Posted by: @scalextrixPosted by: @jamespaAre there 2*22mm (eg upstairs and downstairs) or only 1*22mm.
The current boiler has a single 22mm pipe, but as you suggest that splits into a 22mm feed for upstairs and a 22mm feed for downstairs. That split occurs inside the airing cupboard so a new installation could have a larger diameter to an ASHP to feed them both if necessary.
If DT5 @22mm can carry 6kW as the chart suggested, that should be enough for each leg. Also the largest room has 2kW heat loss, but has two emitters which could be roughly equally sized, so they would easily be below the 2.75kW cap for 15mm.
After checking some utility bills, annual gas consumption is roughly 16000kWh, will be interesting to see if my insulation works reduce that at all.
This is where my experiment comes unstuck, because the current boiler has a DT11 and so that means the single 22mm feed is enough now, but not enough at DT5. As such I can't really tell if it would work.
Though if I balance my rads now, and create a DT5 across them all, that would be a way to test it? But I would be limited to 6 kW down the single 22mm boiler feed...
Afaik there are two considerations namely pump head and water velocity (causes noise and erosion). A short piece of straight 22mm isn't going to increase the head needed much. If it is in a noise insensitive area then the noise doesn't matter. From an erosion standpoint up to 1.5,m/s is sometimes considered acceptable for copper pipes, so about one third more capacity than the heat geek guidance. In summary you may well get away with it!
16000kWh is roughly 7-8kW, so an 8kW pump is reasonable unless you are doing something odd.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @cathoderayI assume my heat pump is 300% efficient
Be careful with that assumption - why
The CoP includes many things a gas boiler efficiency doesn't. A gas boiler doesn't include any electric inputs.
Example when running in heating mode I am getting a CoP of 5 to 6. However when not running, you are still running the circulation pump, controller, any crankcase heaters and they are all added to the CoP figure. On mild day, my daily CoP can drop to 3.5, while the heat pump will run 4 to 6 time for 20 to 30min over 24 hrs. No much heat added compared to standby losses. As it gets colder the standby losses reduce as heat pump runs longer. Also the better insulated your house the more pronounced this effect. But the real point is below.
Posted by: @cathoderaythen using the chart above, I can estimate my total heat loss at a design OAT of -1 degrees C to be 12kW
Moving to chart you could well be a mile out. By a factor of three. CoP has nothing to do with heat pump sizing.
The CoP is just a measure of energy in to energy out. So if you need 4kW of gas (I assume your vertical part of the chart is kW not kWh) you need 4kW for any heat source. So at zero you need approx 4kW not 12kW. So allowing for DHW I would be looking at a 6kW heat pump based on your facts presented.
Design temp really needs the lowest temp you are likely see over 99.6% of the year. Most places are well under -1 or -2.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @jamespa16000kWh is roughly 7-8kW, so an 8kW pump is reasonable unless you are doing something odd.
I am not sure the divide fossil fuel kWh by 2000 rule of thumb works. I was going to remark 16000kWh per annum is rather on the high side, suggesting a high heat loss, and a correspondingly large output heat pump, very likely more than 8kW. Take my own very approximate historic figures, 1000L of oil say 10000kWh per annum = I need a 5kW heat pump when actually I need a 12kW heat pump.
The discrepancy may arise from different usage patterns, steady Eddie vs timed fast and furious.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay10000kWh per annum = I need a 5kW heat pump when actually I need a 12kW heat pump.
See my post above - you don't need 12kW.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @scalextrixThough if I balance my rads now, and create a DT5 across them all, that would be a way to test it?
I really would not do that, if your heating is working leave it.
1. You boiler may not like it or cope with dT5.
2. If you mess up and you need heat, you may well be out of heating properly mode for a couple of days, while you reverse everything.
If you know the approx heat loss and you can measure your rads do the radiator calculation, to see your output at different flow rates.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @cathoderayTake my own very approximate historic figures, 1000L of oil say 10000kWh per annum = I need a 5kW heat pump when actually I need a 12kW heat pump.
The discrepancy may arise from different usage patterns, steady Eddie vs timed fast and furious.
If you want to run a heat pump inefficiently then of course you will need a higher capacity.
How did you come to the conclusion you need 12kW?
If you live in an uninsulated barn and heat only for a small proportion of the day then the divide by 2000 rule of thumb will be well out. If your house takes many hours to cool when you turn the heating off, lead a reasonably normal life, and live in the UK but not in some far flung area of the UK, then it's unlikely to be so far off that it can't serve as a sanity check, which is all that is claimed.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @johnmoBe careful with that assumption
I should have explained more. The 300% efficiency is actually based on my monitored energy in/energy out (energy out divided by energy in), and is a long term or SCOP type of efficiency figure. The real figure is just under 300%, but I rounded it as i was just showing an example of my workings.
Posted by: @johnmoCoP has nothing to do with heat pump sizing.
It does, a bit, indirectly (if you choose a heat pump with a dreadful COP you will need a bigger one, or rather one that uses more energy) but the point here is I am not using the COP, or efficiency as defined above, to determine heat pump size, but to estimate energy out, that is, energy delivered to the house. Assuming a steady IAT, then that heat supplied is the heat loss.
Posted by: @johnmoI assume your vertical part of the chart is kW not kWh
It is kWh (I am measuring energy in and energy out, not instantaneous power) but as it is over an hour, it could also be viewed as power. Each point is the last hour's energy use (because that's what I monitor), in kWh, so a point at 2kWh is also 2lW for an hour...
