Mitsubishi Ecodan not good enough ?

68 Posts
13 Users
26 Reactions
7,993 Views
(@goody)
Trusted Member Member
137 kWhs
Joined: 1 year ago
Posts: 25
Topic starter  

Hi

We used to heat our 1930's, well insulated, underfloor heated (with upstairs rads) home with a gas boiler set at 55c flow temp.

Since we had an Mitsubishi Ecodan 8.5KW heast pump fitted in March 2021-June 2021, by an incompetent company - Hero Renewables, we struggle to get anywhere near a comfortable room temperature. Since the installation Hero Renewables had been on BBC's Rip Off Britain and have thankfully ceased trading.

Outside, a very chilly -6C inside a very chilly 12C! I know we are in a cold snap with the weather, but last year we struggled when it went below 0C.

The pump is continuously on and we are hitting record daily electricity usage everyday since last week

Are we expecting too much?

I am so glad we kept the dirty coal fire!!

I am starting to decide which rooms we can sacrifice for the greater good, which is quite difficult when it is a full house.

I am thinking that the heat pump was undersized for the property, and we can either get a larger heat pump, but, someone will have to do some hard selling for me to be convinced that a larger pump will solve all our problems with cold rooms and extortionate electricity costs, or, go back to a gas boiler

I am waiting to hear back from Mitsubishi to hear what they suggest

Any ideas would be appreciated

Thanks


   
Quote
(@derek-m)
Illustrious Member Moderator
13705 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4163
 

Do you have any heat loss calculations for your home? Do you have a buffer tank or low loss header in your system? Is your system operating in weather compensation mode? How much energy are you using? How does that compare with your previous gas consumption?

 


   
mjr reacted
ReplyQuote
(@hughf)
Noble Member Member
2918 kWhs
Joined: 2 years ago
Posts: 479
 

Mitsubishi won’t help you….

What was the design flow temperature for this retrofit? That’s the key. And yes, it will run continuously when it’s -6 outside. The system was probably designed for -2 or -3.

And yes, heating a house continuously at those temperatures costs money. Be that gas, oil, electricity or coal. At the moment, oil is probably the lowest cost per kWh delivered into the property.

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote
(@parmstar)
Estimable Member Member
274 kWhs
Joined: 1 year ago
Posts: 51
 

sorry to hear this - we are having similar issues unfortunately! Ours has only been in 2 weeks so trying to exercise my consumer right to reject as it’s within 30 days - really wish I didn’t bother switching from gas! Been nothing but a nightmare.


   
ReplyQuote
(@oswiu)
Reputable Member Member
793 kWhs
Joined: 2 years ago
Posts: 121
 

Posted by: @goody

Since the installation Hero Renewables had been on BBC's Rip Off Britain and have thankfully ceased trading.

What did they say about them on the show? Did you experience the same problems as discussed on the programme? 

With regards to your issues, there is certainly a way to go with fixing this as 12C is quite the deficit, but I've seen some good improvements on this forum so there's no harm in trying before making a decision on upgrading or going back to gas. 

For starters in addition to Derek's questions, can you tell us a bit about the positioning of the unit outside? Is it in open space or surrounded on one or more sides? How far from the sides is it? How long is the pipe run from the pump to the house? What's the insulation on the pipework like? 

Then on your install itself, did you keep 55C as the design flow? Did your installer recommend changing any rads to meet this and did you do so? Can you see statistics on your unit regarding heat delivered and information from sensors? I would be interested in hearing the difference in temperature between incoming and outgoing water and the flow rate of the water at a time when you think it's going flat out to see if it's working to full capacity. 

A flow temp of 55C makes for an expensive system to run, but if your installer matched that up with the power of your rads at 55C from a heat pump then that's not a blocker on the output power of the heat pump, just the electricity used. 

Finally, have you implemented any basic easy wins on insulation? Eg draught proofing, adding a bit of loft insulation, secondary glazing where you only have single glazing? 

 


   
ReplyQuote
 SKD
(@skd)
Estimable Member Member
710 kWhs
Joined: 2 years ago
Posts: 55
 

Hi.  Just a thought, but has your Ecodan been set to one of the two Quiet Mode settings? 

 

It's not visible on the normal FTC displays, but if you can access your Service menu and open Heat Pump Settings you can see and edit Quiet Mode.

 

There should be 3 levels, max being full power. 

So if you're on less than three dashes the rated capacity will be reduced. 

I forgot that ours had been turned down and had to turn it back up this week.

Hope you get things resolved soon 🤞

Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6kW hybrid inverter; 10kWh LFP battery storage


   
Derek M and Oswiu reacted
ReplyQuote



Mars
 Mars
(@editor)
Illustrious Member Admin
16904 kWhs
Veteran
Joined: 3 years ago
Posts: 2337
 

@skd, can you post a photo of the settings page you’re referring to?

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU

Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk


   
ReplyQuote
 SKD
(@skd)
Estimable Member Member
710 kWhs
Joined: 2 years ago
Posts: 55
 

@editor Here goes Mars.  I've put the screens in sequence into a pdf.  Hopefully it views okay.  You do need to be able to access your FTC Service menu (between screen 1 and 2) - the default password should be 0000 (unless the installer changed it).

Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6kW hybrid inverter; 10kWh LFP battery storage


   
ReplyQuote
 SKD
(@skd)
Estimable Member Member
710 kWhs
Joined: 2 years ago
Posts: 55
 

Posted by: @skd

@editor Here goes Mars.  I've put the screens in sequence into a pdf.  Hopefully it views okay.  You do need to be able to access your FTC Service menu (between screen 1 and 2) - the default password should be 0000 (unless the installer changed it).

 Just to add that the photos show mine in the quietest mode (one dash).  

Interim = two dashes;

Full power = three dashes.

 

Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6kW hybrid inverter; 10kWh LFP battery storage


   
ReplyQuote
(@benseb)
Reputable Member Member
735 kWhs
Joined: 2 years ago
Posts: 105
 

Just to add, I’ve found my Ecodan excellent in this cold snap. It’s not faultered once and has kept us nice and warm. 

So if you can get the install and commissioning sorted, you can be reassured the actual heat pump is good (as long as corrrctly specced)

250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.


   
ReplyQuote
 SKD
(@skd)
Estimable Member Member
710 kWhs
Joined: 2 years ago
Posts: 55
 

Posted by: @benseb

Just to add, I’ve found my Ecodan excellent in this cold snap. It’s not faultered once and has kept us nice and warm. 

So if you can get the install and commissioning sorted, you can be reassured the actual heat pump is good (as long as corrrctly specced)

Yes definitely.  Excellent piece of kit so far,  now nearing first full yesr of service.  Not troubled at all by -8degC, snow, freezing fog etc recently.

 

Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6kW hybrid inverter; 10kWh LFP battery storage


   
ReplyQuote
(@goody)
Trusted Member Member
137 kWhs
Joined: 1 year ago
Posts: 25
Topic starter  

@hughf 

Yes, you are correct,  it was designed at -3 C

Thanks

This post was modified 1 year ago by Goody

   
ReplyQuote