Towel rails. An unexpected final hurdle
I thought, our potential heat pump supplier thought, we’d agreed the final design specifications for our install. But we have a problem. Well I do. The installer wants to remove the current ladder type towel rails in two bathrooms and replace them with standard Stelrad radiators to meet emitter requirements. These are the radiators that they supply. That would leave us with no way to hang or dry towels.
One radiator requirement is 1181watts @50C and the other 600 watts @50C.
Has anyone else had this issue and how did you resolve it?
I’ve looked at some suppliers on line and there do seem to be high output options available - I suppose I could have the standard radiators installed and simply replace them but that seems very wasteful.
I faced this one also. The problem with towel rails is that they don't actually emit much heat, and if you then present them with a low flow temperature its almost nothing.
I considered standard rads with a hanging rail (several are available as add ons). One supplier suggested a fancoil or an electric element in the radiator. A couple of potential installers said - 'if I were you I'd just leave it as is and change it later if its a problem - most of the bathrooms we do are non-compliant'.
In then end I reasoned that the bathroom door is usually left open, there is excess heat available from the adjacent hall, and if you are having a bath/shower there is excess heat available from the water in the bath, so I went with the 'leave it' approach. That was the right decision for me.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks - however the installation wouldn’t be compliant if I left it as is would it and therefore wouldn’t be signed off? That would be my preferred option as, at the moment, one is dual fuel and I can heat by electricity as well when needed. The other towel rail has never really been that effective but is in a small shower room which is heated as you say by basically leaving the door open.
Posted by: @davesoaThanks - however the installation wouldn’t be compliant if I left it as is would it and therefore wouldn’t be signed off? That would be my preferred option as, at the moment, one is dual fuel and I can heat by electricity as well when needed. The other towel rail has never really been that effective but is in a small shower room which is heated as you say by basically leaving the door open.
There is compliant and compliant.
The bus rules say that the heat pump is compliant if it
(c)it replaces the heat generating components of the original heating system installed in that property (where applicable), other than any—
(i)supplementary electric heater, including any immersion heater,
(ii)circulation pump, or
(iii)solar thermal collector.
I would suggest that a towel rail heater could be considered a 'supplementary electric heater' provided that the total emitter capacity (excluding the electric heater) is sufficient to heat the entire house.
I would have a quiet word with your prospective installer!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Technically correct. The best sort of correct. Thanks I’ll do exactly that.
@jamespa I wasn’t aware there might be a problem in a bathroom; we have always had a radiator in our < 4 sq.m. bathroom and I requested having a dual fuel towel rail placed above it. In fact I had requested the largest that could be fitted in the space and the electrical element is ~ 300 Watts - this dries the towels nicely and adds a little supplentary warmth to the bathroom - which we like.😉 Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I think the issue is that MCS recommends 23C for bathrooms, which requires large emitters, and as mentioned above most towel rails simply do not emit that much heat, so are unlikely to meet the design criteria for the room. For us, the solution was to install standard Stelrad radiators to meet the design criteria in addition to towel rails for drying towels (which emit even less heat when covered with wet towels). I appreciate not every bathroom will have physical space for two radiators, and I know our system designers highlighted it was a real problem for them getting large enough radiators into many bathrooms to meet the design temps. Challenging if they are required to have MCS sign off on the installation.
@old_scientist As I mentioned, our approx. 2 x 2 metre bathroom has a radiator and dual fuel towel rail and I requested an elevated temperature of 25 degrees - in fact we have 25-26 degrees which we enjoy and find very comfortable. Happy Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles @jamespa. Your guidance is really helpful. I’ve found two towel rails at Victorian Plumbing that seem to meet the output requirements. One is rated at 1100 watts at 50C and the other 600 watts @50C. I’ll see if my installer will accept them. It may be I have to buy them and they give a credit for the two Stelrads. They are big beasts but they will fit.
Posted by: @old_scientistI think the issue is that MCS recommends 23C for bathrooms, which requires large emitters, and as mentioned above most towel rails simply do not emit that much heat, so are unlikely to meet the design criteria for the room.
Fair enough. Although the requirement is in a paragraph which starts
The following procedure shall be followed for systems where the heat pump is to supply 100% of the space heating load with or without a supplementary electric heater to ensure the correct sizing and selection of a heat pump and related components for each installation:
a) A heat load calculation should be performed on the building using internal temperatures not less than those specified in Table 1 and external temperatures
specified in Table 2 column A or B, according to the MCS Contractor's assessment of the building location. If column B is selected, no uplift factor for intermittent heating is required. Heat load calculations shall in other respects comply with BS EN 12831-12017"
and 'should' is defined as
" the term ‘should’ prescribes a requirement or procedure that is intended to be complied with unless reasonable justification can be given"
so there is arguably some limited wiggle room to provide a reasoned justification. I have an understairs toilet without any heating, would any reasonable installer insist on putting in a radiator to guarantee its always at 18C?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 21 Forums
- 1,958 Topics
- 42.5 K Posts
- 42 Online
- 2,272 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
I have to wonder if the cold lounge needs a much bigger...
By JohnR , 20 minutes ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 1 hour ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Looking at it since it's been a steady 34 The heat pu...
By Joshua , 2 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 2 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 4 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 6 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 8 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 9 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 10 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 13 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 14 hours ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 1 day ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 1 day ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 1 day ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 1 day ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 1 day ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@editor But do you wear your peaked cap the right way r...
By Toodles , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I’d be interested to hear the feedback and consensus on...
By Mars , 2 days ago
-
RE: Forum updates, announcements & issues
@sussex-greenish thank you. As a general and quick no...
By Mars , 2 days ago
Latest Topics
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 9 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 12 hours ago
-
By Toodles 1 day ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 1 day ago
-
Towel rails. An unexpected final hurdle
By Davesoa 2 days ago
-
By big_si 2 days ago
-
Act now to defer the UK road tax increase on EVs
By downfield 2 days ago