Question about Heating Pump Operation mode – Ecodan FTC6 v20.06
I have a Mitsubishi Ecodan EHST20D-YM9D with PUHZ-SWM80 outdoor unit, FTC6 controller (firmware 20.06), and an external 100 L buffer tank. The system is controlled via room temperature sensor.
I would like the internal heating circulation pump to stop immediately when the compressor stops, instead of running during heating demand but compressor is off and stop only when heat pump is in standby because indoor temp is reached.
Is there any installer parameter or menu setting in FTC6 (v20.06) that allows this — for example:
or perhaps a “Delay Time before pump switched off” that can be set to zero?
the reason why i want this is that the internal circulation pump is causing distortion in the buffertank if it runs when the compressor does not heat the water.
This isn't an exact reply to your question, as I don't have the same hardware as you, however if you want the primary/circulation pump to stop shortly (/immediately) after the compressor stops, on my FTC6 settings I'd adjust the following (see image - 'water pump' isn't that helpful here, it's not pump 4 that overruns, it's 1 & 2, and perhaps 3 if you've two zones) - I don't know if zero is allowed but the default is 10 mins overrun (and note the manual's commentary on the effect of reducing the time); without knowing what 'distortion in the buffer tank' means, I'd probably avoid zero if you can help it, if only to dissipate a bit of recently-generated heat [away from the outdoor unit]...
Thanks, I have à split model so there is no water circulating to and from the outdoor unit. Only between the cylinder and the buffer tank, and the from buffer to radiators.
the Buffer is a 4 pipe model, ment to have the coldest water at the bottom and the warmer water at the top.
As it works for me now is that the main water pump in the cylinder does not stop until the heating goes in standby due to indoor temperatur is overreached.
in autoadapt mode it goes on and cycles the compressor several times, and each time the compressor stops at the top of a heating cycle the waterpump continues to run hence pumping colder water from the bottom of the buffer through the cylinder and then back to the warmer water at the top of the buffer. It means i am cooling the top of the buffer which i already spent energy of heating up and seems to be a waste.
That is why i would like to configure the activation of the water pump to the compressor running.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 258 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 31 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 42 minutes ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 2 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 3 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 3 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 19 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 20 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 24 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 24 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago