Rethinking the mindset for mass retrofit - a provocative idea
Posted by: @chickenbigI'd be tempted to just drop rule i) as it seems unenforceable and puts additional red-tape on A2A heat pumps. Alternatively perhaps it could be inverted to "the air source heat pump must be used for heating purposes" to rule out cooling-only applications?
I don't think it puts additional red tape on A2A because it says 'used' not 'capable of' (fortunately). Most A2W HPs are also 'capable of' cooling. To the best of my knowledge only Vaillant sell A2W heat pumps which are not capable of cooling (well they are of course, but you need to buy a £200 resistor worth no more than £5, probably no more than 5p, as an accessory to 'convert' them, and in the UK they sell them without this resistor fitted I am told.)
I don't know what the authors were thinking but, based on my interactions with my LPA, I think a good rationale is as follows:
Dropping this constraint muddies the water on the noise issue.
A HP used solely for heating is only used when its cold, and most people (in particular the neighbours) are inside with windows closed. So the MCS-020 fixed sound constraint (sound pressure <= -37dBA at the assessment points), which is readily calculated by anyone, is also justifiable even if the background noise is lower than this value, because -37dBA will be inaudible inside.
As soon as you permit cooling then you have to assume that the unit will be used when windows are open and people outside. At this point background level needs to be considered if the HP is not to cause nuisance, in which case you introduce the need for a house-specific assessment, requiring a sound consultant and additional expense which burdens the installation of HPs for heating unnecessarily.
The current wording permits you to install a heat pump and use it for heating with a very simple noise calculation which makes sense given the characteristics of when they make most noise. If you want to use it for cooling you can always apply for planning consent later to do this and go through the full noise assessment etc. which matter for cooling.
Now you might say, once its in, how is this enforceable? I think the answer is that, if there were a complaint about noise whilst cooling, the LPA (which is also responsible for environmental nuisance) would investigate and either issue a planning enforcement notice or a noise abatement notice. Either is enforceable. And if there isn't a complaint about noise it doesn't matter that the rule has been breached! On balance its actually a well written part of the regs as far as I can see(!)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @chickenbigI'd be tempted to just drop rule i) as it seems unenforceable and puts additional red-tape on A2A heat pumps. Alternatively perhaps it could be inverted to "the air source heat pump must be used for heating purposes" to rule out cooling-only applications?
I don't think it puts additional red tape on A2A because it says 'used' not 'capable of' (fortunately). Most A2W HPs are also 'capable of' cooling. To the best of my knowledge only Vaillant sell A2W heat pumps which are not capable of cooling (well they are of course, but you need to buy a £200 resistor worth no more than £5, probably no more than 5p, as an accessory to 'convert' them, and in the UK they sell them without this resistor fitted I am told.)
I don't know what the authors were thinking but, based on my interactions with my LPA, I think a good rationale is as follows:
Dropping this constraint muddies the water on the noise issue.
A HP used solely for heating is only used when its cold, and most people (in particular the neighbours) are inside with windows closed. So the MCS-020 fixed sound constraint (sound pressure <= -37dBA at the assessment points), which is readily calculated by anyone, is also justifiable even if the background noise is lower than this value, because -37dBA will be inaudible inside.
As soon as you permit cooling then you have to assume that the unit will be used when windows are open and people outside. At this point background level needs to be considered if the HP is not to cause nuisance, in which case you introduce the need for a house-specific assessment, requiring a sound consultant and additional expense which burdens the installation of HPs for heating unnecessarily.
The current wording permits you to install a heat pump and use it for heating with a very simple noise calculation which makes sense given the characteristics of when they make most noise. If you want to use it for cooling you can always apply for planning consent later to do this and go through the full noise assessment etc. which matter for cooling.
Now you might say, once its in, how is this enforceable? I think the answer is that, if there were a complaint about noise whilst cooling, the LPA (which is also responsible for environmental nuisance) would investigate and either issue a planning enforcement notice or a notice to cease making the noise. Either is enforceable. And if there isn't a complaint about noise it doesn't matter that the rule has been breached! On balance its actually a well written part of the regs as far as I can see(!)
I suppose the noise aspect is very much a 'can of worms' and also subjective, since different individuals will have varying levels of noise tolerance.
We have an A2A heat pump which is used predominantly for heating, and only occasionally for cooling, and I would assess is not as noisy as our bathroom extractor fan. It is quite possible that A2W heat pumps will be used to produce hot water in the Summer months, so heating is not just a Winter pastime.
We live in a noisy World and most have become accustomed to a certain level of noise, so whatever system is used for heating and producing hot water, should be acceptable, provided that it is below the maximum acceptable noise levels.
I would personally suggest that A2A heat pumps are not included in the BUS scheme, since I suspect the net effect would be to increase the price of A2A systems, which at the moment are much cheaper than A2W. I also suspect, though don't have the data to prove it, that A2A heat pumps may be more efficient than A2W heat pumps, since they introduce at least one less heat exchanger into the equation. An A2A heat pump also raises the indoor air temperature much quicker than a water based heating system, since the fan coil unit is directly heating the air. I also read an article yesterday giving details of an A2A heat pump that could be used to provide DHW, when operating in cooling mode.
Today I watched an episode of 'The Climate Show' on sky news, were one of the topics was district heating at a village with older, difficult to heat, type homes. A district heating facility, using both GSHP's and ASHP's, produced a supply of hot water at temperature up to 70C, which was used to supply the homes without the need for any internal changes to be made.
