I had my system working quite well, a cop of around 3.8, and I had a plan about how to improve it with a few new radiators. I was controlling the system with a Hive, that my installer wired in for me.
- I set the Hive to about 28 degrees, it would fire up the compressor I left it like this 24/7
- I would adjust the outlet temp to get the room temps I wanted, with no weather compensation.
- Rather manual I know, but I wanted to get a feel for what flow temps worked well given the outside temp.
- Its a simple set up, two bed terrace house, one open loop heating zone, all radiator valves full open.
However I wanted to try running the system without the Hive, using the standard Samsung wired controller, and setting up weather comp, so I disconnected the Hive.
I'd set the system to run based on the water outlet temp, which I had set at 30, which would have been about right for today.
But without the hive the compressor wont stay on. What happens is the compressor turns on for maybe 3 mintues, water outlet shoots up to 38 to 40ish, the compressor turns off. The water outlet temp very slowly drops until below 33, then fires up again for a few minutes.
Any ideas on what is wrong?
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
I’ve exchanged a few messages about this with Graham Hendra, and according to him this unit won't reduce its output below 40%, leading to cycling; it's simply how it operates. Since it can't modulate below this threshold, temperature control tends to be uneven and spikey, with noticeable fluctuations. This appears to be a common characteristic of newer models.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @ecobakerI'd set the system to run based on the water outlet temp, which I had set at 30, which would have been about right for today.
But without the hive the compressor wont stay on. What happens is the compressor turns on for maybe 3 mintues, water outlet shoots up to 38 to 40ish, the compressor turns off. The water outlet temp very slowly drops until below 33, then fires up again for a few minutes.
Any ideas on what is wrong?
As Mars says, the Samsung will cycle when the heat emitted by the radiators is lower than the minimum power that the heat pump can modulate down to - around 40% of its peak output. With a water outlet temperature of 30C, your radiators are unlikely to be emitting much heat especially if your room temperature is that high and it is mild outside. When the Samsung cycles, several users have commented on its tendency to cycle on and off every 8 minutes or so.
Posted by: @ecobakerHowever I wanted to try running the system without the Hive, using the standard Samsung wired controller, and setting up weather comp, so I disconnected the Hive.
If you change your settings to :
Indoor Zone Option --> Standard Temperature --> Indoor
and FSV 2091 & 2092 --> 0 (Not use)
and FSV 2093 --> 1 (Thermostat only)
then the thermostat in the wired controller will switch the heat pump on and off at temperatures determined by your desired temperature settings. The outlet temperature will be determined by your weather compensation settings which are set using FSV 2011, 2012, 2021, 2022, 2031, 2032.
So you will still get cycling if you choose outlet temperatures that are too low.
Mine is set to 47.5C at -5C outside air temperature (OAT) and 33.5C at 10C OAT as my 12kW Gen 6 Samsung can only modulate down to 3.6kW and my radiators need the outlet temperature to be above 33C to emit this minimum 3.6kW.
This just in from a Samsung Product Specialist: I think it might just overshoot target within the first 5 minutes of operation. That is often the case in systems with a too low active volume.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@ecobaker some more feedback on how to remedy your issue, also from the product specialist: "Calculate minimum required active volume for (extreme) part load operation of 12 minutes (as stated in Samsung's Installer Reference Guide). And check quantity in the system. If there is insufficient volume, increase it by adding a buffer vessel."
Hmmm.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editor@ecobaker some more feedback on how to remedy your issue: "Calculate minimum required active volume for (extreme) part load operation of 12 minutes (as stated in Samsung's Installer Reference Guide). And check quantity in the system. If there is insufficient volume, increase it by adding a buffer vessel."
Hmmm.
Add a Volumiser, NOT a Buffer Vessel.
@editor Thanks, sounds like you know all the right people to speak to. When I do have it set running with the hive I do the cycling. So I think my volume will be too low and below 40% at 30 degrees. I guess I should do the calculations like you say and see what my system requires. If I put more radiators in that would increase the volume right and maybe get it closer to the 40% right? I do have some larger rads arriving next week.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@mike-h Thanks thats really useful.
So my system is set at 42C for -3C OAT and 30C for 16C OAT, but I actually think I can have a lower flow temp maybe down to 27 or 28c on warmer days. I have an 8kw pump, so I guess I need more volume in my system for it to get down to the lower flow temps and not cycle too much.
I have got some new larger radiators coming next week, that would help wouldn't it?
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
Posted by: @editor@ecobaker some more feedback on how to remedy your issue: "Calculate minimum required active volume for (extreme) part load operation of 12 minutes (as stated in Samsung's Installer Reference Guide). And check quantity in the system. If there is insufficient volume, increase it by adding a buffer vessel."
Hmmm.
