Minimum ASHP outputs?
Posted by: @sunandairSo to summarise:- Of the 365 days of the year our heat pumps will try to operate for 160 days at less than 20% capacity. (If they can cope with the modulation, that is.)
On the other side of the coin - although not the subject of this topic - the heat pump will operate at greater than 80% capacity on only 12 days. Although an installer can be expected to design a system capable of meeting the heating requirements on these days, other influences are likely to lead to over-specification. Without over-specification, the customer may be prepared to accept a handful of days when heat pump is struggling (e.g. to avoid a planning application, avoid a double-fan unit, avoid radiator replacement, etc). This is a variant of the '80/20 rule' - 80% of what you want for 80% fewer issues.
Posted by: @sunandairPosted by: @robsWhat was the total output capacity of your radiators at a flow temperature of 30C? Is it less than the minimum output of your heat pump at 30C flow temperature?
At a 21kw combined rad load
30c LWT = 1.785kw total output
35c LWT = 3.47kw total output
The first issue I recall, was to notice that the manufacturers correction charts do not go down low enough or fine enough to take account of 5c circuit DT (temp drop) and 30c LWT.
...
So after a bit of trial and error I was left thinking the 30c outlet temperature at under 2 kw output it was the reason for the cycling we encountered.
Yes, your figures correlate well with your heat pump having a minimum output of about 3kW at these outside temperatures. Have you tried your heat pump at a 34C flow temperature?
Posted by: @robsyour figures correlate well with your heat pump having a minimum output of about 3kW at these outside temperatures. Have you tried your heat pump at a 34C flow temperature?
At first I tried 32c for about 10days. It was ok but still cycling a bit too much. So I took it straight to 35c.
But you make a valid point. A small reduced flow temp, by 1 or 2 degrees, may give improved efficiency without increased cycling.
I will do this and let you know how I get on. Thanks for your useful observations.
Behaviour of compressor is subtly different as flow temperature is dropped to 34 and 33c. The original lowest flow temp of 35c as set on weather compensation which was the set flow temp for all outdoor Ambients 10c and above.
At 34c the cycling increases to 4 per hour with short 5 minute pauses.
At 33c the cycling drops to 3 per hour but the temperature drop appears to be done by creating longer pauses of 10 minutes.
In all cases the flow temperature still registers 35 or 36c. It appears to use variable pauses in operation to reduce the average energy input to 33c.
This operation seems to still be within acceptable Mitsubishi operating tolerances.
To clarify, these graphs are from a radiator only system with a total RAD DT50 capacity of 21kw. Which is greatly reduced to 3.4kw when operating at flow temp 35c. These graphs are specific to our setup and not necessarily typical.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 32 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
I think the setup I have could use wireless sensors, th...
By cathodeRay , 28 minutes ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I couldn't agree more. This is a case where you buy as...
By JamesPa , 4 hours ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 18 hours ago
-
Inventor (Midea) Heat Pump short cycling advice
Hello, I have a Inventor (Midea) 8kW with a 800meters Φ...
By immunity , 19 hours ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
I have signed up as well. @belsnugg could you outline ...
By JamesPa , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 1 day ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 2 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 2 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 2 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 2 days ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 3 days ago
-
@drei When I was in local government we were of cours...
By JamesPa , 3 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 3 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 4 days ago