Samsung Gen 6 Issues with outlet temp
I had my system working quite well, a cop of around 3.8, and I had a plan about how to improve it with a few new radiators. I was controlling the system with a Hive, that my installer wired in for me.
- I set the Hive to about 28 degrees, it would fire up the compressor I left it like this 24/7
- I would adjust the outlet temp to get the room temps I wanted, with no weather compensation.
- Rather manual I know, but I wanted to get a feel for what flow temps worked well given the outside temp.
- Its a simple set up, two bed terrace house, one open loop heating zone, all radiator valves full open.
However I wanted to try running the system without the Hive, using the standard Samsung wired controller, and setting up weather comp, so I disconnected the Hive.
I'd set the system to run based on the water outlet temp, which I had set at 30, which would have been about right for today.
But without the hive the compressor wont stay on. What happens is the compressor turns on for maybe 3 mintues, water outlet shoots up to 38 to 40ish, the compressor turns off. The water outlet temp very slowly drops until below 33, then fires up again for a few minutes.
Any ideas on what is wrong?
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
I’ve exchanged a few messages about this with Graham Hendra, and according to him this unit won't reduce its output below 40%, leading to cycling; it's simply how it operates. Since it can't modulate below this threshold, temperature control tends to be uneven and spikey, with noticeable fluctuations. This appears to be a common characteristic of newer models.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @ecobakerI'd set the system to run based on the water outlet temp, which I had set at 30, which would have been about right for today.
But without the hive the compressor wont stay on. What happens is the compressor turns on for maybe 3 mintues, water outlet shoots up to 38 to 40ish, the compressor turns off. The water outlet temp very slowly drops until below 33, then fires up again for a few minutes.
Any ideas on what is wrong?
As Mars says, the Samsung will cycle when the heat emitted by the radiators is lower than the minimum power that the heat pump can modulate down to - around 40% of its peak output. With a water outlet temperature of 30C, your radiators are unlikely to be emitting much heat especially if your room temperature is that high and it is mild outside. When the Samsung cycles, several users have commented on its tendency to cycle on and off every 8 minutes or so.
Posted by: @ecobakerHowever I wanted to try running the system without the Hive, using the standard Samsung wired controller, and setting up weather comp, so I disconnected the Hive.
If you change your settings to :
Indoor Zone Option --> Standard Temperature --> Indoor
and FSV 2091 & 2092 --> 0 (Not use)
and FSV 2093 --> 1 (Thermostat only)
then the thermostat in the wired controller will switch the heat pump on and off at temperatures determined by your desired temperature settings. The outlet temperature will be determined by your weather compensation settings which are set using FSV 2011, 2012, 2021, 2022, 2031, 2032.
So you will still get cycling if you choose outlet temperatures that are too low.
Mine is set to 47.5C at -5C outside air temperature (OAT) and 33.5C at 10C OAT as my 12kW Gen 6 Samsung can only modulate down to 3.6kW and my radiators need the outlet temperature to be above 33C to emit this minimum 3.6kW.
This just in from a Samsung Product Specialist: I think it might just overshoot target within the first 5 minutes of operation. That is often the case in systems with a too low active volume.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@ecobaker some more feedback on how to remedy your issue, also from the product specialist: "Calculate minimum required active volume for (extreme) part load operation of 12 minutes (as stated in Samsung's Installer Reference Guide). And check quantity in the system. If there is insufficient volume, increase it by adding a buffer vessel."
Hmmm.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @editor@ecobaker some more feedback on how to remedy your issue: "Calculate minimum required active volume for (extreme) part load operation of 12 minutes (as stated in Samsung's Installer Reference Guide). And check quantity in the system. If there is insufficient volume, increase it by adding a buffer vessel."
Hmmm.
Add a Volumiser, NOT a Buffer Vessel.
@editor Thanks, sounds like you know all the right people to speak to. When I do have it set running with the hive I do the cycling. So I think my volume will be too low and below 40% at 30 degrees. I guess I should do the calculations like you say and see what my system requires. If I put more radiators in that would increase the volume right and maybe get it closer to the 40% right? I do have some larger rads arriving next week.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@mike-h Thanks thats really useful.
So my system is set at 42C for -3C OAT and 30C for 16C OAT, but I actually think I can have a lower flow temp maybe down to 27 or 28c on warmer days. I have an 8kw pump, so I guess I need more volume in my system for it to get down to the lower flow temps and not cycle too much.
I have got some new larger radiators coming next week, that would help wouldn't it?
