Posted by: @scalextrixPosted by: @jamespaAre there 2*22mm (eg upstairs and downstairs) or only 1*22mm.
The current boiler has a single 22mm pipe, but as you suggest that splits into a 22mm feed for upstairs and a 22mm feed for downstairs. That split occurs inside the airing cupboard so a new installation could have a larger diameter to an ASHP to feed them both if necessary.
If DT5 @22mm can carry 6kW as the chart suggested, that should be enough for each leg. Also the largest room has 2kW heat loss, but has two emitters which could be roughly equally sized, so they would easily be below the 2.75kW cap for 15mm.
After checking some utility bills, annual gas consumption is roughly 16000kWh, will be interesting to see if my insulation works reduce that at all.
This is where my experiment comes unstuck, because the current boiler has a DT11 and so that means the single 22mm feed is enough now, but not enough at DT5. As such I can't really tell if it would work.
Though if I balance my rads now, and create a DT5 across them all, that would be a way to test it? But I would be limited to 6 kW down the single 22mm boiler feed...
Afaik there are two considerations namely pump head and water velocity (causes noise and erosion). A short piece of straight 22mm isn't going to increase the head needed much. If it is in a noise insensitive area then the noise doesn't matter. From an erosion standpoint up to 1.5,m/s is sometimes considered acceptable for copper pipes, so about one third more capacity than the heat geek guidance. In summary you may well get away with it!
16000kWh is roughly 7-8kW, so an 8kW pump is reasonable unless you are doing something odd.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @cathoderayI assume my heat pump is 300% efficient
Be careful with that assumption - why
The CoP includes many things a gas boiler efficiency doesn't. A gas boiler doesn't include any electric inputs.
Example when running in heating mode I am getting a CoP of 5 to 6. However when not running, you are still running the circulation pump, controller, any crankcase heaters and they are all added to the CoP figure. On mild day, my daily CoP can drop to 3.5, while the heat pump will run 4 to 6 time for 20 to 30min over 24 hrs. No much heat added compared to standby losses. As it gets colder the standby losses reduce as heat pump runs longer. Also the better insulated your house the more pronounced this effect. But the real point is below.
Posted by: @cathoderaythen using the chart above, I can estimate my total heat loss at a design OAT of -1 degrees C to be 12kW
Moving to chart you could well be a mile out. By a factor of three. CoP has nothing to do with heat pump sizing.
The CoP is just a measure of energy in to energy out. So if you need 4kW of gas (I assume your vertical part of the chart is kW not kWh) you need 4kW for any heat source. So at zero you need approx 4kW not 12kW. So allowing for DHW I would be looking at a 6kW heat pump based on your facts presented.
Design temp really needs the lowest temp you are likely see over 99.6% of the year. Most places are well under -1 or -2.
Posted by: @jamespa16000kWh is roughly 7-8kW, so an 8kW pump is reasonable unless you are doing something odd.
I am not sure the divide fossil fuel kWh by 2000 rule of thumb works. I was going to remark 16000kWh per annum is rather on the high side, suggesting a high heat loss, and a correspondingly large output heat pump, very likely more than 8kW. Take my own very approximate historic figures, 1000L of oil say 10000kWh per annum = I need a 5kW heat pump when actually I need a 12kW heat pump.
The discrepancy may arise from different usage patterns, steady Eddie vs timed fast and furious.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay10000kWh per annum = I need a 5kW heat pump when actually I need a 12kW heat pump.
See my post above - you don't need 12kW.
Posted by: @scalextrixThough if I balance my rads now, and create a DT5 across them all, that would be a way to test it?
I really would not do that, if your heating is working leave it.
1. You boiler may not like it or cope with dT5.
2. If you mess up and you need heat, you may well be out of heating properly mode for a couple of days, while you reverse everything.
If you know the approx heat loss and you can measure your rads do the radiator calculation, to see your output at different flow rates.
Posted by: @cathoderayTake my own very approximate historic figures, 1000L of oil say 10000kWh per annum = I need a 5kW heat pump when actually I need a 12kW heat pump.
The discrepancy may arise from different usage patterns, steady Eddie vs timed fast and furious.
If you want to run a heat pump inefficiently then of course you will need a higher capacity.
How did you come to the conclusion you need 12kW?
If you live in an uninsulated barn and heat only for a small proportion of the day then the divide by 2000 rule of thumb will be well out. If your house takes many hours to cool when you turn the heating off, lead a reasonably normal life, and live in the UK but not in some far flung area of the UK, then it's unlikely to be so far off that it can't serve as a sanity check, which is all that is claimed.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @AnonymousBe careful with that assumption
I should have explained more. The 300% efficiency is actually based on my monitored energy in/energy out (energy out divided by energy in), and is a long term or SCOP type of efficiency figure. The real figure is just under 300%, but I rounded it as i was just showing an example of my workings.
Posted by: @AnonymousCoP has nothing to do with heat pump sizing.
