Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Time to seriously consider the Homely System perhaps?
My current heating setup is a Samsung 12Kw High Temperature Quiet heat pump fitted in parallel with a Grant Votex Blue flame oil boiler, all controlled using a Honeywell Resideo TR6_HW smart thermostat.
As the HP was fitted in June of this year I have been going through the process of fine tuning the weather compensation control, now that the outside environment is getting to proper winter temperatures and through testing, finding out the capabilities of my old 1970's / 80's rads, as these were an unknown in the initial calculations.
Following the HeatGeeks procedure and using little Govee thermometers to verify the temperatures in various parts of the house, I was confident that the system was now functioning optimally, house reaching 21C, Good Lady happy until... I reintroduced the smart thermostat into the control loop... Good Lady no longer as happy due to feeling colder than before.
Hmmm I thought, so I placed one of my Govee thermometers right next to the thermostat to monitor what was going on and have now learnt something new!
Smart thermostats, from what I know, have algorithms in their programming to avoid temperature overshoot which is a waste of energy when these devices are being used with fossil fuel systems. As fossil fuel systems push a large amount of heat energy into the building during each cycle, the thermostat compensates for this (in my case) by shortening the cycle time the closer the room temperature gets to the target temperature.
So the result is, when the room temperature reaches approximately 1C to 1.5C within range of the target temperature, the thermostat changes its behaviour by reducing the cycle time.
Now this has the effect on my oil boiler of slowing the heating rate to 0.5C / hour for the final 3 hours of heating, meaning the room finally gets to 21C within 30 minutes of going to bed, so I have now adjusted the start time to enable most of the evening to be 21C.
However as we know HP's are not so great at producing large quantities of heat quickly per cycle and need to run for longer times per cycle to achieve the required flow temperatures. This was not so in my case, the thermostat throttles back the HP to the point the flow temperatures only get within 4 to 5 degrees of the required temperature on each cycle, resulting in less heat to the room and a cold Wife.
Two options were open to me at this point, increase the weather compensation curve to hopefully cater for this but completely ruin the COP or make the thermostat think its colder than it is. Opting for option 2 I adjusted the temperature offset to -1C to see how that helped which I am pleased to say, as a temporary work around, has the desired effect. The thermostat keeps the longer cycle times until the room gets to within 0.5C before slowing the rate meaning the final stage now only takes 2 hours not the 6 hours I was experiencing with the HP.
This leaves me with the question, are current smart thermostats on the market actually suitable for HP's? Is it time to seriously consider a control system such as the Homely?
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
Posted by: @technogeekMy current heating setup is a Samsung 12Kw High Temperature Quiet heat pump fitted in parallel with a Grant Votex Blue flame oil boiler, all controlled using a Honeywell Resideo TR6_HW smart thermostat.
As the HP was fitted in June of this year I have been going through the process of fine tuning the weather compensation control, now that the outside environment is getting to proper winter temperatures and through testing, finding out the capabilities of my old 1970's / 80's rads, as these were an unknown in the initial calculations.
Following the HeatGeeks procedure and using little Govee thermometers to verify the temperatures in various parts of the house, I was confident that the system was now functioning optimally, house reaching 21C, Good Lady happy until... I reintroduced the smart thermostat into the control loop... Good Lady no longer as happy due to feeling colder than before.
Hmmm I thought, so I placed one of my Govee thermometers right next to the thermostat to monitor what was going on and have now learnt something new!
Smart thermostats, from what I know, have algorithms in their programming to avoid temperature overshoot which is a waste of energy when these devices are being used with fossil fuel systems. As fossil fuel systems push a large amount of heat energy into the building during each cycle, the thermostat compensates for this (in my case) by shortening the cycle time the closer the room temperature gets to the target temperature.
So the result is, when the room temperature reaches approximately 1C to 1.5C within range of the target temperature, the thermostat changes its behaviour by reducing the cycle time.Now this has the effect on my oil boiler of slowing the heating rate to 0.5C / hour for the final 3 hours of heating, meaning the room finally gets to 21C within 30 minutes of going to bed, so I have now adjusted the start time to enable most of the evening to be 21C.
However as we know HP's are not so great at producing large quantities of heat quickly per cycle and need to run for longer times per cycle to achieve the required flow temperatures. This was not so in my case, the thermostat throttles back the HP to the point the flow temperatures only get within 4 to 5 degrees of the required temperature on each cycle, resulting in less heat to the room and a cold Wife.Two options were open to me at this point, increase the weather compensation curve to hopefully cater for this but completely ruin the COP or make the thermostat think its colder than it is. Opting for option 2 I adjusted the temperature offset to -1C to see how that helped which I am pleased to say, as a temporary work around, has the desired effect. The thermostat keeps the longer cycle times until the room gets to within 0.5C before slowing the rate meaning the final stage now only takes 2 hours not the 6 hours I was experiencing with the HP.
This leaves me with the question, are current smart thermostats on the market actually suitable for HP's? Is it time to seriously consider a control system such as the Homely?
Or you could just use the controller that was designed to control the heat pump. Simples. 😎
@derek-m I wish it was! 🤣 Sadly due to the HP and controller being located within the outside boiler room, running the data cable for the built in thermostat to the lounge was not an option plus the Resideo is still needed when I use the oil boiler 🙁
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
@Technogeek I've recently been attempting to characterise my gas-fired central heating and radiators prior to a possible transition to an ASHP and stumbled across the same problem with my 'smart' thermostat. I had turned down the boiler output - which has control algorithms of its own - removed the overnight temperature setback and found we were variously throwing on extra clothes or ripping them off once the outside temperature started going low. The situation varied from room to room, probably not helped by unbalanced radiators and the odd 30 year old TRV deciding to stick again. I suppose it may help convince my good lady that we really do need to replace what we have 😉 .
@derek-m Admittedly, we have only had the Homely smart controller for a few weeks but it seems to have settled down now and is keeping the house at the temperatures we require at different times - without any problems; the radiators seem to be warm most of the time now and our consumption now when the temp. has dropped to 1 - 3 degrees most days is lower than when we were at 8 - 9 degrees and using the Heatmiser Neo on/off stat. I had spent some time carefully tweeking the LWT and WC settings on our Daikin EDL08 hp to get the best out of the system - but Homely has improved on this considerably! Well worth considering I think. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 771 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
@david999 Thanks, I have read that some detergents are ...
By colinc , 1 minute ago
-
RE: Our 10 year old Grant heat pump failed
Glad you got a resolution but £11k to £14.5k to replace...
By JamesPa , 1 hour ago
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
OOch thats leaking quite a lot! it looks like...
By JamesPa , 1 hour ago
-
RE: Indevolt Batteries UK Support & Info Thread
@indevolt-uk Keen to know more about the pricing and wh...
By ChandyKris , 1 hour ago
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 6 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 15 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 18 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 19 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 19 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 20 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 23 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 23 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago