Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
The Full Installation Service
Octopus provides a complete installation service, handling everything from the initial quote and survey to supply, removal of old equipment, installation, commissioning and aftercare support. If, like me, you’re looking for a turnkey solution, this comes as close as I’ve found.
However, it’s not yet a commercial off-the-shelf (COTS) product. Having gone through the conversion from a gravity-fed water system to mains supply, I found this was a bigger deal than expected. The pump itself has been great, and I highly recommend ASHPs.
Here’s my take on how things went with this new technology and bespoke installation.
The Quote
In May 2024, I saw an Octopus campaign on Facebook offering a “quick quote” for heat pumps and solar. I clicked through and received a quote almost instantly.
The following week, I had a pre-sales call with Octopus to go over details. The process involved a £500 fully refundable deposit (which is now down to £200) to get a heat loss survey. I decided to go for it. My 24-year-old 3kW Ideal system boiler was showing its age. Since I was planning a kitchen refurbishment and considering moving to a combi boiler in the airing cupboard, this seemed a more long-term option. Gas will be phased out in the next 25 years, so I didn’t want to be stuck with an obsolete gas boiler.
Though the wait time was expected to be up to three months, there was an opening the following week, so I booked it.
Why I Chose Octopus
I wouldn’t say I’m an Octopus fan, but I am a convert. I checked out founder Greg Jackson and his values, which I found aligned with my own. Having worked in high-tech and multi-billion-pound corporations all my life, I know all big companies have their downsides, but Octopus has been impressive. I’d been moved to Octopus from Bulb after they went bust. For anyone interested, there’s a great interview with Greg Jackson by Heat Geek, which gives insight into the company’s vision.
The Octopus service includes a pre- and post-contract insurance policy with HIES, electrical certification through NAPIT, and MCS certification, which grants access to the £7,500 Boiler Upgrade Scheme (BUS) via Ofgem. Given the horror stories of fly-by-night installers and local companies online, Octopus felt like a safe bet.
At this point, I broke from tradition and didn’t seek other quotes. I didn’t feel knowledgeable enough to make an informed choice, so, like picking wine by the label, I chose based on Octopus’s reputation.
The Survey
Not knowing much about heat pumps, I turned to the internet and came across Heat Geek, Renewable Heating Hub and Skill Builder on YouTube. It all seemed quite complex. I’m an engineer by trade and a project manager by occupation, so I’m comfortable with numbers. I even tried a few heat loss calculations through online radiator shops.
When the Octopus surveyor arrived, he spent about five hours on the survey. He went over radiator plans, room-by-room heat loss, the 50°C design flow temperature and cable routing. We also discussed the loft insulation, and placement of the ASHP and consumer unit. I felt reassured by the surveyor’s approach and the quality of his analysis.
The Results
Most of the discussion focused on my pipework. I live in a timber-framed, well-insulated 2000-built semi-detached home. Two years ago, I added 300mm of loft insulation. The old boiler was fitted with primary pipework that runs from the kitchen to the airing cupboard and loft, where there’s a header tank. The pipework is 10mm microbore, which Octopus allows as long as it’s barriered, which mine is.
After discussing the radiator plan, I signed the contract, and within a week, I had an install date for August – just two months away.
The Equipment
The heat loss survey was done with a design temperature of 22°C for bathrooms, 18°C for bedrooms and 21°C elsewhere, with an outside design temperature of -2.4°C. The survey showed a heat loss of 4.1kW. The surveyor recommended swapping six radiators, providing a total output of 4.6kW. Initially, Octopus specified a Daikin Altherma 4kW Monoblock with a 180L hot water cylinder. Later, I switched to the Cosy 6 and upgraded to a 250L cylinder, as recommended by MCS.
Pre-Installation Requirements
The only pre-installation task on my end was clearing a space for the pump in the garden. Octopus handled everything else, including a new EPC, BUS grant application and DNO approval for the electrical circuit. My EPC came back as a C rating, and the BUS grant was approved.
Cosy 6 Launched
After signing the contract, I was offered a swap to the Cosy 6, Octopus’s in-house unit. Given that the future of Octopus seemed to be in its own products, I decided to switch to the Cosy 6. I also upgraded to a 250L hot water cylinder to better meet my household’s needs.
Pre-install Setup
A week before installation, scaffolding went up so Octopus could run a cable from the new consumer unit through the loft to the ASHP. The scaffolding was up front and back, depending on where your installation needs it, and was taken down a few days after installation.
