Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@iantelescope there’s so much about MCS and the secondary and tertiary organisations lurking behind the scenes that just doesn't add up, and it's genuinely giving me a headache.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
On this , and other forums I suspect that I have overdone my criticism of some of the Engineers who have appeared in my kitchen over the last two years.
All Heat Pump Engineers are not however uniformly incompetent , innumerate or illiterate. Many are trying to repair devices without experience , measuring equipment, circuit diagrams or spare parts.
Some Heat Pump engineers have said that "in their opinion , Heat Pumps are NOT THE SOLUTION to the energy crisis ................they are BUT ONE SOLUTION ."
The Next "Engineer" who appears in my kitchen , however, would be advised NOT to use You Tube as the SINGLE source for repairing my HEAT PUMP.
Warning, the next " Engineer" who, under the supervision of a You Tube video , who installs pumps or flow sensors on the wrong pipe will be promptly ejected through my front door.
Questions about Octopus?
My Energy supplier, the woeful Shell Energy, has been taken over by Octopus.
Does anyone know if Octopus any good as HEAT PUMP repairers or Installers?
Apart from my Faulty Heat Pump , my Shell supplied Smart Energy Meter has not worked for the last two years!
Again, Do Octopus have a good record with Smart Meter installations or repair?
Hi,
You seem to be in a similar frustrating situation to me.
I, like you, have been repeatedly let down by my , now former , installer , the MCS and the NIC-EIC .
Unlike you, my "installer" has now been STRUCK OFF and subjected to multiple unspecified "sanctions" by the NIC on several occasions.
With my installer STUCK OFF, Home Energy Scotland refused to repay my initial down payment of £6k covering the initial Heat Pump installation.
The HES ( rightly !!) refused repayment of the Loan and Grant given the failure of my installer to test the system and provide the warranties for the Samsung Heat Pump and two Telford cylinders.
After many months my MSP obtained a direct contact with a manager within EST Scotland, with the EST agreeing to a " DRAW DOWN " payment in late December 2023.
Draw Down payments provide the Heat Pump customer with the , otherwise substantial , upfront funds, required for the installation.
If we can establish a system of direct communication I will safely give you the names of the managerial contacts within EST.
Please send me your Heat Pump story?
I understand that Octopus want to be trendy and be ahead of the curve but there aren't many houses in the UK that will pull off this purple look.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor There is a solution! https://www.creative-solutions-direct.co.uk/shop/category/air-source-heat-pump-wrapping-service#:~:text=Most%20Air%20Source%20Heat%20Pumps,its%20warranty%2C%20running%20or%20efficiency.
Regards with tongue in cheek, Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
@editor I found this on YouTube and it would appear the presenter has had an Octopus Energy onstallation recently and perhaps someone who uses social media (I don’t) might like to invite him to tell us how he rates his installation.
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles good suggestion. If anyone knows this chap or follows him please invite him. I’d be very curious to find out more.
On semi-related note, if anyone is on Facebook and is inclined to promote our forums to attract more users and grow our community, please feel free to do so.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
My "installer" was finally STRUCK-OFF for modifying the MCS House Energy Requirements to justify the installation of a Heat Pump they just happened to have available in their back room.
This feat of backward Engineering was accomplished by changing the Thermal conductivity of my walls .......until the total power equalled that provided by the Back room Heat Pump.
One of the installation engineers blushed , bright red, when discovered.
Adjustment of the Wall Thermal conductivity makes a mockery of the MCS House Energy requirements!.
Now entering my second year in my attempt at getting a stable and economic replacement for my Gas boiler can I vent my exasperation with the conflicting advice of Heat Pump experts.
I have a system, that , according to many of the "experts" is totally unnecessary , and constitutes an act of rear end protection.
Needless to say, many other "experts", including BOTH of my system manufacturers demand a Buffer for four different reasons:
1: To dump hot water during very cold Scottish nights, thus preventing icing.
2: To help isolate the Heat pump from changes in the water flow rate in the radiator circuit.
3: To reduce , or eliminate "Short Cycling" when the water temperature is reducing.
4: To reduce , or eliminate "Short Cycling " in Spring and Autumn when the Heat Pump is operating at it's lowest controlled power , usually one third of the system maximum power.
