Our Daikin ASHP
Hi Derek, thanks so much again for sharing your expertise.
You are quite correct I was confusing the terminology. I have put equilibrium temp back to the default of -4°C.
That makes complete sense, so we should expect to the ASHP running more given the higher pricing for gas and electricity. I will leave the curve at 45°C at -10°C and 25°C @ 18°C and with the lot max modulation now set at 10°C and monitor the cycling and overall COP.
Thanks,
Adam
Hi @adaml
When time allows, monitor how long the heat pump runs and then how long it is stopped before restarting. Also record the water flow and return temperatures, which may highlight any possible problems with your system. If your heat pump is running for short time periods then stopping for short time periods then it may be necessary to adjust some of the operating parameters.
Hi Derek,
I've been watching it run tonight and it is sometimes running for about 20 minutes and then stops and other times it is starting, running for only a couple of minutes and then stops. The required flow temp for tonight is showing as 31°C. The required was showing as 26°C and the lwt modulation seems to have increased this. The house is sitting at 21.7°C at the moment.
I think one potential problem could be that the Daikin thermostat/controller is situated in our downstairs hallway, with the kitchen door relatively close to it. This means that when we're cooking the temperature raises in the hall and trips the thermostat off, despite other parts of the house being cooler. I wonder if increasing the thermostat temp in the hall to say 22°C could be worth a shot?
Jan shows the compressor has been running for 4 hours with 42 starts at the moment. Other snapshots were 27 at 2 hours and 36 at 3 hours.
Stats from the controller tonight, couple of snapshots;
Outdoor temp. 9.0°C
Leaving water 26.8°C
Leaving water (PHE) 26.8°C
Inlet water temp. 25.3°C
Refrigerant temp. 26.0C
Flow rate 12.9l/min
Outdoor temp. 9.0°C
Leaving water 30.4°C
Leaving water (PHE) 30.0°C
Inlet water temp. 30.2°C
Refrigerant temp. 29.7C
Flow rate 12.6l/min
Hi @adaml
First of all let's clarify what is meant by running, do you mean that the compressor is actually running, or that it is just the water pump that is running?
The water pump is often started before the compressor is started, and continuous to run for a short period after the compressor has stopped. The water pump is also run for short periods of time to check the water temperature, so that the controller knows when to start the compressor to provide more heat energy.
Looking at your snapshots, I would say that the upper one has the water pump running but the compressor is stopped, and in the lower one both compressor and water pump appear to be running.
I think that you may find that the data relating to running and starts should be interpreted in the following manner.
'Jan shows the compressor has been running for 4 hours with 42 starts at the moment'.
I think that this actually means that since the start of January, the compressor has run for a total of 4 hours, and since the start of January the compressor has started 42 times. So it would appear that what has actually happened is that the compressor has started 42 times in approximately 42 hours, so has started on average once per hour, and has run for an average 5.77 minutes each time.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 32 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@patrickvito We have had car dealers re-powder coat the...
By ASHP-BOBBA , 15 minutes ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 45 minutes ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 47 minutes ago
-
Engineer has been. Prob air locks....undid a few things...
By Profzarkov , 2 hours ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 4 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 5 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 7 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 8 hours ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 18 hours ago
-
@drei When I was in local government we were of cours...
By JamesPa , 1 day ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 2 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 2 days ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 2 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 3 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 3 days ago