with interest and found them really useful in helping to plan for installing a heat pump, but I haven't seen any discussion of underfloor heating other than to say that it is generally considered to work well with ASHPs.
We're in the process of renovating a 1920s semi in the north of England with a view to replacing the gas boiler with ASHP in the next few years when funds allow. We want to install underfloor heating in the ground floor which we are currently working on. We had some heat loss calculations done for the house last year to understand what size heat pump we would need and any upgrading of radiators etc that would be required. We said at the time that we would be installing UFH in the ground floor. The calculations that were done recommended 100mm pipe centres for the UFH to provide sufficient output at ASHP flow temperature of 50°C.
The ground floor is a suspended timber floor throughout. I was hoping to install the UFH using an overlay system on top of the floor boards (I can insulate from below via basement), however most of the systems available seem to use a minimum of 150mm pipe spacing.
I have read elsewhere that 150mm is the maximum pipe spacing recommended for use with a heat pump, so wondering if this will be alright. The heat calcs assume a design temperature of 21°C. We rarely have the heating above 18°C so I wonder if the lower output might be fine for us.
I assume a lot of people on here have UFH with their heat pumps so would be interested to know what pipe spacing people have and if anyone has had issues with the output not being high enough? Also if anyone has recommendations for a good system to use on suspended floors any advice would be much appreciated.
Many thanks!
-
Rodents! A word of warning for heat pump owners
5 days ago
-
Is this ASHP install OK?
1 month ago
-
Surface mount or bury primaries for heat pump installation?
2 months ago
-
UFH and ASHPs
4 months ago
-
Installing your own ASHP - DIY
5 months ago
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 24 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
I think the setup I have could use wireless sensors, th...
By cathodeRay , 2 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I couldn't agree more. This is a case where you buy as...
By JamesPa , 6 hours ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 20 hours ago
-
Inventor (Midea) Heat Pump short cycling advice
Hello, I have a Inventor (Midea) 8kW with a 800meters Φ...
By immunity , 20 hours ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
I have signed up as well. @belsnugg could you outline ...
By JamesPa , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 1 day ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 2 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 2 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 2 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 2 days ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 3 days ago
-
@drei When I was in local government we were of cours...
By JamesPa , 3 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 3 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 4 days ago