Similar arguments are put forward , and virulently opposed by other "experts" for my Heat Exchanger.
Both the buffer and the heat exchanger taken together loose some 22-23% in energy, so this is no academic conversation.
Buffer ....Yes or No?
Heat Exchanger........ Yes or No?
I understand the arithmetic for calculating the buffer size , but, as the MCS says, "a buffer will increase your running costs".
Hi Ian,
I understand your frustration, particularly when being provided with conflicting advice.
It is still my considered opinion that if at all possible buffer tanks should not be installed in the first place, and if one has been installed it should be re-piped to convert it into a volumiser.
Item 1. A buffer tank will not prevent icing, and unless it has a reasonably large volume will not help too much during the defrosting process.
Item 2. You actually need sufficient water flowrate through both the heat pump and the heat emitters. Having a buffer tank that is not correctly balanced can dramatically reduce overall efficiency.
Items 3 & 4. A heat pump is always going to cycle once the heating demand falls below the minimum continuous thermal energy output of the heat pump. As has been discussed previously on the forum, there are different methods of control that can be used to minimise cycling to improve overall efficiency, it is a matter of finding the method that works best for your system.
Without reading back through the various threads, where is the PHE that you mention?
Hi Derek,
Please accept my apologies , I am at my wits end with the second anniversary of my Heat Pump odyssey.
A recent visit by a pair of "engineers" from my , now former, Installer, accompanied by an " NIC Inspector" totally destroyed any confidence in both my Installer and the NIC.
The trio of "engineers" attempted to force the Water Temperature when the Water Temperature was controlled by the Samsung Weather Compensation module , aka Samsung Water Law.
The trio abandoned the attempt leaving the Heat Pump faulty and inoperative .
I repaired the heat Pump within 30 minutes of their departure.
The NIC "engineer Inspector" was upset by the Buffer tank and the Heat Exchanger saying he had no knowledge or experience of Weather compensation , Continuous Power control , Buffer Tanks or Heat Exchangers!
Despite having no knowledge or experience , the NIC "Expert Engineer" proceeded to attack me for fitting the buffer tank?
Plate Heat Exchanger, PHE
The PHE came with the Telford 200 litre tank fitted by Telford to "provide hydraulic isolation and prevent Glycol from entering the radiator circuit".
The PHE (hopefully) protected the Heat Pump when my "installer" ran the heat pump without fitting a Expansion vessel, flow rate meter or PRV, whilst attempting to run the heat pump during the first month of the installation.
I do not know what damage was done to the Heat Pump , running for a month without sufficient cooling water !!
50 litre Buffer
Telford, the tank manufacturer, said , in a telephone call that "All their Tanks should be fitted with 50 L Buffer tanks , without exception"!
Samsung -Dalliam in Wigan also recommended the installation of a Buffer tank "to prevent Ice build up on the fins of the Heat Exchanger".
My "installer" then intervened saying that "their boys are perfectly capable of installing the Buffer Tank".
My "installer", then STRUCK-OFF for the first time, went silent for two months before announcing that " a 50L tank had been found under the table of the , now former , chief maintenance "engineer".
NIC Engineer
The NIC engineer , a very nice personable character, abandoned me to a broken heat pump after the last visit.
de-icing
The de-icing routine, where the contents of the Buffer tank are dumped into the heat pump , does seem to work during the cold Scottish nights , often dumping water up to four times while consuming no electricity.
De-icing works ........but I do not know how well!
Since fitting the Buffer tank , no vast water vapour clouds have appeared .......but that could be different weather conditions.
"Short Cycling"
I can reduce, and almost eliminate, short Cycling, by increasing the Samsung water law Graph and/or increasing the setting on the Water law Thermostat but at the cost of efficiency.
Short Cycling has however contaminated the pipe water resulting in a black ink like residue , even after cleaning the pipes to BS7593:2019 at a cost of £600.
Many thanks Derek, your patience is appreciated!
Let me have a read back through your previous posts to see what suggestions I may be able to make.
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 298 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 5 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 5 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 6 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 6 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 7 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 7 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 8 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 10 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 11 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 13 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 15 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 19 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago