Scottish power blocking install

25 Posts
6 Users
9 Reactions
3,044 Views
(@waylander)
Eminent Member Member
94 kWhs
Joined: 2 years ago
Posts: 13
Topic starter  

@derek-m im hoping they do, they asked early on Friday for my MPAC or whatever the number is on my bill and this was passed on, not sure of having 2 numbers on my bill makes it worse, 1 for standard electricity and 1 for economy 2000, got a phone call at 18:00 stating it was delayed or cancelled  due to unit being too big, I explained it was going from 12kw down to 5.3kw, they said they put this across but peak current is too high. 

It was to late in the day to contact Grant to find out what Peak current is of the 13kw model,  I have since read as above the 10kw ASHP can be installed so if I cant get the 13kw unit I will ask for the 10kw hoping it will be sufficient.


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

@waylander

Did your installer carry out a heat loss calculation detailing the before and after improved insulation?


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26271 kWhs
Veteran
Joined: 4 years ago
Posts: 2983
 

This isn’t overly helpful, but as a comment I find it disturbing that the UK announced its bold electrification plans where air source heat pumps are key to actualising the vision, and we have scenarios where DNOs aren’t approving installations. Instead of saying no and rejecting the application, should this not prompt DNOs to upgrade networks so that they can handle peak draw? 

Specifically on the subject, Scottish Power are our DNO, and we had to apply for approval for our 18kW ASHP - it took six months, but we did get an approval to proceed.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

@editor

I do believe that both National Grid and the DNO's are gradually in the process of upgrading the electricity distribution systems, but you must realise that this is not a 5 minute job and the costs are quite considerable. I suspect that the politicians and probably their advisors don't fully understand the complexity and timescales involved. Whilst I was working for National Power in Pakistan, a Unit Transformer developed a fault and caught fire, a replacement from Brazil had a lead time of 18 months.

It is also not just a matter of installing thicker cables, but also upgrading the switchgear and transformers on the system, which get larger and more expensive the further you go back up the distribution network.

Whilst the politicians may think that it looks very good in their manifesto's to champion heat pumps and EV's, along with solar farms and wind farms, I do believe that they think that energy gets from the generator to the consumer in some form of magical way.

I still maintain that they are putting the cart before the horse, and should instead be championing energy efficiency first, which should reduce the need for much of the system upgrades that are hopefully being planned.

The powers that be should also be encouraging battery storage systems, both domestic and within the electricity supply networks. This would allow the peaks and troughs of the supply and demand to be smoothed out, and hence once more reduce the need for extensive upgrades to the distribution networks. 

As I have stated repeatedly, if you don't need the energy in the first place, then it doesn't need to be generated and transmitted.

Let's have some grown up thinking for a change.


   
👍
1
ReplyQuote
(@saenergy)
Trusted Member Member
126 kWhs
Expert
Joined: 3 years ago
Posts: 17
 

You can check the ENA database and it will tell you what the max demand is as well as if it is connect and notify or not.  

easiest solution is to switch to an alternative ASHP. You can check the alternatives, again on the ENA database.  

ENA Database link at bottom of page

 

 

Internationally recognised award winning installer of heat pumps and stuff


   
👍
1
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26271 kWhs
Veteran
Joined: 4 years ago
Posts: 2983
 

Here’s some feedback from the Heat Pump Federation on this topic:

On the Energy Networks Association (ENA) data base the Grant Aerona 3 HPID13R32 is not a "connect & notify" model, but there is likely to be other air-source units of this capacity that are "connect & notify". There is a significant degree of confusion around what DNOs will do for free. The Department for Business, Energy and Industrial Strategy (BEIS) has said in the past that all DNOs will upgrade fuses to 100A for free, this is not currently the case. DCP 205 (under the Ofgem governed DCUSA Agreement that governs DNO activities in this respect) sets out what is currently socialised costs. This is all likely to change in April 2023 when the new EDII charging period starts.

Bottom line is that a great deal of work is being done in the background to ease heat pump deployment at domestic level. In the short term, it's worth installers and homeowners seeking out devices that are "connect & notify" where possible.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
👍
1
ReplyQuote



Mars
 Mars
(@editor)
Illustrious Member Admin
26271 kWhs
Veteran
Joined: 4 years ago
Posts: 2983
 

Another reply from an experienced engineer on the subject. Very interesting: 

I've had a pantomime with my DNO Northern Powergrid - very similar issue. I had planned to install a Grant 13kW ASHP, needing a 32A MCB and isolator even though the maximum full load current is 23A & inverter soft start compressor. The DNO wanted to charge me about £800 to upgrade their incoming fuse from 63A to 80A. Our village has a 'fragile and ageing' DNO infrastructure (I choose my words carefully mindful of the number of power cuts we routinely suffer)

It took the DNO 4 weeks to respond to the enquiry (vs the 5 working days stated in their service level agreement). The lead time on the work was 8 weeks from acceptance of their quotation.

The price & lead time are very much a 'go away and don't bother us' proposition from the DNO.

We've got round this issue by revisiting the heat load calcs for the property, and reselecting on a 10kW Grant ASHP (actual capacity 11.5kW). This unit requires a 20A MCB with a max FLC of 17.5A. That is compatible with a 63A incoming main fuse under the 'connect and notify approved method'. The DNO only considers the size of the circuit protective devices added when reviewing their fuse rating, and the 13kW Grant unit drops onto a 32A MCB/isolator.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
👍
1
ReplyQuote
(@waylander)
Eminent Member Member
94 kWhs
Joined: 2 years ago
Posts: 13
Topic starter  

Update, installers came out and did a max current flow check, ie everything turned on, they are passing this to Scottish power, tbf they are really on the ball.

Bit of bad news my huge 12kw tank has srarted leaking at the bottom, nothing major but floor is wet, think its trying to tell me something.

I had no idea the complexity of getting an ASHP, im quickly learning,  once I get the Ok from SP I can get my internal walls insulated.

Fingers crossed, 


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26271 kWhs
Veteran
Joined: 4 years ago
Posts: 2983
 

@waylander, good luck.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26271 kWhs
Veteran
Joined: 4 years ago
Posts: 2983
 

I’ve just been informed via a credible source that they heard a “rumour that Northern Powergrid are now charging for processing DNO notifications, the only DNO to start doing that. I've not got confirmation that is so, but it came from a Project Manager in the renewables who does a lot of install work with them. Totally contrary to the Government's stated objectives of rolling out renewable solutions such as heat pumps. Contrary to the ENA's policy as well.”

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@waylander)
Eminent Member Member
94 kWhs
Joined: 2 years ago
Posts: 13
Topic starter  

Great news, I just received news im good to go, new insulation and some pipework next week with ASHP the following week,

By current boilers leak is getting pretty now, going to drain it on Sunday unless leak gets really bad.

What a difference a week makes. 


   
👍
3
ReplyQuote
(@kev-m)
Famed Member Member
5606 kWhs
Joined: 4 years ago
Posts: 1276
 
Posted by: @waylander

Great news, I just received news im good to go, new insulation and some pipework next week with ASHP the following week,

By current boilers leak is getting pretty now, going to drain it on Sunday unless leak gets really bad.

What a difference a week makes. 

Did you get your original ASHP or did you have to go for a smaller one?


   
ReplyQuote



Page 2 / 3



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security