My logic is this: if the heat pump used 2kWh in the last hour, (ie ran at an average of 2kW for the hour) then, given a measured efficiency 300%, the house had 6kWh of heat delivered. If the IAT is constant, then it follows that the heat loss must also be 6kW.
I did mention design OAT does vary on location, I just used -1 or -2 degrees as it happens to be the figure for around here.
Using the logic again: if at an OAT of -1 the heat pump uses 4kWh over the hour (as in the chart), then the heat delivered to the house is 12kWh, and that, given a steady IAT, is the heat loss.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @johnmoSee my post above - you don't need 12kW.
I do - see my previous post! Plus it also happens to be the figure decent heat loss calculations come up with.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @jamespaIf you want to run a heat pump inefficiently then of course you will need a higher capacity.
I'm not sure that answers my question (is the divide by 2000 rule of thumb unreliable?). You divided 16000kWh pa (current/historic fossil fuel use) by 2000 to get 8kW heat pump output; I divided 10000kWh historic fossil fuel use pa by 2000 and got 5kW heat pump, when in fact I actually need 12kW. Might the 8kW figure be unreliable?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderaynot sure that answers my question (is the divide by 2000 rule of thumb unreliable?). You divided 16000kWh pa (current/historic fossil fuel use) by 2000 to get 8kW heat pump output; I divided 10000kWh historic fossil fuel use pa by 2000 and got 5kW heat pump, when in fact I actually need 12kW.
How did you come to the conclusion you need 12kW (what calculation did you do?). I'm genuinely trying to understand. It doesn't prima face make much sense so there must be some factors that aren't obvious to me (or @johnmo it seems).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaHow did you come to the conclusion you need 12kW
He multiple gas kW by CoP (off 3) 4x3, so 12kW.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @ianmk13Posted by: @jamespaWhere are you located? With this info maybe someone here can provide.a recommendation
I'm in Milton Keynes.
I have performed my own quite thorough heat loss analysis. taking into account my detailed knowledge of the construction of my unconventional home. I also paid a modest sum for a remote, desk-based report as a 'sanity check'. When calculating my heat loss through windows, I contemplated replacing my old (35 year old) DG units with new argon-filled ones but this didn't give a sufficiently marked improvement to the heat loss. By far the biggest unknown was the loss due to air change. I don't consider my home to be draughty, but short of commissioning a pressure test, my estimation of the heat loss is no better than a finger in the air.
During last November to January, I set my boiler to its lowest setting of 12kW (I didn't notice any modulation of the fan while the burner was on) with no overnight setback and recorded daily gas use, flow and return temperatures, IAT and OAT. I have a lot of data if I can find a proper ASHP heating engineer who will make use of it. I also have a detailed plan of my existing plumbing which includes pipe gauges but I need to add lengths.
I strongly recommend a door pressure test. We had one done for ~£300 and it showed our air leakage was less than one air change per hour. Since we have an MVHR our loss is ~2% of total but with default values it would have been +30% more heat loss.
The guy who did the measurement left it running and encouraged us to go around the house finding which rooms had most leakage and where. It’s so easy to find the leaks when the flow is forced.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
-
ASHP install contract and BUS grant money
1 week ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 week ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 weeks ago
-
Heat Pump starting current
1 month ago
-
Running my new Nibe ASHP efficiently
1 month ago
- 21 Forums
- 1,966 Topics
- 42.7 K Posts
- 48 Online
- 2,279 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
@jamespa I will wait for smart heating to come back wit...
By Eliuccio , 3 minutes ago
-
RE: Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
Sorry, yes, 2105. OOPS! If I recall the unit circulates...
By AllyFish , 9 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
No pressure or obligation, this discussion has moved on...
By JamesPa , 40 minutes ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
It may be be because the controller has been changed, a...
By cathodeRay , 1 hour ago
-
RE: Battery storage to run Heat Pump.
The problem with current tariff proposals is that they ...
By Transparent , 1 hour ago
-
RE: Who's your electricity provider and what's your tariff?
So far, I'm happy with moving to Eon next. Not paid any...
By Andris , 2 hours ago
-
RE: Split system and pipe lengths for air source heat pump installation
@johnmo got it. Thanks.
By nickmorgan , 2 hours ago
-
RE: Setback savings - fact or fiction?
And finally, the R version tidied up a bit and larger, ...
By cathodeRay , 6 hours ago
-
RE: Ecodan ASHP - How to optimise my set up?
Thanks everyone for posting this, so much useful info t...
By Bamnio , 8 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
I have the same pump and if I am operating it correctly...
By Broadsman , 9 hours ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@editor Will get back. Lots to try. Thanks to everyon...
By cliffhanger , 9 hours ago
-
RE: Towel rails. An unexpected final hurdle
I had a similar issue but convinced the installer to le...
By Pie_Eater , 20 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
This whole discussion highlights just how much of a mes...
By Mars , 20 hours ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
@cheshirejohn thanks for the update and for sharing. I’...
By Mars , 21 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 23 hours ago
-
@robs useful thread! Thanks for sharing - Octopus are c...
By big_si , 24 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 1 day ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 1 day ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 2 days ago
Latest Topics
-
Battery storage to run Heat Pump.
By Broadsman 9 hours ago
-
Heat Pump Sizing & Installation Costs
By Mars 1 day ago
-
SolarPV tables / online calculator
By MichelleC 2 days ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 2 days ago