New member - advice sought on Mitsubishi heat pump
Hello, just joined after going through most of the heat pump info on this site. Great site! - loads of useful info.
I'm new to heat pumps but am a chartered engineer with good electrical/electronic/mechanical knowledge - and a deal of practical electrical and plumbing installation. Recently acquired a 3 year old Mitsubishi (W85VAA) 8.5kW packaged heat pump together with an FTC6 control box. Heat loss calculations for house showed annual heating requirement of 6600 kWh (space heating load of 5.3kW) and recommended a 6kW ASHP.
House is a well-insulated timber frame construction in Bedfordshire with gas boiler to UFH on ground floor and radiators first floor. The current system is well-controlled and running fine so my thoughts (for which I would appreciate comments) is to utilise the ASHP in a hybrid situation until the boiler is end-of-life and then go full heat pump. My thoughts would be to connect the heat pump inside the house to a plate HEX in the return pipe to the boiler. That might sound crazy when there is already a plate HEX inside the outdoor unit but I really don't want glycol mix running round the whole system - and current controls are adequate! I guess the heat pump circuit would need a pump and expansion vessel inside the house. Comments and criticisms from the experts welcome!
Hi @jvs197 and welcome!
My first observation is that your 8.5kW ASHP is already oversized for your sumptuously-insulated house.
So your system design will need to avoid two possible events
- the HP cycling on/off, which uses more energy (and hence lowers the COP)
- the return water temperature to the HP being too warm... because it's unable to export enough heat into the boiler circuit via your HEX
At this point it is usual for a professional installer to insert an overly-expensive buffer-tank in the return pipe to the HP.
Heat is lost in that, thereby keeping the return water cool enough.
It's worse in your case because you aren't sending the output from the HP to anywhere else... just the HEX.
My next observation is that the rise in temperature of the return to the boiler is bringing forward the moment when it will drop out of condensing mode.
So it too would now be operating inefficiently.
The key to these issues must surely lie in a 'control' which prevents the boiler firing if the water arriving in it's return is above the temperature at which the condensing operation ceases.
It's typical of an Arduino project... which you may find appealing, given your background!
One of the first professionally implemented Heat Pump trials in the UK was done with funding assistance from the Welsh Government.
The Freedom Project implemented hybrid heat-pump systems in a number of housing authority homes.
Unusually, the highly competent engineers who designed the systems also supervised the installation and operation throughout the trial.
The results therefore show a level of competence which was in short supply from later BEIS-funded trials!
If I wanted to analyse the best way to implement a hybrid system, that's where I'd start.
The Freedom engineers were drawn from Western Power Distribution (electricity) and Wales & West Utilities (gas).
Some those engineers now work in senior roles within National Grid Electricity Distribution.
With a bit of ingenuity, you can probably work out their email addresses and contact them direct!
Save energy... recycle electrons!
Posted by: @jvs197Heat loss calculations for house showed annual heating requirement of 6600 kWh (space heating load of 5.3kW) and recommended a 6kW ASHP.
We swapped to a HP 2 years ago, after running a regular gas boiler for many years. We have smart meters, so could correlate daily gas kWh with the outdoor temperature. An advantage of gas boilers is that gas in very closely aligns to heat out - just assume an efficiency of 90%. Do you have figures for how many kWh/year of gas you have used? It's a great way to check the calculations!
I'm a little confused by the figs you gave - 6600kWh annually is lower than a heating load of 5.3kW would imply. Our measured numbers are 4500kWh/yr heat (using 1400kWh elec), 2kW peak heat load.
While "short cycling" of a heatpump is bad (more than 6 On/Off cycles per hour), there will inevitably be On/Off cycling when you need less than the minimum power of the heatpump which is perhaps 30% of full power. Cycling fatigues copper joints, and leaves heat in the outdoor stuff which is a waste. Our heatpump cycles once / hour, and can't be avoided as I see it.
The manufacturers will give minimum required system water volumes, so that there's enough thermal mass to cope with defrost. Zoning and TRV throttling reduces the minimum volume, and is the reason that a buffer is generally added. We don't have a buffer, have no zones, TRV's either removed or set to max.
Cheers, R
@transparent Thank you for your quick reply (anyone want an 8.5kW HP?!!)
Yes, I was a bit concerned that the HP is over-powered but then, with the assumptions made in heat loss calculations (I used the HeatPunk one), the final figures are only 'ballpark'. If I had an 11 or 14 kW Mitsubishi then I would certainly not go ahead - but 8.5...? In fact I have seen on this site that some over-sizing is quite acceptable in some folk's opinions.
Interesting point about boiler not condensing because return water temperature might be too high. I understand that it needs to be below 55 deg. The calculation for the heat pump was based on a flow from the HP at 45 deg - so no worries there.
