Posted by: @iantelescopeHeat-Ex-changer upside down ?
Is it possible that my Heat -Exchanger was installed with the temperature difference , or gradient , hot to cold, in the same direction between input and output ports?
I know, I have asked this question before ,so please accept my apologies in advance ............. a seniority deficit!
My EAC Heat Ex-changer has no markings other than the EEC directives .
I have been here before ...............but as Oliver Cromwell did not say to the General assembly in 1651, I do " think it possible that I could have been wrong", maybe the heat ex changer is fitted upside down!
As you state, it is not so much orientation as flow direction.
If the PHE is mounted vertically, the flow from the heat pump should enter at the top of the primary side and return to the heat pump from the bottom of the primary side.
The water from the heat emitters should enter at the bottom of the secondary side and exit from the top of the secondary side.
Heat Ex changer confusion!
My heat ex changer has a hidden torn label giving the (assumed standard) EEC Port connections , K1,K2,K3 and K4. as,
K1 = Primary Hot water Input
K4 = Primary Input Cold, Return
K2 = Secondary Cold Water Input
K3 = Secondary Hot water Output
My Heat Ex changer has been configured such that :
K1 = Secondary Cold Input
K4 = Secondary Hot Output
K3 = Primary Hot water Input
K2 = Primary Cold Water Return
I have a Heat Ex changer that has the correct gradient , Hot to Cold, but is a mirror image !
Does this mirror image, Outputs and inputs being reversed have any effects on the Heat Ex changer performance?
Time for stiff coffee!
A photo would be useful.
Many thanks derek , my heat ex changer is , probably , been wrongly mounted !
My heat ex changer has a hidden torn label giving the (assumed standard) EEC Port connections , K1,K2,K3 and K4. as,
K1 = Primary Hot water Input
K4 = Primary Input Cold, Return
K2 = Secondary Cold Water Input
K3 = Secondary Hot water Output
My Heat Ex changer has been configured such that :
K1 = Secondary Cold Input
K4 = Secondary Hot Output
K3 = Primary Hot water Input
K2 = Primary Cold Water Return
I have a Heat Ex changer that has the correct gradient , Hot to Cold, but is a mirror image !
Does this mirror image, Outputs and inputs being reversed have any effects on the Heat Ex changer performance?
The heat pump is feeding hot water from the heat pump into the bottom of the Heat Ex changer port K3 instead of the K1 port .
The Flow directions are ,however, opposing .................that was why I previously assumed that the heat pump was correctly configured.
Mental gymnastics of Heat Ex changers?
Posted by: @derek-mNormal practice is to carry out a legionalla cycle once every 7 to 10 days, so during the Spring through to Autumn period there should not be a problem.
But do you need to do it all? 45 to 50 legionella is dormant, 50 degs 90% is killed within 2 hrs. If you have a decent turnover of hot water do you need the cycle at all?
We just store at 50 and heat to that twice per day. Anything in there is dead. Most of the cylinder contents are either at above 45 and dormant or above 50 and actively being killed.
Main water in UK is treated to kill just about anything, so if it doesn't exist, what are you killing?
@johnmo I think the danger is not from the water supply as such, more a case of air borne bacteria. (Someone will be along to correct me if I am talking wrollocks. Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodles@johnmo I think the danger is not from the water supply as such, more a case of air borne bacteria. (Someone will be along to correct me if I am talking wrollocks. Toodles.
Airborne may be relevent in an open vented cylinder but
Water is treated by chlorination or other means and passed under pressure around the country in a sealed system. Enters house, goes into an unvented cylinder all sealed from atmosphere. Only in contact with air as it comes out of tap etc.
@johnmo I seem to remember when large outbreaks were traced to an air conditioning system as water passed through cooling processes involving mesh filters and evaporation processes or similar. After several lethal outbreaks, H&SE regs were brought in to prevent air borne transference of the spores responsible. Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodles@johnmo I seem to remember when large outbreaks were traced to an air conditioning system as water passed through cooling processes involving mesh filters and evaporation processes or similar. After several lethal outbreaks, H&SE regs were brought in to prevent air borne transference of the spores responsible. Toodles.
Not much to do with the legionella cycles on an unvented cylinder?
Photographs may not help ....but here goes.
The remains of the label gives the following information:
Designed and Manufactured
according to
PED/97/23
EAC
A drawing :
k2 top left
k3 bottom left
k1 top right
k4 bottom right
The Standard EEC designations are given online for K1,K2,K3 and K4.
These photographs show the Heat Pump feeding hot water into K3 .
These photographs show the HEX feeding radiator hot water into the second, radiator, motor.
This photographs show the HEX outputting the primary , HP Cold return from K2.
This photographs also show the Cold Radiator water returning to K1 on the HEX.
Sorry about the photographs ...............difficult to show the pipe connections.
I now doubt that the mirror imaging , with inputs mirrored to outputs would make any appreciable difference....................but I could be wrong.
@johnmo Also, if I remember correctly, the first instance of legionella came about at some sort of convention of old retired Legionnaires (hence the name given to the problem). I seem to also remember that the BBC had a case of it in one of their cooling systems (at Broadcasting House, London I think, memory is a little hazy now). How the spores get into what is effectively a closed loop system of water distribution is outside of my Bailiwick! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
For most efficient heat transfer, the primary inlet should be at the top so that the water is cooling as in flows down to the exit at the bottom. The secondary inlet should be at the bottom, so that the water heats up as it rises, with the exit being at the top.
I'm not certain if using the primary as the secondary and vice versa will cause any reduction in efficiency. You could try asking the manufacturer.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 39 Online
- 3,410 Members
Join Us!
Latest Posts
-
@jamespa Thanks. I did not instruct them not to insul...
By Eliuccio , 43 minutes ago
-
RE: No-code, plug-and-play monitoring for your heat pump
To update an ESP device using ESPHome in Home Assistant...
By Grantmethestrength , 50 minutes ago
-
RE: Compressor and Evaporator Stratification
@trebor12345 I must admit I noticed that about Hitachi ...
By ASHP-BOBBA , 2 hours ago
-
RE: Is this just haze or something more?
I am not a scientist nor a meteorologist and I know the...
By Toodles , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
It will improve performance, but by how much depends on...
By Brendon Uys , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Said I would pop back with a update. Only Mr Jesus h...
By Burtis , 3 days ago
-
RE: Buffers, hot water and cooling
Thats presumably heat pump DT, what about radiator DT a...
By JamesPa , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Exactly the same here. We now have 13.5kWh ...
By Old_Scientist , 3 days ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 4 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 4 days ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 4 days ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 4 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 5 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 6 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 1 week ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 1 week ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 1 week ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 1 week ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 1 week ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 1 week ago