@editor This advice seems to fly in the face of everything I have learnt from the likes of @iancalderbank and @heacol . Perhaps that is why you have added a 'Hmmm', but I am not sure that it is very helpful to the OP. The minimum volume that Samsung recommends does not prevent short cycling and certainly in my case, a 50L buffer made short cycling worse due to the resulting 4-5C reduction in flow temperature to the radiators.
So an update to this issue, I reinstalled the Hive and went back to my old method, had the hive room temp set for 28, but I added water Law compensation. My flow temp has been around 29 all day, and my COP (taken from energy use/genertion on the unit controller, I don't have any monitoring) has been 4.5 today. Although that was without any DWP because I turned it off and forgot about it.
I am short cycling, the compressor is coming off and on, but I don't know how often in an hour. At what point is too cycles in an hour?
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
Posted by: @mike-hPosted by: @editor@ecobaker some more feedback on how to remedy your issue: "Calculate minimum required active volume for (extreme) part load operation of 12 minutes (as stated in Samsung's Installer Reference Guide). And check quantity in the system. If there is insufficient volume, increase it by adding a buffer vessel."
Hmmm.
@editor This advice seems to fly in the face of everything I have learnt from the likes of @iancalderbank and @heacol . Perhaps that is why you have added a 'Hmmm', but I am not sure that it is very helpful to the OP. The minimum volume that Samsung recommends does not prevent short cycling and certainly in my case, a 50L buffer made short cycling worse due to the resulting 4-5C reduction in flow temperature to the radiators.
That is precisely why I wrote hmmm. That is advice straight from Samsung. I just don’t understand it, and I fully concur that this is in no way helpful to the OP. I find it frustrating how poor the advice is, but felt compelled to share because this is directly from Samsung.
I, however, certainly don’t recommend putting a buffer tank in.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 21 Forums
- 1,985 Topics
- 43.2 K Posts
- 43 Online
- 2,311 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@gary I'll try and help, but at the moment I'm not rea...
By BobTSkutter , 2 hours ago
-
RE: Additional Battery v Wind Turbine v Ripple
The biggest problem for the Coops is that Ripple funded...
By Abernyte , 2 hours ago
-
RE: The EPC Dilemma: How Current Ratings Fail Heat Pumps
I've commented earlier in this thread, finding the same...
By Mike Patrick , 3 hours ago
-
RE: To relocate or add extra PV panels..advice required
It looks normal up to 10:30!
By Judith , 3 hours ago
-
RE: Ecodan Auto Adapt Questions
@boycey Think I'll wait to see what Misti come up with....
By Richard24738 , 4 hours ago
-
RE: SolarPV tables / online calculator
This guy did a good analysis in summary go down a...
By Judith , 4 hours ago
-
RE: Is it worth siting panels on an East facing roof?
@carpenterstation oops - yes I do! 7MWh
By downfield , 5 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@dnagre delayed reply! It worked again for a bit but ha...
By Phoenix15 , 6 hours ago
-
RE: Vaillant Arotherm Plus - new build no heating, no radiator
@john1756 did you ever get to the bottom of this?
By Mars , 9 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
We tested the away mode for the first time as we were a...
By ChandyKris , 11 hours ago
-
RE: Plug and play solar. Thoughts?
Looks really expensive to me. For £1200 you can get a 3...
By DerekDeLeon , 11 hours ago
-
RE: Confused about Samsung Gen6 Hot Water Controller
Found a copy on this really good website 🤣 ...
By DerekDeLeon , 12 hours ago
-
RE: Smart TRV experiences (ideally integrating with Midea heat pump)
@madbilly - I think you may risk over-complicating this...
By cathodeRay , 12 hours ago
-
RE: Nibe F2040 ASHP PCB failure
@editor that is awesome! Your help is much appreciated.
By Delta , 22 hours ago
-
RE: Are MCS are finally improving (some of) their guidelines?
Encouragement of installers to take account of the emit...
By JohnR , 23 hours ago
-
In our case the pipe run for the heat pump is short and...
By madbilly , 23 hours ago
-
@toodles no, unfortunately we don’t have access to the ...
By Simon and Zoe , 1 day ago
-
@sandman1600 What I mean is, your UFH power is 79wm2...
By davidnolan22 , 1 day ago
-
RE: Vaillant AroTherm Plus 7kW
Thank you James for such a complete write up. We also h...
By Judith , 1 day ago
Latest Topics
-
To relocate or add extra PV panels..advice required
By WesleyP1874 9 hours ago
-
Is it worth siting panels on an East facing roof?
By Carpenterstation 10 hours ago
-
Plug and play solar. Thoughts?
By Lucia 1 day ago
-
By JamesPa 1 day ago
-
Vaillant water pressure gauge vs Analogue gauge
By jeegnesh 1 day ago
-
Database of heat pump performance data?
By madbilly 2 days ago
-
By madbilly 2 days ago
-
Confused about Samsung Gen6 Hot Water Controller
By ntruby 3 days ago
-
help with new bathroom and towel radiator
By AdamK 3 days ago