Yes, need control to prevent boiler firing if return too hot - but that's a simple circuit (no need for microprocessors!). That point should not however be reached as explained above.
Thank you for your hint about 'FREEDOM'.
@robl Thank you for your reply. The 5.3kW figure came out of the heat loss calculation (using HeatPunk). Gas consumption over the last year was 9890kWh covering space heating and hot water (and a little for cooking). Took the consumption in July/Aug as predominantly meeting hot water requirement and assumed the same rate over the whole year - that was 3270. So space heating was 6620. I accept that figures were therefore approximate!
Posted by: @jvs197I understand that it needs to be below 55 deg. The calculation for the heat pump was based on a flow from the HP at 45 deg - so no worries there.
Erm... what's the return water temperature for your boiler in its present situation?
If it's above 45degC, then your HP won't be able to add anything more to it.
Messrs Flanders and Swann told me that!
Save energy... recycle electrons!
I suggest that you experiment with your present gas system, so that you can determine how well an ashp could work. It’s what I did before installing our gshp. We had a ‘regular’ gas boiler- ie just a heat source, and a smart gas meter. I set the pump to mid, the boiler to low flow temp, the home thermostat to highest, all TRVs on full. Then ran the system for an hour to let it stabilise, upped the flow temp a little to stop it cycling on/off. When running stably, I used a thermocouple taped (and insulation over it) to the boiler flow and return, home air temperature and took a note of the smart meter gas power. From these measurements I accurately predicted the running temp that we would get with a heatpump, just by linearly extrapolating them. I got a 5C ( Tflow-Tair) rise per kW of heat, and a 2C deltaT. This predicts a flow temp of 21C+2.4kW*5. Our gshp is 2.4kW, and it runs at a flow of 32C. (Nb- we have 150mm of EWI now, so this approach works well for us - the original 1963 radiators are now ‘oversized’).
Strictly speaking rads aren’t quite linear, but it’s close enough I think if the difference is small.
-
Where has Watson gone?
9 hours ago
-
First time wall mounting an ASHP
2 weeks ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
3 weeks ago
-
Rodents! A word of warning for heat pump owners
1 month ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
2 months ago
- 26 Forums
- 2,306 Topics
- 51.7 K Posts
- 208 Online
- 5,970 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Commencing on an ASHP Installation Process
Me too, but I think we are in the minority. Most homeo...
By JamesPa , 1 hour ago
-
RE: Electricity price predictions
Simple article with a DENZ graph showing how gas which ...
By Jeff , 2 hours ago
-
RE: 10kw heat pump run in 24*7 data?
Thats really helpful as it clearly says target 49C. So...
By JamesPa , 2 hours ago
-
Power Cut - Heat Pump Evaporator Iced Up
We have just had a power cut and 1 hour later power was...
By trebor12345 , 3 hours ago
-
RE: Buffer tank bypass on EDF Ideal heat pump installation
Well I can try the valving which can be undone so I don...
By KevB , 4 hours ago
-
@sand Yes. The COP is reported and you can split it int...
By bontwoody , 4 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
A few weeks ago, I was having a discussion with someone...
By Majordennisbloodnok , 5 hours ago
-
RE: Don’t Install a Heat Pump Until You Read This
@davidnolan22 Inspired by someone on buildhub I asked C...
By JamesPa , 5 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk Hi I see you posted on openenergymon...
By JamesPa , 7 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Often the default password is in the installation manua...
By JamesPa , 7 hours ago
-
RE: Cashback Incentives That Reward Shorter Heat Pump Warranties
@andrewj Indeed, ’Appalling’ is a rather mild term for ...
By Toodles , 8 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
@editor When do “Mars Heat Pump Installation and Servic...
By Toodles , 8 hours ago
-
@morgan Likewise, I realise that some readers will appr...
By Toodles , 9 hours ago
-
A Smarter Smart Controller from Homely?
I received an email from Homely this morning enquiring ...
By Toodles , 9 hours ago
-
RE: Grant Aerona 3 and Drayton system questions
Yes in general terms (obviously I cant tell if its exac...
By JamesPa , 11 hours ago
-
Yes, the Grundfos pump has a built in timer. However, t...
By DavidAlgarve , 12 hours ago
-
RE: Heat Pump on Flat Roof Low Frequency Noise from Detached Neighbor
1) talk to your neighbour, that's unacceptable noise, a...
By davidnolan22 , 13 hours ago
-
Ecodan - Flow temperature spiking causing shutdown
Hi everyone, looking for some help. I am in a new bu...
By Gl3484 , 1 day ago
-
Solis AI is on the right track to leverage the battery:...
By Batpred , 1 day ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Thanks James, its honestly hard to keep it tog...
By Crimson , 1 day ago