The Installation
Planned for five days, the installation took six. A team of plumbers and electricians arrived on day one with all the required equipment. The ASHP site was prepared with a hard-standing base instead of a soakaway. My pump’s site is close to the garage wall, making for a very short external pipe run.
Inside, Octopus installed the DHW cylinder, a 26L volumiser, a Fernox TF1 filter, ESBE diverter valve, expansion vessel and a by-pass valve. In the airing cupboard, they cleared out the old system, making it available for storage. Octopus also took care of all the installation waste.
Conclusions
The system was completed with thermostat and humidity sensors (one per zone; I have one zone with two sensors). The small, wireless sensors are discreet and functional. The Cosy Hub, which connects to Wi-Fi, was set up quickly and is straightforward to use. Though the app currently has basic functionality, the system defaults to weather compensation, which has kept our home warm.
In October and November, with outdoor temperatures around 7-11°C, the ASHP used 234.01kWh, delivering 964.32kWh of output with a SCOP of 4.12. The Cosy Tariff, with three off-peak slots daily, has also been beneficial.
Finally, I opted for the £9/month service plan (included free for the first year), covering annual maintenance.
The Octopus Cosy 6 ASHP – What is it?
The Octopus Cosy 6 Air Source Heat Pump (ASHP) runs on R290 (propane) refrigerant. This system has a 6kW output and is installed with a Cosy Hub controller, along with up to four thermostat and humidity sensors. For Octopus customers, it can be accessed in the Octopus App under “Devices.” Recently, Octopus also announced the Cosy 10, a 10kW version of the heat pump.
@wreckguru where was the heat pump finally installed, as in the final location?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor it's in the back garden, behind the attached garage. It faces the same way as the solar so 145 degrees SE and gets a bit of sun.
The DHW is the other side of the garage wall with a short flow/return about 50cm.
Your edited article looks good.
@wreckguru so the actual heat pump is not sited near a door or window?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor well the house has both😂
To the left in this picture there is a door, to the right the kitchen window. A bit further down the wall an air brick.
A building surveyor passed the site for controlled zone. This was done during the swap from Daikin to Cosy.
Given I keep 10,000 L of medical grade oxygen at 220 bar in my garage I am not concerned at all about a tea cup of refrigerant in my garden.
This is just a small point, to get SCOP value you have to run it for a whole year. I think you mean COP.
@wreckguru can’t say I disagree with your assessment and choices. Just for clarity in light in light of this article and journey, did Octopus ever give you advice on positioning?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor yes. For the initial assessment for the Daikin we basically ruled out all my thoughts and landed at the current spot.
When changing to Cosy the assessor needed more measurements and pictures before oking it.
The swap was done late in the day, just days after it was available and not confirmed till Thursday before the team arrived (after the scaffolding was up).
As sure as I can me this is #1 install (it is for this team😂)
App estimates SCOP from COP. I don't know if it is using the rolling figures or something else, there is no info. I suppose that would make sense and would agree with your comment.
-
7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
2 weeks ago
-
Bosch CS5800i 5kW - Experience So Far
3 months ago
-
Yes, the "zoning with ASHP" topic again...
12 months ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
2 years ago
-
Low shower pressure after ASHP retrofit
2 years ago
- 26 Forums
- 2,610 Topics
- 60.8 K Posts
- 279 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Anyone concerned about GivEnergy?
Yes and no. Native controllers generally do a good jo...
By Majordennisbloodnok , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@temperature_gradient I've had air-to-air for just over...
By Anne Smith , 12 hours ago
-
RE: Home automation and the cloud; is there a better way?
+1 It's not just cloud though. Many devices have repla...
By bobflux , 12 hours ago
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
We've started to document everything, and part 2 of the...
By Mars , 18 hours ago
-
RE: Summer usage. Why is my Vaillant Aerotherm using so much energy on "heating"?
So the red bars are 'DHW' and the yellow bars 'heating'...
By JamesPa , 19 hours ago
-
Its good kit the Midea and significantly cheaper, you w...
By ASHP-BOBBA , 22 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Have you tried cutting the grid feed to see what actual...
By JamesPa , 22 hours ago
-
Contractors pack for inta antifreeze valves are around ...
By ASHP-BOBBA , 22 hours ago
-
RE: Renewables & Heat Pumps in the News
Critics and naysayers will be negative whatever the gov...
By JamesPa , 22 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 1 day ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 1 day ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 2 days ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 2 days ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 2 days ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 2 days ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 2 days ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 3 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 3 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 3 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 4 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 4 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 4 days ago