Posted by: @derek-mI suppose the noise aspect is very much a 'can of worms' and also subjective, since different individuals will have varying levels of noise tolerance.
We have an A2A heat pump which is used predominantly for heating, and only occasionally for cooling, and I would assess is not as noisy as our bathroom extractor fan.
Quite possibly not. However ASHPs are associated with air-conditioning and LPAs are accustomed to imposing noise constraints. So I think we have to be thankful that there is a simple PD rule for ASHPs used for heating, bank that and move on.
Posted by: @derek-mIt is quite possible that A2W heat pumps will be used to produce hot water in the Summer months, so heating is not just a Winter pastime.
In summer they are unlikely to be working at their maximum noise level, because its warm. And producing water is not all day. So its a diminished level of issue in summer (when people are outside/windows open.
Posted by: @derek-mWe live in a noisy World and most have become accustomed to a certain level of noise, so whatever system is used for heating and producing hot water, should be acceptable, provided that it is below the maximum acceptable noise levels.
The problem is 'maximum acceptable' Its a fair argument that a higher level of noise is acceptable in winter than in summer because in winter people are inside. So Again, I think we have to be thankful that there is a simple PD rule for ASHPs used for heating, bank that and move on.
Posted by: @derek-mI would personally suggest that A2A heat pumps are not included in the BUS scheme, since I suspect the net effect would be to increase the price of A2A systems, which at the moment are much cheaper than A2W. I also suspect, though don't have the data to prove it, that A2A heat pumps may be more efficient than A2W heat pumps, since they introduce at least one less heat exchanger into the equation. An A2A heat pump also raises the indoor air temperature much quicker than a water based heating system, since the fan coil unit is directly heating the air. I also read an article yesterday giving details of an A2A heat pump that could be used to provide DHW, when operating in cooling mode.
I too am in two minds about this (and you are right they are more efficient). The person who suggested it, and those who supported it, on the Buildhub forum, were making that case that A2A is unfamiliar technology in the UK but, in open plan houses particularly, has a real place to play. I think they are right. They also argued that even in houses which aren't open plan, a single A2A downstairs may well eliminate 60% plus of the emissions. Personally I think this argument is strong enough to give the benefit of the doubt. I grant however that there is a risk of a price increase, although perhaps less so since there are plenty of A2A installers out there, nothing to do with MCS, who install in commercial premises where A2A is more or less the norm.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
It is my understanding that air conditioning units (A2A heat pumps) have the same limitations for permitted development as A2W heat pumps, the main reason that they are excluded from the BUS scheme is because they can more readily be used for cooling as well as heating, whereas an A2W heat pump requires additional equipment to be used for cooling as well as heating.
It is therefore permissible to install a A2A heat pump under permitted development, but you cannot claim the £5000 'bribe'.
Posted by: @derek-mIt is my understanding that air conditioning units (A2A heat pumps) have the same limitations for permitted development as A2W heat pumps, the main reason that they are excluded from the BUS scheme is because they can more readily be used for cooling as well as heating, whereas an A2W heat pump requires additional equipment to be used for cooling as well as heating.
It is therefore permissible to install a A2A heat pump under permitted development, but you cannot claim the £5000 'bribe'.
FUN FACT
Although the heat pumps have the ability to cool, they need a 2p resistor sold as a £250-£300 chip 🤣
£7 for the same thing for the gas boilers
https://www.mpmoran.co.uk/vaillant-boiler-spare-part-plug-coding-yellow-0020242593-109135116
€46-67 over the continent
https://lbge.be/product/vaillant-codeerstekker-voor-activatie-van-de-koelfunctie-0020269259/
Just something I noticed but according to USwitch- 80% of boilers in the UK are combis so the cost of a new DHW cylinder and related plumbing often included in ASHP quotes is going to be unavoidable for a large part of the prospective market. https://www.uswitch.com/energy/boilers/boiler-statistics/
Smart Tech Specialist with Octopus Energy Services (all views my own). 4.4kW PV with 9.5kWh Givenergy battery. 9kW Panasonic Aquarea L ASHP
@dougmlancs interesting, I'm surprised it's that high although with new properties being small it's perhaps not surprising.
Having had combos in the past I think this is a big challenge for the ashp market, space is a definite issue and the lack of physical variety in solutions (they are pretty much all a cylinder) is limiting.
I was in France recently and the rental property I had was fitted with a 90 litre wall hung rectangular tank with a 1.5kW immersion fitted in a little alcove. I googled it and they appear quite common and are as cheap as chips. Not sure how teenagers accustomed to unlimited power showers would cope.
I've so far deliberately avoided thinking about the combi/ashp issue as it's too difficult.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,057 Topics
- 44.9 K Posts
- 21 Online
- 3,299 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@editor it’s a defrost buffer, it uses an Esbe 4 way ...
By Damon Blakemore , 4 hours ago
-
RE: Rate the quality of your heat pump design and installation
@davesoa very good to know... I'll convey this to Clayt...
By Mars , 6 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 10 hours ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 11 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 2 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 2 days ago
-
RE: Is your heat pump insured?
@johnmo sorry it comes across like that. The post is au...
By KevinPotts , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo Perhaps a little detail might explain my reason...
By Toodles , 2 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 2 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 2 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 2 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 2 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 3 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 3 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 3 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 3 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 3 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Took a while to find on the OFGEN site: ”The FIT sche...
By AgentGeorge , 4 days ago