It does, a bit, indirectly (if you choose a heat pump with a dreadful COP you will need a bigger one, or rather one that uses more energy) but the point here is I am not using the COP, or efficiency as defined above, to determine heat pump size, but to estimate energy out, that is, energy delivered to the house. Assuming a steady IAT, then that heat supplied is the heat loss.
Posted by: @AnonymousI assume your vertical part of the chart is kW not kWh
It is kWh (I am measuring energy in and energy out, not instantaneous power) but as it is over an hour, it could also be viewed as power. Each point is the last hour's energy use (because that's what I monitor), in kWh, so a point at 2kWh is also 2lW for an hour...
My logic is this: if the heat pump used 2kWh in the last hour, (ie ran at an average of 2kW for the hour) then, given a measured efficiency 300%, the house had 6kWh of heat delivered. If the IAT is constant, then it follows that the heat loss must also be 6kW.
I did mention design OAT does vary on location, I just used -1 or -2 degrees as it happens to be the figure for around here.
Using the logic again: if at an OAT of -1 the heat pump uses 4kWh over the hour (as in the chart), then the heat delivered to the house is 12kWh, and that, given a steady IAT, is the heat loss.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @AnonymousSee my post above - you don't need 12kW.
I do - see my previous post! Plus it also happens to be the figure decent heat loss calculations come up with.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @jamespaIf you want to run a heat pump inefficiently then of course you will need a higher capacity.
I'm not sure that answers my question (is the divide by 2000 rule of thumb unreliable?). You divided 16000kWh pa (current/historic fossil fuel use) by 2000 to get 8kW heat pump output; I divided 10000kWh historic fossil fuel use pa by 2000 and got 5kW heat pump, when in fact I actually need 12kW. Might the 8kW figure be unreliable?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderaynot sure that answers my question (is the divide by 2000 rule of thumb unreliable?). You divided 16000kWh pa (current/historic fossil fuel use) by 2000 to get 8kW heat pump output; I divided 10000kWh historic fossil fuel use pa by 2000 and got 5kW heat pump, when in fact I actually need 12kW.
How did you come to the conclusion you need 12kW (what calculation did you do?). I'm genuinely trying to understand. It doesn't prima face make much sense so there must be some factors that aren't obvious to me (or @johnmo it seems).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaHow did you come to the conclusion you need 12kW
He multiple gas kW by CoP (off 3) 4x3, so 12kW.
Posted by: @ianmk13Posted by: @jamespaWhere are you located? With this info maybe someone here can provide.a recommendation
I'm in Milton Keynes.
I have performed my own quite thorough heat loss analysis. taking into account my detailed knowledge of the construction of my unconventional home. I also paid a modest sum for a remote, desk-based report as a 'sanity check'. When calculating my heat loss through windows, I contemplated replacing my old (35 year old) DG units with new argon-filled ones but this didn't give a sufficiently marked improvement to the heat loss. By far the biggest unknown was the loss due to air change. I don't consider my home to be draughty, but short of commissioning a pressure test, my estimation of the heat loss is no better than a finger in the air.
During last November to January, I set my boiler to its lowest setting of 12kW (I didn't notice any modulation of the fan while the burner was on) with no overnight setback and recorded daily gas use, flow and return temperatures, IAT and OAT. I have a lot of data if I can find a proper ASHP heating engineer who will make use of it. I also have a detailed plan of my existing plumbing which includes pipe gauges but I need to add lengths.
I strongly recommend a door pressure test. We had one done for ~£300 and it showed our air leakage was less than one air change per hour. Since we have an MVHR our loss is ~2% of total but with default values it would have been +30% more heat loss.
The guy who did the measurement left it running and encouraged us to go around the house finding which rooms had most leakage and where. It’s so easy to find the leaks when the flow is forced.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
1 day ago
-
Rodents! A word of warning for heat pump owners
3 weeks ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
1 month ago
-
Running my new Nibe ASHP efficiently
1 month ago
-
Weather compensation- why you should use it
1 month ago
Currently viewing this topic 3 guests.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 683 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
That’s my pleasure, @andrewj. The only challenge now is...
By Majordennisbloodnok , 56 minutes ago
-
RE: Electricity price predictions
@toodles @skd Then there is not going to be much from t...
By ChandyKris , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
@batpred I reckon Andy might know a thing or 2 about...
By Bash , 2 hours ago
-
RE: What determines the SOC of a battery?
@batpred Ironically you didn't have anything good to...
By Bash , 3 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here’s a current graph showing a bit more info. The set...
By benson , 3 hours ago
-
RE: Setback savings - fact or fiction?
True there is a variation but importantly it's understa...
By RobS , 3 hours ago
-
Below is a better quality image. Does that contain all ...
By trebor12345 , 4 hours ago
-
Sorry to bounce your thread. To put to bed some concern...
By L8Again , 4 hours ago
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 4 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 8 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 11 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 13 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 1 day ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 2 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 2 days ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago