Testing new controls/monitoring for Midea Clone ASHP
Posted by: @bensonBy leaving the serviceman settings completely alone, turning off weather comp settings and running on set outlet flow temps I am hoping it will run a bit better.
Interesting. Basically a DIY weather compensation setup with fine tuning based on the IAT, if I have understood right. I don't see anything wrong with the idea at all, and if it avoids the turn my heat pump off without asking 'feature' then you will certainly have avoid a nuisance. I wonder, how often do you run the checks?
The only thing I might mention is making sure the logic can't somehow take the Set LWT too high (>60°C). I do this by only adding to or subtracting from a baseline, not the current Set LWT, and make sure the sum of the baseline plus the increments doesn't put my heat pump Set LWT over 60 degrees.
It will be very interesting to hear how you get on.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay it is currently set to run the checks every 15 minutes. What I really like in home assistant is that there seems to be a solution for almost every problem. For example, I queried how defrost cycles would affect it and sure enough there is a workaround for that. I have set up a filter helper which then averages out the OAT sensor over a half hour period so if the 15 minute check happens to coincide with a defrost run, it won't suddenly and erroneously drop the outlet flow temp. It will run it's calculation based upon the smoothed out sensor readings (the average outdoor temp over that half hour period).
As for the upper and lower limits the offset calculator can only go to a maximum of +5 and -5 from the set 'curve' value.
Posted by: @benson- second automation will adjust this outlet flow temp value if needed. For example, if the IAT is outside of our indoor temp comfort zone which might happen if it is particularly windy (today for example), it will offset the flow temp value by +2. If it is even further out of this temp comfort zone it will boost it further with an offset of +3. The same logic will apply at the other end so if it overshoots it will adjust by -2.
What you are actually implementing is a closed loop control idea, rather than the "open loop" WCC curve approach. It has been my postulate all along that this is the preferable method and I am sure your experimentation will show this.
However, your control logic is necessarily rather crude, I understand you may not have experience with PI controls etc. But classic PI requires a model of the process, which is not available. If you want to take it further, I would suggest a linguistic fuzzy PI control (OK it sounds exotic). This is what I am trying to do at the moment, but since I do not have an appropriate temp sensor, I am simulating.
Good overall work though !
Midea MHCV10WD2N7 R290, 5.8kWp energy community solar power.
@benson — good point about the defrosts, as you know they push up the OAT, which is actually the AIT, Air Intake Temp, by several degrees, which could erroneously lower the Set LWT by several degrees. I think your setup, being independent of the wired controller logic, could also be relatively easy to set up to use the true OAT, got from an independent sensor.
Midea 14kW (for now...) ASHP heating both building and DHW
@tasos it was likely your post mentioning running outside of WCC settings that gave me the idea. Whilst initially I was surprised and quite pleased with regard to how one set curve could keep my IAT steady, it has become clear that the odd windy and cold day will cause me issues. Yesterday was particularly bad in this regard and IAT was dropping- I had the day off from work so I thought it was as good a time as any just to bite the bullet and look to move across. Gemini wrote all of the automations for me in yaml.
Id be interested to know how yours develops. For me, a comfort offset based on IAT seems sufficient rather than needing to incorporate weather forecasting as well (assuming that is what you are looking at when you say my setup is quite basic?)
Anyway all seems to be working well so far with my set up. Nice and steady outlet flow temps and COP seems good.
@cathoderay yes the OAT according to the ashp sensor will actually rise a few degrees during defrosts as you know so that would have no doubt caused some issues. A completely separate outdoor sensor is certainly an option. For now the smoothed out sensor readings seem to be doing the job. My hope as said is that this will result in much smoother operating when the automations run and adjust the outlet flow temp when overshooting, and in particular undershooting so I don’t get the prolonged drops in heating output.
Posted by: @bensonId be interested to know how yours develops. For me, a comfort offset based on IAT seems sufficient rather than needing to incorporate weather forecasting as well (assuming that is what you are looking at when you say my setup is quite basic?)
I meant the following rule you mentioned using:
"second automation will adjust this outlet flow temp value if needed. For example, if the IAT is outside of our indoor temp comfort zone which might happen if it is particularly windy (today for example), it will offset the flow temp value by +2. If it is even further out of this temp comfort zone it will boost it further with an offset of +3. The same logic will apply at the other end so if it overshoots it will adjust by -2."
What this actually amounts to, is a simple proportional (to the error) rule. This has the drawback of not achieving zero steady state error. However, it is simple and wouldn't need any modifications, if you are satisfied with its performance.
Of course one could incorporate OAT in the control logic, but this one level higher also.
By the way, what type of temperature sensor are you using for IAT ?
I need a wireless, modbus one, to do proper testing.
Midea MHCV10WD2N7 R290, 5.8kWp energy community solar power.
@tasos the OAT is incorporated into the control logic. This is what sets the outlet flow temp in the first instance.
I use a load of Tapo temp and humidity sensors in various rooms of my house. It is the hallway one which directly influences the comfort adjustment automation. I was considering using an average of all of the sensors combined, but at present the hallway one will do the job that I need, I think.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 822 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
Actually, it’s better for wooden furniture – or at leas...
By Majordennisbloodnok , 4 hours ago
-
This is absolutely standard for any sealed pressurised ...
By JamesPa , 6 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 6 hours ago
-
RE: What determines the SOC of a battery?
@batpred Your BMS parameters will be the same as m...
By Bash , 7 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 8 hours ago
-
RE: Setback savings - fact or fiction?
I also need to correct something I said by mistake earl...
By cathodeRay , 8 hours ago
-
RE: Electricity price predictions
@judith Thanks for sharing, and nice to see how the ...
By Batpred , 9 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos the OAT is incorporated into the control logic. ...
By benson , 10 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 11 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 12 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 12 hours ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 13 hours ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 14 hours ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 15 hours ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 16 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 17 hours ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 1 day ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 1 day ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I don't know about Solis inverters. It isn't a featur...
By Transparent , 1 day ago
-
Daikin Altherma 3 H HT - Freeze Prevention Threshold
Hi. We have an Altherma 3 HT (18kW I think) which, now ...
By RICHARDF5033 , 2 days ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@petch We are not yet compatible with the R290 from Gra...
By Will H , 2 days ago