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
Posted by: @editor@ecobaker some more feedback on how to remedy your issue: "Calculate minimum required active volume for (extreme) part load operation of 12 minutes (as stated in Samsung's Installer Reference Guide). And check quantity in the system. If there is insufficient volume, increase it by adding a buffer vessel."
Hmmm.
@editor This advice seems to fly in the face of everything I have learnt from the likes of @iancalderbank and @heacol . Perhaps that is why you have added a 'Hmmm', but I am not sure that it is very helpful to the OP. The minimum volume that Samsung recommends does not prevent short cycling and certainly in my case, a 50L buffer made short cycling worse due to the resulting 4-5C reduction in flow temperature to the radiators.
So an update to this issue, I reinstalled the Hive and went back to my old method, had the hive room temp set for 28, but I added water Law compensation. My flow temp has been around 29 all day, and my COP (taken from energy use/genertion on the unit controller, I don't have any monitoring) has been 4.5 today. Although that was without any DWP because I turned it off and forgot about it.
I am short cycling, the compressor is coming off and on, but I don't know how often in an hour. At what point is too cycles in an hour?
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
Posted by: @mike-hPosted by: @editor@ecobaker some more feedback on how to remedy your issue: "Calculate minimum required active volume for (extreme) part load operation of 12 minutes (as stated in Samsung's Installer Reference Guide). And check quantity in the system. If there is insufficient volume, increase it by adding a buffer vessel."
Hmmm.
@editor This advice seems to fly in the face of everything I have learnt from the likes of @iancalderbank and @heacol . Perhaps that is why you have added a 'Hmmm', but I am not sure that it is very helpful to the OP. The minimum volume that Samsung recommends does not prevent short cycling and certainly in my case, a 50L buffer made short cycling worse due to the resulting 4-5C reduction in flow temperature to the radiators.
That is precisely why I wrote hmmm. That is advice straight from Samsung. I just don’t understand it, and I fully concur that this is in no way helpful to the OP. I find it frustrating how poor the advice is, but felt compelled to share because this is directly from Samsung.
I, however, certainly don’t recommend putting a buffer tank in.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
- 27 Forums
- 2,475 Topics
- 56.9 K Posts
- 242 Online
- 6,165 Members
Join Us!
Worth Watching
Latest Posts
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Hi, Nothing yet. I've asked customer to measure flow...
By errmm , 5 hours ago
-
RE: High Temp Heat Pumps for fast warm-up of house
I don't know exactly how long it takes to heat up (and ...
By JamesPa , 6 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
OK. What Im seeing looks fairly normal TBH: 1 start ...
By JamesPa , 7 hours ago
-
RE: Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow
@editor thanks for the tips which I will try before cal...
By DavidB , 8 hours ago
-
RE: Daikin 6kw setup with Dixell controller
@jamespa Many thanks for your reply, a very detailed an...
By CraigH , 8 hours ago
-
RE: Exploring the role of alternative clean heating solutions - Government Consultation
Despite reservations, I found some time to respond to t...
By Rusty , 8 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@crankplus, nope, still not, and I've followed up with ...
By Mars , 8 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge Probably, but temperature change at -10 ha...
By AndrewJ , 9 hours ago
-
RE: External wall insulation - your experience
To be clear, my experience was very positive. The journ...
By Batpred , 11 hours ago
-
@foxesfan Re: ‘Servicing’ as @editor has covered in his...
By Toodles , 11 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson No idea why mine doesn’t work, all I see on ...
By Papahuhu , 12 hours ago
-
RE: Battery sizing - How low can you go!
It seems I am seeing something similar to what you do, ...
By Batpred , 13 hours ago
-
RE: Gaslighting in the heat pump industry – has anyone else experienced this?
Don’t know if this is relevant to this thread, but my A...
By Gruff2001 , 14 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
@majordennisbloodnok While getting Home Assistant runni...
By Steelbadger , 1 day ago
-
RE: MCS - BS EN 12831-1:2017 – Heat Loss Survey
Since May 2025 it no longer a requirement in England to...
By JamesPa , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handel @jancold Manufacturer: Daikin Model: E...
By Jancold , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@harriworld it was roughly 3am for an hour as that’s ...
By L2jad , 1 day ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
I have been wondering that myself. The fact is that, ...
By JamesPa , 1 day ago
-
RE: Filtering Tap Water – Share Your Setup for Cleaner, Better-Tasting Water
I remember when I was in my early 20s I was introduced ...
By Majordennisbloodnok , 1 day ago
-
RE: Setback savings - fact or fiction?
But if it is recorded an an integer, which it seems it ...
By cathodeRay , 2 days ago